Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT | |
Connection |
2 x M8 socket, 4-pin, green |
Electrical isolation | 500 V |
Supply voltages | |
Connection | Input: M8 connector, 4-pin Downstream connection: M8 socket, 4-pin, black |
US nominal voltage |
24 VDC (-15 % / +20 %) |
US sum current: IS,sum | max. 4 A |
Current consumption from US | 130 mA + Current consumption of connected end devices + Loads at digital outputs |
Rated voltage UP | 24 VDC (-15 % / +20 %) |
UP sum current: IP,sum | max. 4 A |
Current consumption from UP | None. UP is only forwarded. |
Serial interface | |
Number of channels | 1 |
Interface type | ajustable:
Connection | RS232: 1 x M12 socket RS422: 2 x M12 socket RS485: 1 x M12 socket |
End device power supply | Output voltage: 5 VDC Output current: max. 1 A, short-circuit proof The end device power supply is branched off from the supply voltage US. |
Cable length | RS232: max. 15 m RS422: max. 1000 m RS485: max. 1000 m |
Data transfer rate | Adjustable: 300 … 115,200 baud (bit/s) |
Data format | Adjustable: 8N1, 7E1, 7O1, 8N1, 8E1, 8O1, 7E2, 7O2, 8N2, 8E2, 8O2 |
Flow control | Software flow control "XON/XOFF" |
Bit distortion | < 3 % |
Receive buffer | 846 bytes |
Send buffer | 128 bytes |
Digital inputs | |
Number | 0 to 2 Each digital input can alternatively be used as a digital output. |
Connection | 1 x M12 socket |
Sensor supply | Output voltage: 24 VDC Output current: max. 0.5 A, short-circuit proof The sensor supply is branched off from the supply voltage US. |
Input filter | 10 µs |
Characteristics | Type 3 according to EN61131-2, compatible with type 1 |
Signal voltage "0" | -3…+5 V |
Signal voltage "1" | +11…+30 V |
Input current | 3 mA |
Digital outputs | |
Number | 0 to 2 Each digital output can alternatively be used as a digital input. |
Load type | Ohmic, inductive, lamp load |
Nominal output voltage | 24 VDC |
Output current per channel | max. 0.5 A. Each output is independently short-circuit proof. |
Short circuit current | max. 1.5 A |
Output driver supply | From the supply voltage US. |
Housing data | |
Dimensions W x H x D | 30 mm x 126 mm x 26.5 mm (without connectors) |
Weight | approx. 165 g |
Material |
PA6 (polyamide) |
Environmental conditions | |
Ambient temperature during operation | -25…+60 °C |
Ambient temperature during storage | -40…+85 °C |
Vibration resistance, shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection class | IP65, IP66, IP67 (conforms to EN 60529) |
Approvals | |
Approvals | CE, cURus |
Additional checks
The boxes have been subjected to the following checks:
Verification | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |