Configuration objects
Index 2n02 Amplifier Settings Ch.x
- Index 2002: Amplifier Settings Ch.1
- Index 2802: Amplifier Settings Ch.2
Subindex (hex) | Name | Meaning | Data Type | Flags | Default |
0 | Amplifier Settings Ch.x |
| USINT | RO | 0x7A (122dec) |
12 | Current loop integral time | Integral component of current controller. Unit: [0.1 ms] | UINT | RW | 0xA (10dec) |
13 | Current loop proportional gain | Proportional component of current controller. Unit: [0.1 V/A] | UINT | RW | 0x64 (100dec) |
14 | Velocity loop integral time | Integral component of velocity controller. Unit: [0.1 ms] | UDINT | RW | 0x96 (150dec) |
15 | Velocity loop proportional gain | Proportional component of velocity controller. Unit: [mA / (rad/s)] | UDINT | RW | 0x14 (20dec) |
17 | Position loop proportional gain | Proportional component position controller. Unit: [(rad/s) / rad] | UDINT | RW | 0xA (10dec) |
29 | Amplifier I2T warn level | I²T model warning threshold. Unit: [%] | USINT | RW | 0x50 (80dec) |
2A | Amplifier I2T error level | I²T model error threshold. Unit: [%] | USINT | RW | 0x69 (105dec) |
31 | Velocity limitation | Velocity limitation. If a gear ratio is configured (parameter 6091/6891), this limit value refers to the load side. Unit: [1/min] | UDINT | RW | 0x186A0 (100000dec) |
32 | Short circuit brake duration max | Maximum holding time for anchor short-circuit braking Unit: [ms] | UINT | RW | 0x3E8 (1000dec) |
33 | Stand still window | Standstill window Unit: [1/min] | UINT | RW | 0x1 (1dec) |
49 | Halt ramp deceleration | Halt ramp deceleration. Unit: [0.1 rad / s²] | UDINT | RW | 0xF570 (62832dec) |
54 | Feature bits | Reserved. Please do not change. | UDINT | RW | 0x0 (0dec) |
55 | Select info data 1 | Possible values:
| USINT | RW | 0x2 (2dec) |
56 | Select info data 2 | Possible values:
| USINT | RW | 0x4 (4dec) |
57 | Velocity feed forward gain | Scaling factor for velocity feedforward from the position interpolator. | USINT | RW | 0x64 (100dec) |
58 | Select info data 3 | Possible values:
| USINT | RW | 0x7 (7dec) |
59 | Error suppression mask | Reserved. Please do not change. | UDINT | RW | 0x0 (0dec) |
5F | Sensorless observer bandwidth | Observer bandwidth for sensorless control Unit: [Hz] | UINT | RW | 0xC8 (200dec) |
62 | Position loop deadband window | Deadband window of the position controller Unit: [increments] | UDINT | RW | 0x0 (0dec) |
64 | Commutation type | Possible values:
| USINT | RW | 0x5 (5dec) |
6D | Torque feed forward gain | Internal torque feedforward: scaling factor | UDINT | RW | 0x0 (0dec) |
6E | Torque feed forward filter time | Internal torque feedforward: filter time. Unit: [0.1 ms] | UDINT | RW | 0xA (10dec) |
71 | Error Code Options | Choice of diagnostic messages that are displayed in 0x6n3F “Error code” (PDO mapping possible) Possible values:
72 | Stand still torque limitation | Output standstill holding current for sensorless control | UINT | RW | 0x1F4 (500dec) |
73 | Acceleration limitation | Maximum acceleration (setpoint limit) Unit: [0.1 rad/s²] | UDINT | RW | 0xF570 (62832dec) |
79 | Sensorless Startup Current Scaling | Motor starting current for sensorless control. The current configured here is output at low speeds (“forced startup” phase). Specified in parts per thousand of the rated motor current. | UINT | RW | 0x2EE (750dec) |
7A | Sensorless Stall Reaction | Reaction to a detected commutation error (Motor Stall) in sensorless control. Possible values:
| USINT | RW | 0x0 (0dec) |
Index 2n03 Motor Settings Ch.x
- Index 2003: Motor Settings Ch.1
- Index 2803: Motor Settings Ch.2
Subindex (hex) | Name | Meaning | Data type | Flags | Default |
0 | Motor Settings Ch.x |
| USINT | RO | 0x34 (52dec) |
11 | Max current | Peak current Unit: [mA] | UDINT | RW | 0x445C (17500dec) |
13 | Motor pole pairs | Number of pole pairs | USINT | RW | 0x1 (1dec) |
16 | Torque constant | Torque constant Unit: [mNm/A] | UDINT | RW | 0x12C (300dec) |
18 | Rotor moment of inertia | Motor moment of inertia Unit: [g cm²] | UDINT | RW | 0x1EF (495dec) |
19 | Winding inductance | Winding inductance Unit: [0.1 mH] | UINT | RW | 0x186 (390dec) |
29 | Motor I2T warn level | I²t model warning threshold Unit: [%] | USINT | RW | 0x50 (80dec) |
2A | Motor I2T error level | I²t model error threshold Unit: [%] | USINT | RW | 0x69 (105dec) |
