Specification notes
The following tables with the TC specification apply only when using the internal cold junction. In the ELM334x/ ELM370x, each channel has its own cold junction sensor.
The terminal can also be used with an external cold junction if required. The uncertainties must then be determined for the external cold junction on the application side. The temperature value of the external cold junction must then be communicated to the terminal via the process data for its own calculation. The effect on the TC measurement must then be calculated on the system side.
Thermal stabilization
The specification values for the measurement of the cold junction given here apply only if the following times are adhered to for thermal stabilization at constant ambient temperature
Ambient air in motion
For a constant TC measurement, thermally stable environmental conditions around the ELM terminal are important. Air movements around the terminal with a possibly varying air temperature must be avoided. If these are unavoidable, the separately available ZS9100‑0003 shielding hood should be used for thermal shielding. The following specification was created without a shielding hood in a quiet environment.
Specification notes 1:Fig.91: ZS9100-0003 shielding hood
Wire cross-section on push-in connector
Depending on the temperature gradient, the TC wire supplies heat to the ELM connector or removes heat from it. Even under thermally constant conditions, this leads to an offset deviation. If very accurate measurement is required, this can have a disruptive effect. The above values apply to a wire thickness of 0.2 mm (0.0314 mm²). For thicker wires an offset deviation occurs due to the temperature gradient according to the following diagram:
Specification notes 2:Fig.92: Additional deviation over TC wire cross-section/ diameter of ELM334x-0000 with push-in plug
So the terminal is measuring "too warm" and the specified amount must be subtracted from the measured value accordingly.
The diagram was determined at room temperature (23 °C) and corresponding terminal operational temperature. A deviated room temperature has no appreciable influence, because the terminal temperature adjusts itself accordingly again and the heat gradient remains the same.
Note: Additional measurement deviations related to the TC wire cross-section/diameter are negligibly small for Lemo and Mini-TC connector types.
Specification of the internal cold junction measurement
Measurement mode
Cold junction
ELM3348-0000,
ELM3344-0000
ELM3348-0003,
ELM3344-0003
Basic accuracy: Measuring deviation at 23°C, with averaging 6)
< ±0.5 °C
< ±0.4 °C
Repeatability
ERep
< 25 mK
< 25 mK
Temperature coefficient
Tc
< 7.5 mK/K
< 7.5 mK/K
6) Calculated value according to the equation for estimating usability at the given ambient temperature point or estimating usability over the specified ambient temperature range in operation (Tambient) as stated in chapter "General information on measuring accuracy/measurement uncertainty". In real use, for example at a relatively constant ambient temperature Tambient, a lower (better) achievable uncertainty is attained. A specific calculation according to chapter "General information on measuring accuracy/measurement uncertainty" is recommended, especially if the instrument allows a wider ambient temperature range in operation than 0...55 °C.
In the following, the achievable temperature measurement uncertainty is now specified for the individual TC types, listed by type in ascending order.