Diag Messages

DiagMessages designates a system for the transmission of messages from the EtherCAT Slave to the EtherCAT Master/TwinCAT. The messages are stored by the device in its own CoE under 0x10F3 and can be read by the application or the System Manager. An error message referenced via a code is output for each event stored in the device (warning, error, status change).

Definition

The DiagMessages system is defined in the ETG (EtherCAT Technology Group) in the guideline ETG.1020, chapter 13 “Diagnosis handling”. It is used so that pre-defined or flexible diagnostic messages can be conveyed from the EtherCAT Slave to the Master. In accordance with the ETG, the process can therefore be implemented supplier-independently. Support is optional. The firmware can store up to 250 DiagMessages in its own CoE.

Each DiagMessage consists of

The DiagMessages are explained in text form in the ESI/XML file belonging to the EtherCAT device: on the basis of the Text ID contained in the DiagMessage, the corresponding plain text message can be found in the languages contained in the ESI/XML. In the case of Beckhoff products these are usually German and English.

Via the entry NewMessagesAvailable the user receives information that new messages are available.

DiagMessages can be confirmed in the device: the last/latest unconfirmed message can be confirmed by the user.

In the CoE both the control entries and the history itself can be found in the CoE object 0x10F3:

Diag Messages 1:
DiagMessages in the CoE

The subindex of the latest DiagMessage can be read under 0x10F3:02.

Diag Messages 2:

Support for commissioning

The DiagMessages system is to be used above all during the commissioning of the plant. The diagnostic values e.g. in the StatusWord of the device (if available) are helpful for online diagnosis during the subsequent continuous operation.

TwinCAT System Manager implementation

From TwinCAT 2.11 DiagMessages, if available, are displayed in the device’s own interface. Operation (collection, confirmation) also takes place via this interface.

Diag Messages 3:
Implementation of the DiagMessage system in the TwinCAT System Manager

The operating buttons (B) and the history read out (C) can be seen on the Diag History tab (A). The components of the message:

The meanings of the buttons are self-explanatory.

DiagMessages within the ADS Logger/Eventlogger

From TwinCAT 3.1 build 4022 onwards, DiagMessages sent by the terminal are shown by the TwinCAT ADS Logger. Given that DiagMessages are represented IO- comprehensive at one place, commissioning will be simplified. In addition, the logger output could be stored into a data file – hence DiagMessages are available long-term for analysis.

DiagMessages are actually only available locally in CoE 0x10F3 in the terminal and can be read out manually if required, e.g. via the DiagHistory mentioned above.

In the latest developments, the EtherCAT Terminals are set by default to report the presence of a DiagMessage as emergency via EtherCAT; the event logger can then retrieve the DiagMessage. The function is activated in the terminal via 0x10F3:05, so such terminals have the following entry in the StartUp list by default:

Diag Messages 4:
Startup List

If the function is to be deactivated because, for example, many messages come in or the EventLogger is not used, the StartUp entry can be deleted or set to 0. The value can then be set back to 1 later from the PLC via CoE access if required.

Reading messages into the PLC

- In preparation -

Interpretation

Time stamp

The time stamp is obtained from the local clock of the terminal at the time of the event. The time is usually the distributed clock time (DC) from register x910.

Please note: When EtherCAT is started, the DC time in the reference clock is set to the same time as the local IPC/TwinCAT time. From this moment the DC time may differ from the IPC time, since the IPC time is not adjusted. Significant time differences may develop after several weeks of operation without a EtherCAT restart. As a remedy, external synchronization of the DC time can be used, or a manual correction calculation can be applied, as required: The current DC time can be determined via the EtherCAT master or from register x901 of the DC slave.

Structure of the Text ID

The structure of the MessageID is not subject to any standardization and can be supplier-specifically defined. In the case of Beckhoff EtherCAT devices (EL, EP) it usually reads according to xyzz:

x

y

zz

0: Systeminfo
2: reserved
1: Info
4: Warning
8: Error

0: System
1: General
2: Communication
3: Encoder
4: Drive
5: Inputs
6: I/O general
7: reserved

Error number

Example: Message 0x4413 --> Drive Warning Number 0x13

Text IDs of the ELM72xx

Text ID

Type

Location

Text Message

Comment

0x1201

Information

Communication

Communication re-established

Connection established

0x4101

Warning

General

Terminal-Overtemperature

Overtemperature. The internal temperature of the terminal exceeds the parameterized warning threshold.

0x4102

Warning

General

PDO-configuration is incompatible to the selected mode of operation

The selected PDOs do not match the set operation mode.

Example: Drive operates in velocity mode. However, the velocity PDO is not mapped in the PDOs.

0x4107

Warning

General

Undervoltage Up

 

0x4109

Warning

General

Overvoltage Up

 

0x410A

Warning

General

Fan

 

0x410B

Warning

General

Error detected, but disabled by suppression mask

 

0x4201

Warning

Communication

No communication to field-side (Auxiliary voltage missing)

 

0x4301

Warning

Encoder

Feedback-Warning

General encoder error

0x4411

Warning

Drive

DC-Link undervoltage

The DC link voltage of the terminal is lower than the parameterized minimum voltage. Activation of the output stage is prevented.

0x4412

Warning

Drive

DC-Link overvoltage

The DC link voltage of the terminal is higher than the parameterized maximum voltage. Activation of the output stage is prevented.

0x4413

Warning

Drive

I2T Amplifier overload

  • The amplifier is being operated outside the specification
  • The I2T-model of the amplifier is incorrectly parameterized

0x4414

Warning

Drive

I2T Motor overload

  • The motor is being operated outside the parameterized nominal values.
  • The I2T-model of the motor is incorrectly parameterized.

0x4415

Warning

Drive

Speed limitation active

The maximum speed is limited by the parameterized objects (e.g. velocity limitation, motor speed limitation). This warning is output if the set velocity is higher than one of the parameterized limits.

0x4417

Warning

Drive

Motor-Overtemperature

The internal temperature of the motor exceeds the parameterized warning threshold.

0x4418

Warning

Drive

Limit: Current

Limit: Current is limited

0x4419

Warning

Drive

Limit: Amplifier I2T-model exceeds 100%%

The threshold values for the maximum current were exceeded.

0x441A

Warning

Drive

Limit: Motor I2T-model exceeds 100%%

Limit: Motor I2T-model exceeds 100%

0x441B

Warning

Drive

Limit: Velocity limitation

The threshold values for the maximum speed were exceeded.

0x441C

Warning

Drive

Axis disabled via STO

An attempt was made to activate the axis, despite the fact that no voltage is present at the STO input.

0x4420

Warning

Drive

Cogging compensation not supported (%u)

 

0x4421

Warning

Drive

I2T-Model Brake chopper overload

 

0x4422

Warning

Drive

Limit: Brake chopper I2T-model exceeds 100%%

 

0x4423

Warning

Drive

Brake resistor not connected

 

0x4424

Warning

Drive

Modes of operation invalid

 

0x8104

Error

General

Terminal-Overtemperature

The internal temperature of the terminal exceeds the parameterized error threshold. Activation of the terminal is prevented.

Text ID

Type

Location

Text Message

Comment

0x8105

Error

General

PD-Watchdog

Communication between the fieldbus and the output stage is secured by a watchdog. The axis is stopped automatically if the fieldbus communication is interrupted.

  • The EtherCAT connection was interrupted during operation
  • The Master was switched to Config mode during operation

0x810A

Error

General

Fan

 

0x810B

Error

General

Undervoltage Up

 

0x810C

Error

General

Overvoltage Up

 

0x8135

Error

General

Cycletime has to be a multiple of 125 µs

The I/O or NC cycle time divided by 125 µs does not produce a whole number.

0x8137

Error

General

Electronic name plate: CRC error

Content of the external nameplate memory invalid.

0x8144

Error

General

Hardware fault (%d)

 

0x817F

Error

General

Error: 0x%X, 0x%X, 0x%X

 

0x81B0

Error

General

Content of PDO 0x%X is invalid: Item 0x%X:%X cannot be mapped

 

0x81B1

Error

General

Content of PDO 0x%X is invalid: Item 0x%X:%X has an unsupported length (%d bit)

 

0x8201

Error

Communication

No communication to field-side (Auxiliary voltage missing)

  • There is no voltage applied to the power contacts
  • A firmware update has failed

0x8302

Error

Encoder

Feedback-Error

The amplitude of the resolver is too small.

0x8304

Error

Encoder

OCT communication error

Encoder communication error

0x831A

Error

Encoder

Number of encoder-increments per revolution is not a power of two

 

0x8403

Error

Drive

ADC Error

Error during current measurement in the ADC

0x8404

Error

Drive

Overcurrent

Overcurrent in phase U, V or W

0x8405

Error

Drive

Modulo position invalid (feedback position has changed too much while drive was turned off)

Modulo position invalid

0x8406

Error

Drive

Undervoltage DC-Link

The DC link voltage of the terminal is lower than the parameterized minimum voltage. Activation of the output stage is prevented.

0x8407

Error

Drive

Overvoltage DC-Link

The DC link voltage of the terminal is higher than the parameterized maximum voltage. Activation of the output stage is prevented.

0x8408

Error

Drive

I2T-Model Amplifier overload

  • The amplifier is being operated outside the specification
  • The I2T-model of the amplifier is incorrectly parameterized

0x8409

Error

Drive

I2T-Model motor overload

  • The motor is being operated outside the parameterized nominal values.
  • The I2T-model of the motor is incorrectly parameterized.

0x840B

Error

Drive

Commutation error

 

0x840C

Error

Drive

Motor not connected

 

0x8415

Error

Drive

Invalid modulo range

Modulo factor invalid

0x8416

Error

Drive

Motor-Overtemperature

The internal temperature of the motor exceeds the parameterized error threshold. The motor stops immediately. Activation of the output stage is prevented.

0x8417

Error

Drive

Maximum rotating field velocity exceeded

Rotary field speed exceeds the value specified for dual use (EU 1382/2014).

0x841C

Error

Drive

STO while the axis was enabled

An attempt was made to activate the axis, despite the fact that no voltage is present at the STO input.

0x8420

Error

Drive

Teach-In Process (%d) failed

 

0x8421

Error

Drive

Teach-In Process Timeout (STO, DC-Link, ...)

 

0x8422

Error

Drive

Drive configuration missing

 

0x8423

Error

Drive

Invalid process data format (number of singleturn bits+multiturn bits != 32)

 

0x8441

Error

Drive

Maximum following error distance exceeded

 

0x8443

Error

Drive

Invalid value for Mode of Operation

 

0x8445

Error

Drive

I2T-Model Brake chopper overload

 

0x8446

Error

Drive

Brake chopper overcurrent

 

0x8448

Error

Drive

Drive / axis is not referenced

 

0x8449

Error

Drive

Target position not in modulo range

 

0x844A

Error

Drive

Modulo position: Checksum error

 

0x844B

Error

Drive

Modulo position: Storage not supported for singleturn encoder

 

0x844C

Error

Drive

Position offset cannot be used in the selected configuration

 

0x8450

Error

Drive

Invalid start type 0x%x

 

0x8451

Error

Drive

Invalid limit switch level

 

0x8452

Error

Drive

Drive error during positioning

 

0x8453

Error

Drive

Latch unit will be used by multiple modules

 

0x8454

Error

Drive

Drive not in control

 

0x8455

Error

Drive

Invalid value for "Target acceleration"

 

0x8456

Error

Drive

Invalid value for "Target deceleration"

 

0x8457

Error

Drive

Invalid value for "Target velocity"

 

0x8458

Error

Drive

Invalid value for "Target position"

 

0x8459

Error

Drive

Emergency stop active

 

0x845A

Error

Drive

Target position exceeds Modulofactor

 

0x845B

Error

Drive

Drive must be disabled

 

0x845C

Error

Drive

No Feedback found

 

0x845D

Error

Drive

Modulo factor invalid

 

0x845E

Error

Drive

Invalid target position window