2D | Motor thermal time constant | Thermal time constant Unit: [0.1 s] | UINT | RW | 0x28 (40dec) |
2E | Rated speed | Rated speed Unit: [rpm] | UDINT | RW | 0x3E8 (1000dec) |
30 | Winding resistance | Winding resistance Unit: [mOhm] | UDINT | RW | 0x578 (1400dec) |
31 | Voltage constant | Motor back‑EMF voltage constant Unit: [µV/(1/min)] | UDINT | RW | 0x4E20 (20000dec) |
34 | Configured motor current | Limits the output current. (The output current is limited to the lower of "Rated current" and "Configured motor current".) This parameter allows you to prevent the channel from drawing a disproportionately large share of the available UP total current relative to the other channels. | UDINT | RW | 0x1618 (5656dec) |
2n04 Brake Settings Ch.x
- Index 2004: Brake Settings Ch.1
- Index 2804: Brake Settings Ch.2
0 | Brake Settings Ch.x |
| USINT | RO | 0x18 (24dec) |
01 | Enable manual override | Enable for manual control of the holding brake | BOOL | RW | 00 |
02 | Manual brake state | Possible values:
| BOOL | RW | 00 |
05 | Brake option | Configuration for inverted motor brakes Possible values:
09 | External override | Choice of a digital input that can be used to open the motor brake independently of the drive controller, e.g. for maintenance. Possible values:
11 | Release delay | Time the holding brake requires for opening (releasing) after the current was applied. Unit: [ms] | UINT | RW | 0x0 (0dec) |
12 | Application delay | Time the holding brake requires for closing (holding) after the current was switched off. Unit: [ms] | UINT | RW | 0x0 (0dec) |
13 | Emergency application timeout | Time that the amplifier waits for the velocity to reach the standstill limit after a stop request. Note: This parameter must be set at least to the longest time the axis needs to come to a standstill after it has been switched torque-free. For vertical axes, this parameter should be set to a low value to prevent the axis or load from falling very far. Unit: [ms] | UINT | RW | 0x0 (0dec) |
14 | Brake moment of inertia | Moment of inertia of the brake. Unit: [g cm²] | UINT | RW | 0x0 (0dec) |
18 | Brake Output Features | Control of a motor brake (depending on the drive controller) via a digital output Possible values:
Index 2n05 Filter Settings Ch.x
- Index 2005: Filter Settings Ch.1
- Index 2805: Filter Settings Ch.2
0 | Filter Settings Ch.x |
| USINT | RO | 0x19 (25dec) |
10 | Low pass frequency 1 | Unit: [Hz] | REAL | RW | 0.0 |
11 | Low pass damping 1 |
| REAL | RW | 0.0 |
12 | High pass frequency 1 | Unit: [Hz] | REAL | RW | 0.0 |
13 | High pass damping 1 |
| REAL | RW | 0.0 |
14 | Filter type 1 | Possible values:
15 | Low pass frequency 2 | Unit: [Hz] | REAL | RW | 0.0 |
16 | Low pass damping 2 |
| REAL | RW | 0.0 |
17 | High pass frequency 2 | Unit: [Hz] | REAL | RW | 0.0 |
18 | High pass damping 2 |
| REAL | RW | 0.0 |
19 | Filter type 2 | Possible values:
Index 2n0A Digital Output Settings Ch.x
- Index 200A: Digital Output Settings Ch.1
- Index 280A: Digital Output Settings Ch.2
0 | Digital Output Settings Ch.x |
| USINT | RO | 0x2 (2dec) |
01 | Use Output 1 as +24V power supply | If “TRUE”: The respective digital output is always active and serves as supply voltage, e.g. for limit switches | BOOL | RW | 00 |
02 | Use Output 2 as +24V power supply | BOOL | RW | 00 |
Index 2n10 Feedback Settings Ch.x
- Index 2010: Feedback Settings Ch.1
- Index 2810: Feedback Settings Ch.2
0 | Feedback Settings Ch.1 |
| USINT | RO | 0x17 (23dec) |
11 | Device type |
12 | Singleturn bits | Number of single-turn bits used to represent the position in the process image. The sum of the single-turn bits and multi-turn bits must be 32. | USINT | RW | 0x14 (20dec) |
13 | Multiturn bits | Number of multi-turn bits used to represent the position in the process image. The sum of the single-turn bits and multi-turn bits must be 32. | USINT | RW | 0xC (12dec) |
14 | Observer bandwidth | Bandwidth of the velocity observer in [Hz] | UINT | RW | 0xC8 (200dec) |
15 | Observer feed-forward | Load ratio in [%] between internal rotor inertia of the motor and the total inertia of the driven system. Load ratio = internal moment of inertia / (internal moment of inertia + mass moment of inertia of the load). Examples: 100 % = load-free 50 % = moments of inertia of input and output are equal | USINT | RW | 0x64 (100dec) |
17 | Position offset | The position offset is subtracted from the raw position of the encoder. It can only be written with the axis stopped. | DINT | RW | 0x0 (0dec) |
Index 2n20 Vendor data Ch.x
- Index 2020: Vendor data Ch.1
- Index 2820: Vendor data Ch.2
0 | Vendor data Ch.x |
11 | Amplifier peak current | Amplifier peak current (peak value) Unit: [mA] | UDINT | RW | 0x445C (17500dec) |
12 | Amplifier rated current | Amplifier rated current (peak value) Unit: [mA] | UDINT | RW | 0x1618 (5656dec) |
13 | Amplifier thermal time constant | Thermal time constant Unit: [0.1 s] | UINT | RW | 0x23 (35dec) |
14 | Amplifier overcurrent threshold | Per‑phase instantaneous current threshold for short‑circuit detection Unit: [mA] | UDINT | RW | 0x7530 (30000dec) |
15 | Max rotary field frequency | Maximum rotary field frequency Unit: [Hz] | UINT | RW | 0x257 (599dec) |
18 | Vendor feature bits |
1A | Amplifier Rated Sum Current | Unit: [mA] | UDINT | RW | 0x2C30 (11312dec) |
Index 2n08 DMC Settings Ch.x
- Index 2108: DMC Settings Ch.1
- Index 2908: DMC Settings Ch.2
0 | DMC Settings Ch.x | - | USINT | RO | 0x17 (23dec) |
07 | Emergency deceleration | Deceleration for the emergency stop ramp. (In [ms] from rated motor speed to standstill) | UINT | RW | 0x64 (100dec) |
08 | Calibration position | If homing is successful, the “Actual position” is set to this value. | LINT | RW | 0x0 (0dec) |
09 | Calibration velocity (towards plc cam) | Velocity when hitting the cam in 10000ths of the rated motor speed. | INT | RW | 0x64 (100dec) |
0A | Calibration Velocity (off plc cam) | Velocity when driving off the cam in 10000ths of the rated motor speed. | INT | RW | 0xA (10dec) |
0E | Modulo factor | Feedback increments for one mechanical revolution. | LINT | RW | 0x100000000 (4294967296dec) |
12 | Block calibration torque limit | Torque limitation for approaching the end stop. In parts per thousand of the rated motor current. | UINT | RW | 0x64 (100dec) |
13 | Block calibration stop distance | After reaching the calibration position, the axis moves out of the end position by this distance. | LINT | RW | 0x100000000 (4294967296dec) |
14 | Block calibration lag threshold | When this following error is exceeded, the axis is in the end position. | LINT | RW | 0x100000000 (4294967296dec) |
15 | Target position window | Target position window: The in-target bit is set when the axis is within this window for at least the time set under subindex 16. | LINT | RW | 0x16C16C1 (23860929dec) |
16 | Target position monitor time | See subindex 15 Unit: [ms] | UINT | RW | 0x14 (20dec) |
17 | Target position timeout | When the setpoint generator has reached its end position and the axis is not in the target window after this time has elapsed, the task is terminated and the in-target bit is not set. Unit: [ms] | UINT | RW | 0x1770 (6000dec) |
Index 2n09 DMC Features Ch.x
- Index 2109: DMC Features Ch.1
- Index 2909: DMC Features Ch.2
0 | DMC Features Ch.x |
| USINT | RO | 0x1B (27dec) |
13 | Invert calibration cam search direction | Invert the direction of movement to search for the limit switch. Default: FALSE = search with positive direction of rotation. | BOOL | RW | 00 |
14 | Invert sync impulse search direction | Invert the direction of rotation to exit the limit switch. Default: TRUE = exit in negative direction of rotation. | BOOL | RW | 01 |
19 | Calibration cam source | Source for the reference switch:
1A | Calibration cam active level | State of the reference switch in the actuated state:
1B | Latch source | Source for the latch unit:
F800 DRV Amplifier Settings
Index (hex) | Name | Meaning | Data Type | Flags | Default |
F800:0 | DRV Amplifier Settings |
F800:10 | Nominal DC link voltage | Rated DC link voltage. Unit: [mV] | UDINT | RW | 0xBB80 (48000dec) |
F800:11 | Min DC link voltage | Minimum DC link voltage. Unit: [mV] | UDINT | RW | 0x1A90 (6800dec) |
F800:12 | Max DC link voltage | Maximum DC link voltage. Unit: [mV] | UDINT | RW | 0xEA60 (60000dec) |
F800:15 | Amplifier Temperature warn level | Amplifier temperature warning threshold. Unit: [0.1 °C] | UINT | RW | 0x320 (800dec) |
F800:16 | Amplifier Temperature error level | Amplifier temperature error threshold. Unit: [0.1 °C] | UINT | RW | 0x3E8 (1000dec) |
F800:17 | Feature bits |