Configuration objects
8pp0 PWM Settings Ch.n
Subindex (hex)
Meaning
Data type
Flags
Default
0
PWM Settings Ch.n
USINT
RO
0x22 (34dec)
03
Enable Dithering
Enables dithering. Dithering is a square wave signal that is modulated onto the current signal.
See chapter Dithering.
RW
00
05
Watchdog
Enables the watchdog.
The watchdog sets the output to a defined value if EtherCAT communication is interrupted.
See chapter Behavior on EtherCAT failure: watchdog.
Possible values:
  • 0dec: Default Watchdog Value
  • 1dec: Watchdog Ramp Active
  • 2dec: Last Output Value Active
USINT
RW
0x0 (0dec)
07
Operation Mode
Operation mode. Possible values:
  • 0: "Current Control"
    The output operates as a PWM-controlled current output.
    Use "PWM Output" to specify the output current.
  • 1: "Voltage Control"
    The output operates as a regular PWM output.
    Use "PWM Output" to specify the duty cycle.
USINT
RW
0x0 (0dec)
09
Enable Feedforward
Enables the feedforward pre-control for the ohmic resistance of the load.
Before enabling, set the parameter 8pp0:19 "Coil Resistance" correctly.
RW
00
0B
Offset
User calibration offset in [mA].
INT
RW
0x0 (0dec)
0C
Gain
User calibration gain.
DINT
RW
0x10000 (65536dec)
0D
Default Output
Parameter for the watchdog. See chapter Behavior on EtherCAT failure: watchdog.
INT
RW
0x0 (0dec)
0E
Default Output Ramp
UINT
RW
0xFFFF (65535dec)
10
Max Current
Maximum output current.
Specification in % of the parameter 8ppF:06 "Nominal Current" (2 A)
USINT
RW
0x64 (100dec)
12
Kp Factor
Proportional component of the current controller.
UINT
RW
0xFA (250dec)
13
Ki Factor
Integral component of the current controller.
UINT
RW
0x4 (4dec)
14
Kd Factor
Differential component of the current controller.
UINT
RW
0x0 (0dec)
19
Coil Resistance
The ohmic resistance of the connected inductance in [0.01 Ohm].
Must only be set when using feedforward pre-control (8pp0:09).
UINT
RW
0xFA (250dec)
1E
Dithering Frequency
Frequency of the dither in [Hz].
UINT
RW
0x64 (100dec)
1F
Dithering Amplitude
Amplitude of the dither.
Specified as a percentage of the maximum current configured via 8pp0:10.
USINT
RW
0xA (10dec)
Subindex (hex)
Meaning
Data type
Flags
Default
21
Select Info Data 1
Possible values:
  • 0dec: Actual Current
  • 1dec: Set Current
  • 2dec: Duty Cycle
  • 3dec: Supply Voltage
USINT
RW
0x0 (0dec)
22
Select Info Data 2
Possible values:
  • 1dec: Set Current
  • 2dec: Duty Cycle
USINT
RW
0x1 (1dec)