ADS Error Codes
Error codes are generated in the event of an error during ADS access to an IO-Link device.
The possible error codes are listed in tables C.1 and C.2.
Example of an AdsReturnCode
AdsReturnCode 0x80110700
- 80: Device Application Error (IO-Link Spec),
- 11
: Index not Available (IO-Link Spec),
- 0700
: General ADS Error
ErrorTypes (IO-Link Spec)
Incident
Error Code
Additional Code
Definition
Device application error – no details
0x80
0x00
APP_DEV
This ErrorType shall be used if the requested service has been refused by the Device application and no detailed
Index not available
0x80
0x11
IDX_NOTAVAIL
This ErrorType shall be used whenever a read or write access occurs to a not existing Index.
Subindex not available
0x80
0x12
SUBIDX_NOTAVAIL
This ErrorType shall be used whenever a read or write access occurs to a not existing Subindex.
Service temporarily not available
0x80
0x20
SERV_NOTAVAIL
This ErrorType shall be used if a parameter is not accessible for a read or write service due to the current state of the Device application.
Service temporarily not available – local control
0x80
0x21
SERV_NOTAVAIL_LOCCTRL
This ErrorType shall be used if a parameter is not accessible for a read or write service due to an ongoing local operation at the Device (for example operation or parameterization via an on-board Device control panel).
Service temporarily not available – Device control
0x80
0x22
SERV_NOTAVAIL_DEVCTRL
This ErrorType shall be used if a read or write service is not accessible due to a remote triggered state of the device application (for example parameterization during a remote triggered teach-in operation or calibration).
Access denied
0x80
0x23
IDX_NOT_WRITEABLE
This ErrorType shall be used if a write service tries to access a read-only parameter.
Parameter value out of range
0x80
0x30
PAR_VALOUTOFRNG
This ErrorType shall be used for a write service to a parameter outside its permitted range of values.
Parameter value above limit
0x80
0x31
PAR_VALGTLIM
This ErrorType shall be used for a write service to a parameter above its specified value range.
Parameter value below limit
0x80
0x32
PAR_VALLTLIM
This ErrorType shall be used for a write service to a parameter below its specified value range.
Parameter length overrun
0x80
0x33
VAL_LENOVRRUN
This ErrorType shall be used when the content of a write service to a parameter is greater than the parameter specified length. This ErrorType shall also be used, if a data object is too large to be processed by the Device application (for example ISDU buffer restriction).
Parameter length underrun
0x80
0x34
VAL_LENUNDRUN
This ErrorType shall be used when the content of a write service to a parameter is less than the parameter specified length (for example write access of an Unsigned16 value to an Unsigned32 parameter).
Function not available
0x80
0x35
FUNC_NOTAVAIL
This ErrorType shall be used for a write service with a command value not supported by the Device application (for example a SystemCommand with a value not implemented).
Function temporarily unavailable
0x80
0x36
FUNC_UNAVAILTEMP
This ErrorType shall be used for a write service with a command value calling a Device function not available due to the current state of the Device application (for example a SystemCommand).
Invalid parameter set
0x80
0x40
PAR_SETINVALID
This ErrorType shall be used if values sent via single parameter transfer are not consistent with other actual parameter settings (for example overlapping set points for a binary data setting
Inconsistent parameter set
0x80
0x41
PAR_SETINCONSIST
This ErrorType shall be used at the termination of a block parameter transfer with ParamDownloadEnd or ParamDownloadStore if the plausibility check shows inconsistencies
Application not ready
0x80
0x82
APP_DEVNOTRDY
This ErrorType shall be used if a read or write service is refused due to a temporarily unavailable application (for example peripheral controllers during startup).
Vendor specific
0x81
0x00
UNSPECIFIC
This ErrorType will be propagated directly to higher level processing elements as an error (no warning) by the Master.
Vendor specific
0x81
0x01 to 0xFF
VENDOR_SPECIFIC
Table C.1 ErrorTypes, IO-Link Spec
Derived ErrorTypes (IO-Link Spec)
Incident
Error Code
Additional Code
Definition
Master – Communication error
0x10
0x00
COM_ERR
The Master generates a negative service response with this ErrorType if a communication error occurred during a read or write service, for example the SDCI connection is interrupted.
Master – ISDU timeout
0x11
0x00
I-SERVICE_TIMEOUT
The Master generates a negative service response with this ErrorType, if a Read or Write service is pending longer than the specified I-Service timeout in the Master.
Device Event – ISDU error (DL, Error, single shot, 0x5600)
0x11
0x00
I-SERVICE_TIMEOUT
If the Master received an Event with the EventQualifier and the EventCode 0x5600, a negative service response indicating a service timeout is generated and returned to the requester (Master – ISDU timeout).
Device Event – ISDU illegal service primitive (AL, Error, single shot, 0x5800)
0x11
0x00
I-SERVICE_TIMEOUT
If the Master received an Event with the EventQualifier and the EventCode 0x5800, a negative service response indicating a service timeout is generated and returned to the requester (Master – ISDU timeout).
Master – ISDU checksum error
0x56
0x00
M_ ISDU_CHECKSUM
The Master generates a negative service response with this ErrorType, if its data link layer detects an ISDU checksum error.
Master – ISDU illegal service primitive
0x57
0x00
M_ ISDU_ILLEGAL
The Master generates a negative service response with this ErrorType, if its data link layer detects an ISDU illegal service primitive.
Device Event – ISDU buffer overflow (DL, Error, single shot, 0x5200)
0x80
0x33
VAL_LENOVRRUN
If the Master received an Event with the EventQualifier and the EventCode 0x5200, a negative service response indicating a parameter length overrun is generated and returned to the requester (see parameter length overrun)
Events from legacy Devices shall be redirected in compatibility mode to this derived ErrorType
Table C.2 Derived ErrorTypes, IO-Link Spec