PT500 specification

Electrical measuring range used

2000 Ω

5000 Ω

Applicable also for ELM3704
-1001 = X

Connection

4-wire

2/3-wire 1)

4-wire

2/3-wire 1)

X

Starting value

-200°C

-200°C

X

End value

850°C

850°C

X

Basic accuracy: Measuring deviation at 23°C terminal environment, with averaging, typ.

< ±0.068 K

< ±0.14 K

< ±0.12 K

< ±0.2 K

 

Basic accuracy: Measuring deviation at 55°C terminal environment, with averaging, typ.

< ±0.23 K

< ±0.5 K

< ±0.25 K

< ±0.6 K

 

Temperature coefficient 2), typ.

< 1.4 mK/K

< 5.8 mK/K

< 1.9 mK/K

< 6 mK/K

 

PDO LSB (Legacy Range only)

0.1/0.01/0.001°C/digit, depending on PDO setting

X

1) See initial remarks about 2/3-wire operation. The offset specification does not apply in 2-wire operation, as the offset is increased due to the connection. In 2-wire operation, an offset compensation is to be carried out after installation; refer to the ELM's internal functions Tare (chapter “ELM Features“/ “Tare“) or Zero Offset (chapter “ELM Features“/ “ZeroOffset“). The given offset specification of the terminal thus plays practically no further part. The offset deviation of a resistance measurement can change over time, therefore Beckhoff recommends a regular offset compensation or attentive monitoring of the change.

2) The temperature coefficient, i.e. the change in the measured temperature value in relation to the change in the ambient temperature of the terminal, is not constant, as can be seen in the following plot. The value at a sensor temperature of 0 °C is given here as an orientation value. Further values can be taken from the plot.

Measurement uncertainty for Pt500 in the electr. measuring range 2000 Ω, 4-wire connection:

PT500 specification 1:

Measurement uncertainty for Pt500 in the electr. measuring range 2000 Ω, 3-wire connection:

PT500 specification 2:

Measurement uncertainty for Pt500 in the electr. measuring range 5000 Ω, 4-wire connection:

PT500 specification 3:

Measurement uncertainty for Pt500 in the electr. measuring range 5000 Ω, 3-wire connection:

PT500 specification 4: