Standard objects
1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: the Lo-Word contains the used CoE profile (5001). The Hi-Word contains the module profile according to the modular device profile. | UDINT | - | 0x00001389 (5001dec) |
1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave. | STRING | - | EP6601 |
1009 Hardware version
1009:0 | Hardware version | Hardware version of the EtherCAT slave. | STRING | - | - |
100A Software version
100A:0 | Software version | Firmware version of the EtherCAT slave. | STRING | - | - |
100B Bootloader version
100B:0 | Bootloader version | Bootloader version of the EtherCAT slave. | STRING | RO | - |
1011 Restore default parameters
1011:0 | Restore default parameters | Restore the delivery state. | USINT | RO | 0x01 (1dec) |
1011:01 | SubIndex 001 | If you set this object to "0x64616F6C", all backup objects are reset to the delivery state. |
| RW | 0 |
1018 Identity
1018:0 | Identity | Information for identifying the slave. | USINT | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave. | UDINT | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave. | UDINT | RO | 0x19C94052 (432619602dec) |
1018:03 | Revision | Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description. | UDINT | RO | 0 |
1018:04 | Serial number | Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0. | UDINT | RO | 0 |
10E2 Manufacturer-specific Identification Code
10E2:0 | Manufacturer-specific Identification Code | Vendor-specific identification code. | USINT | RO | 0x01 (1dec) |
10F0 Backup parameter handling
10F0:0 | Backup parameter handling | Information for standardized loading and saving of backup entries. | USINT | RO | 0x01 (1dec) |
10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave. | UDINT | RO | 0 |
1C00 Sync manager type
1C00:0 | Sync manager type | Using the Sync Managers | UINT8 | RO | 0x04 (4dec) |
1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dec) |
1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dec) |
1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dec) |
1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dec) |
1C32 SM output parameter
1C32:0 | SM output parameter | Synchronization parameters for the outputs | UINT8 | RO | 0x20 (32dec) |
1C32:01 | Sync mode | Current synchronization mode:
3: DC-Mode - Synchron with SYNC1 Event | UINT16 | RW | 0x0001 (1dec) |
1C32:02 | Cycle time | Cycle time (in ns):
DC-Mode: SYNC0/SYNC1 Cycle Time | UINT32 | RW | 0x000F4240 (1000000dec) |
1C32:03 | Shift time | Time between SYNC0 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:04 | Sync modes supported | Supported synchronization modes:
Bit 14 = 1: dynamic times (measurement through writing of 1C32:08) | UINT16 | RO | 0x0003 (3dec) |
1C32:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x0003D090 (250000dec) |
1C32:06 | Calc and copy time | Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) | UINT32 | RO | 0 |
1C32:07 | Minimum delay time | Delay due to signal propagation times in hardware, minimum value. Unit: ns | UINT32 | RO | 0 |
1C32:08 | Get Cycle Time |
Entries 1C32:03, 1C32:05, 1C32:06, 1C32:09, 1C33:03, 1C33:06, 1C33:09 are updated with the maximum measured values. For a subsequent measurement the measured values are reset | UINT16 | RW | 0 |
1C32:09 | Maximum delay time | Time between SYNC1 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0 |
1C32:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0 |
1C32:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0 |
1C32:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only). | UINT | RO | 0 |
1C32:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0 |
1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | USINT | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
34: Synchron with SM 2 Event (outputs available) | UINT | RW | 0 |
1C33:02 | Cycle time | Cycle time (in ns):
DC-Mode: SYNC0/SYNC1 Cycle Time | UDINT | RW | 0 |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, DC mode only) | UDINT | RO | 0 |
1C33:04 | Sync modes supported | Supported synchronization modes:
Bit 14 = 1: dynamic times (measurement through writing of 1C33:08) | UINT | RO | 0x0002 (2dec) |
1C33:05 | Minimum cycle time | Minimum cycle time (in ns) | UDINT | RO | 0 |
1C33:06 | Calc and copy time | Time between reading of the inputs and the inputs being available for the master (in ns, only DC mode) | UDINT | RO | 0 |
1C33:07 | Minimum delay time | Delay due to signal propagation times in hardware, minimum value. Unit: ns | UDINT | RO | 0 |
1C33:08 | Get Cycle Time |
The entries 1C33:03, 1C33:06, 1C33:07, 1C33:09 are updated with the maximum measured values. | UINT | RW | 0 |
1C33:09 | Maximum delay time | Time between SYNC1 event and reading of the inputs (in ns, DC mode only) | UDINT | RO | 0 |
1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT | RO | 0 |
1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT | RO | 0 |
1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT | RO | 0 |
1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOL | RO | 0 |
F000 Modular Device Profile
F000:0 | Modular Device Profile | General information for the Modular Device Profile. | USINT | RO | 0x02 (2dec) |
F000:01 | Index distance | Index distance of the objects of the individual channels. | UINT | RO | 0x0010 (16dec) |
F000:02 | Maximum number of modules | Number of channels. | UINT | RO | 0 |
F008 Code word
F008:0 | Code word | reserved | UDINT | RW | 0 |
F081 Download revision
F081:0 | Download revision |
F081:01 | Revision number | Revision number of the module. Relevant as a startup list entry for compatibility. | UDINT | RW | 0x00120002 (1179650dec) |