Measurement ±20 mA, 0…20 mA, 4…20 mA, NE43
ELM310x
Measurement mode
±20 mA
0…20 mA
4…20 mA
3.6…21 mA
(NAMUR NE43)
Measuring range, nominal
‑20…+20 mA
0…20 mA
4…20 mA
4…20 mA
Measuring range, end value (FSV)
20 mA
Measuring range, technically usable
‑21.474…+21.474 mA, overcurrent-protected
0 …21.474 mA, overcurrent-protected
0…21.179 mA, overcurrent-protected
3.6…21 mA, overcurrent-protected
Fuse protection
Internal overload limiting, continuous current resistant
PDO resolution
(including sign)
24 bit
16 bit 2)
24 bit
16 bit 2)
24 bit
16 bit 2)
24 bit
16 bit 2)
PDO LSB (Extended Range)
2.56 nA
655.36 nA
2.56
nA
655.36 nA
2.048
nA
524.288
nA
2.048
nA
524.288
nA
PDO LSB (Legacy Range)
2.384.. nA
610.37.. nA
2.384..
nA
610.37.. nA
1.907..
nA
488.29..
nA
n.a.
Common-mode voltage Ucm
max. ±10V
related to –Uv (internal ground)
Input impedance ±Input 1
(internal resistance)
Differential typ. approx. 150 Ω || 11 nF
CommonMode typ. approx. 40 nF against SGND
2) The analog measurement is always done with 24 bits, in 16-bit mode the eight least significant bits are cut off. For further information see chapter “Commissioning”/ “Process data overview”
Specific data:
Measurement mode
Basic accuracy: Measuring deviation at 23°C, with averaging 3) 6)
< ±0.008 %, < ±80 ppmFSV typ.
< ±1.6 µA typ.
Extended basic accuracy: Measuring deviation at 0…55°C, with averaging 3) 6)
< ±0.0135 %, < ±135 ppmFSV typ.
< ±2.7 µA typ.
Offset/Zero point deviation (at 23°C) 3)
EOffset
< 25 ppmFSV
Gain/scale/amplification deviation (at 23°C) 3)
EGain
< 60 ppm
Non-linearity over the whole measuring range 3)
ELin
< 45 ppmFSV
Repeatability, over 24 h, with averaging 3)
ERep
< 10 ppmFSV
Temperature coefficient 3)
TcGain
< 3 ppm/K typ.
TcOffset
< 1.5 ppmFSV/K typ.
< 30 nA/K typ.
Largest short-term deviation during a specified electrical interference test
Value to follow… ppmFSV typ.
3) Valid for ELM3102-00x0 from HW02; valid for ELM3104-00x0 from HW04; Specifications of predecessor-HW on request.
6) Calculated value according to the equation for estimating usability at the given ambient temperature point or estimating usability over the specified ambient temperature range in operation (Tambient) as stated in chapter "General information on measuring accuracy/measurement uncertainty". In real use, for example at a relatively constant ambient temperature Tambient, a lower (better) achievable uncertainty is attained. A specific calculation according to chapter "General information on measuring accuracy/measurement uncertainty" is recommended, especially if the instrument allows a wider ambient temperature range in operation than 0...55 °C.
ELM3102 (20 ksps)
Noise (without filtering)
ENoise, PtP
< 150 ppmFSV
< 1172 [digits]
< 3.00 µA
ENoise, RMS
< 25 ppmFSV
< 195 [digits]
< 0.50 µA
Max. SNR
> 92.0 dB
Noisedensity@1kHz
< 5.0 Measurement ±20 mA, 0…20 mA, 4…20 mA, NE43 1:
Noise (with 50/60 Hz FIR filter 5))
ENoise, PtP
< 12 ppmFSV
< 94 [digits]
< 0.24 µA
ENoise, RMS
< 2.0 ppmFSV
< 16 [digits]
< 40.0 nA
Max. SNR
> 114.0 dB
Common-mode rejection ratio (without filter), typ.
DC: < 35 nA/V
50/60 Hz: < 200 nA/V
1 kHz: < 2 µA/V
Common-mode rejection ratio (with 50/60 Hz FIR filter 5)), typ.
DC: < 35 nA/V
50/60 Hz: < 10 nA/V
1 kHz: < 10 nA/V
ELM3104 (10 ksps)
ENoise, PtP
< 118 ppmFSV
< 922 [digits]
< 2.36 µA
ENoise, RMS
< 19 ppmFSV
< 148 [digits]
< 0.38 µA
Max. SNR
> 94.4 dB
Noisedensity@1kHz
< 5.37 Measurement ±20 mA, 0…20 mA, 4…20 mA, NE43 2:
ENoise, PtP
< 12 ppmFSV
< 94 [digits]
< 0.24 µA
ENoise, RMS
< 2.0 ppmFSV
< 16 [digits]
< 40.0 nA
Max. SNR
> 114.0 dB
DC: < 35 nA/V
1 kHz: < 2 µA/V
DC: < 35 nA/V
50/60 Hz: < 10 nA/V
1 kHz: < 10 nA/V
5) the 50/60 Hz filter setting must be selected via the settings in the CoE depending on the local mains frequency (50 or 60 Hz); the respective nominal mains frequency then applies as the measuring point for common mode rejection or crosstalk.
Current measurement range ±20 mA
Measurement ±20 mA, 0…20 mA, 4…20 mA, NE43 3:Fig.29: Representation current measurement range ±20 mA
Note: In Extended Range Mode the Underrange/Overrange display in the PDO status has the character of an information/warning when the nominal measuring range is exceeded, i.e. no Error is displayed in the PDO status and LED. If the technical measuring range is also exceeded, Error = TRUE is also displayed. The detection limit for Underrange/Overrange Error can be set in the CoE.
In Legacy Range mode, an Underrange/Overrange event also leads to an Error in the PDO status.
Current measurement range 0…20 mA
Measurement ±20 mA, 0…20 mA, 4…20 mA, NE43 4:Fig.30: Representation current measurement range 0…20 mA
Current measurement range 4…20 mA
Measurement ±20 mA, 0…20 mA, 4…20 mA, NE43 5:Fig.31: Representation current measurement range 4…20 mA
Note: The channel also works in electrically bipolar mode and records negative values in the unipolar measuring ranges (measurement from 0 V, 0 mA, 4 mA, 0 Ω). This enables the channel to provide a precise diagnosis even with signals < 0. In these measuring ranges the limit value for the "Underrange Error" in Extended Mode is -1% of the full scale value (FSV). The limit value can be set in CoE object 0x80n0:32. This avoids irritating error messages if the channel is not wired (e.g. without sensor) or the electrical signal fluctuates slightly around zero. The process data value of 0x00000000 is not undershot.
If the "UnderrangeError" detection is to be set even less sensitive, the magnitude of the negative limit value in the CoE object referred to above can be set even higher.
Current measuring range 3.6…21 mA (NAMUR)
Measurement ±20 mA, 0…20 mA, 4…20 mA, NE43 6:Fig.32: Chart: current measuring range 3.6…21 mA (NAMUR)
Measurement ±20 mA, 0…20 mA, 4…20 mA, NE43 7:
Only Extended Range mode for measuring range 4 mA NAMUR
Legacy Range mode is not available for this measurement range. The Extended Range Mode will be set automatically and although a corresponding write access to the CoE Object 0x8000:2E (Scaler) is not declined, the parameter is not changed.