User calibration in the PLC
You can also perform the correction calculation in the PLC instead of in the box. This has the advantage that you can set the measured value resolution as required: if the correction calculation is carried out in the box, the measured value resolution is limited to 1 mg/LSB.
Beckhoff also recommends reading the calibration coefficients from the CoE parameters provided for this purpose when calculating corrections in the PLC. This means that the PLC program does not have to be adapted when the box is replaced.
Sample program for the X-axis
Preparation:
PROGRAM MAIN
    nAmsNetIdArr AT %I*: T_AmsNetIdArr;
    nSlaveAddress AT %I*: WORD;
    nAxis_Value AT %I*: DINT;
    eState: (IDLE, INIT_READ_OFFSET, READING_OFFSET, INIT_READ_GAIN, READING_GAIN,
             NOMINAL_OPERATION, ERROR);
    fbSdoRead: FB_EcCoESdoRead;
    sAmsNetId: T_AmsNetId;
    nOffset: INT;
    nGainRaw: INT;
    fGain: REAL;
    fAxCalibrated: REAL;
    bExecute: BOOL;
CASE eState OF
    IDLE:
        fbSdoRead(bExecute := FALSE);
        sAmsNetId := F_CreateAmsNetId(nAmsNetIdArr);
        IF bExecute THEN
            eState := INIT_READ_OFFSET;
        END_IF
    INIT_READ_OFFSET:
        fbSdoRead(
            sNetId := sAmsNetId,
            nSlaveAddr := nSlaveAddress,
            nSubIndex := 16#17,
            nIndex := 16#8000,
            pDstBuf := ADR(nOffset),
            cbBufLen := SIZEOF(nOffset),
            bExecute := TRUE
        eState := READING_OFFSET;
    READING_OFFSET:
        fbSdoRead();
        IF NOT fbSdoRead.bBusy THEN
            IF fbSdoRead.bError THEN
                eState := Error;
            ELSE
                eState := INIT_READ_GAIN;
            END_IF
        END_IF
    INIT_READ_GAIN:
        fbSdoRead(
            nSubIndex := 16#18,
            nIndex := 16#8000,
            pDstBuf := ADR(nGainRaw),
            cbBufLen := SIZEOF(nGainRaw),
            bExecute := TRUE
        eState := READING_GAIN;
    READING_GAIN:
        fbSdoRead();
                eState := ERROR;
            ELSE
                fGain := INT_TO_REAL(nGainRaw) / 16384;
                eState := NOMINAL_OPERATION;
            END_IF
        END_IF
    NOMINAL_OPERATION:
        fAxCalibrated := fGain * DINT_TO_REAL(nAxis_Value - nOffset);
    ERROR:
END_CASE