0x80n0 PAI Settings Ch.[n+1]
0 ≤ n ≤ m, n+1 = Channel number, m+1 = max. No. of channels
80n0:0 | PAI Settings |
| UINT8 | RO | 0x41 (65dec) |
80n0:01 | Interface | Selection of the measurement configuration: | UINT16 | RW | 0x0000 (0dec) |
80n0:02 | Sensor Supply | Sensor supply: | UINT16 | RW | 0x0000 (0dec) |
80n0:03 | IEPE AC Coupling | 0 - Off (DC Coupling) | UINT16 | RW | 0x0000 (0dec) |
80n0:04 | Start Connection Test | Start connection test with rising edge (see section Connection test/switchable connection diagnosis) | BOOLEAN | RW | 0x00 (FALSE) |
80n0:05 | Coldjunction Compensation | 0 - Intern | UINT8 | RW | 0x00 (0dec) |
80n0:06 | Enable Autorange | Autorange (Enable/ Disable) | BOOLEAN | RW | 0x00 (FALSE) |
80n0:07 | IEPE Bias Current | 0 - 0 mA | BIT4 | RW | 0x00 (0dec) |
80n0:08 | Enable Shunt Calibration | Shunt calibration (Enable/ Disable) | BOOLEAN | RW | 0x00 (FALSE) |
80n0:13 | Wire Resistance Compensation | Wire resistance compensation | REAL32 | RW | 0x00000000 (0dec) |
80n0:14 | RTD Element | 0 – None | UINT16 | RW | 0x0000 (0dec) |
80n0:15 | TC Element | 0 – None | UINT16 | RW | 0x0000 (0dec) |
80n0:16 | Filter 1 | Options for filter 1: 0 – None | UINT16 | RW | 0x0000 (0dec) |
80n0:17 | Average Filter 1 No of Samples | Number of samples for user-defined Average Filter 1 | UINT16 | RW | 0x0001 (1dec) |
80n0:18 | Decimation Factor | Factor of the individual sampling rate (min. 1) | UINT16 | RW | 0x0001 (1dec) |
80n0:19 | Filter 2 | Options for filter 2: | UINT16 | RW | 0x0000 (0dec) |
80n0:1A | Average Filter 2 No of Samples | Number of samples for user-defined Average Filter 2 | UINT16 | RW | 0x0001 (1dec) |
80n0:1B | True RMS No. of Samples | Number of samples for "True RMS" calculation (min. 1, max. 1000); | UINT16 | RW | 0x0001 (1dec) |
80n0:1C | Enable True RMS | Activation of "True RMS" calculation | BOOLEAN | RW | 0x00 (FALSE) |
80n0:1D | Enable Frequency Counter | Enable Frequency Counter | BOOLEAN | RW | 0x00 (FALSE) |
80n0:1E | Reset Load Cycle Counter | Reset Load Cycle Counter | BOOLEAN | RW | 0x00 (FALSE) |
80n0:2B | Extended Functions | Options for future functions/settings | UINT16 | RW | 0x0000 (0dec) |
80n0:2C | Integrator/Differentiator | Options: | UINT16 | RW | 0x0000 (0dec) |
80n0:2D | Differentiator Samples Delta | Distance of samples for the differentiation; max. value = 1000; except ELM36xx with max value = 5000 | UINT16 | RW | 0x0001 (1dec) |
80n0:2E | Scaler | Scaling (enum): Optional: | UINT16 | RW | 0x0000 (0dec) |
80n0:2F | Lookup Table Length | Number of taps of the LookUp table | UINT16 | RW | 0x0064 (100dec) |
80n0:32 | Low Range Error | Lowest limit at which the error bit and the error LED are set | INT32 | RW | 0xFF800000 |
80n0:33 | High Range Error | Highest limit at which the error bit and the error LED are set | INT32 | RW | 0x007FFFFF |
80n0:34 | Timestamp Correction | Value for correcting StartNextLatchTime (timestamp of the first sample) | INT32 | RW | 0xFFFB6C20 |
80n0:35 | Low Limiter | Smallest PDO output value | REAL32 | RW | 0xFF7FFFFD |
80n0:36 | High Limiter | Largest PDO output value | REAL32 | RW | 0x7F7FFFFD |
80n0:37 | Bridge Resistance | Bridge resistance | REAL32 | RW | 0x43AF0000 |
80n0:38 | Wire Resistance neg. Supply | Wire Resistance neg. Supply | REAL32 | RW | 0x00000000 (0dec) |
80n0:39 | Wire Resistance pos. Supply | Wire Resistance pos. Supply | REAL32 | RW | 0x00000000 (0dec) |
80n0:3A | Low Load Cycle Limit | Low load cycle limit | REAL32 | RW | 0x00000000 (0dec) |
80n0:3B | High Load Cycle Limit | High load cycle limit | REAL32 | RW | 0x00000000 (0dec) |
80n0:3C | TC CJ Value | Value of the cold junction | REAL32 | RW | 0x00000000 (0dec) |
80n0:40 | Filter 1 Type Info | Filter 1 type information | STRING | RW | N/A |
80n0:41 | Filter 2 Type Info | Filter 2 type information | STRING | RW | N/A |
1) Functionality is only available from FW03
