Sample program 1 and 2 (offset/gain)
Download TwinCAT 3 project:
Program description / function:
- Calculation of an Offset (correction) value on the basis of the amplitudes of an AC input voltage (DC component ≠ 0) until a deviation of the offset smaller than "wOFFSET_MIN_VAL_REF" (in digits) is achieved.
- Calculation of a Gain correction value by presetting via "nPRESET_MAX_VAL" (in digits).
The configuration of the minimum permitted input frequency, the order of the Gain and Offset calculations, and the direct writing to the CoE directory ("PAI Scaler Settings" object) can be done in this sample program (see Variable declaration).
The following procedure is foreseen:
- Configuration of "bWriteToCoEEnable" = TRUE, i.e. on completion of the calculation of the correction values, they are written to the CoE object "PAI Scaler Settings".
- Set the Klemme to "Extended Range" (0) via the object "PAI Settings Ch. 1" 0x8000:2E in the CoE directory.
- Connect a periodic signal (triangle, sine, square, …) to the Klemme within the selected voltage/current range via the PAI Settings object 0x8000:01 (Interface).
- Start the program by setting "bEnable" to "TRUE".
- The end of the execution is recognizable by the variables "bScaleGainDone" and "bScaleOffsetDone", which are then both TRUE.
- If writing is enabled in the CoE ("bWriteToCoEEnable" = TRUE), the values determined should have been written to the object "PAI Scaler Settings" in the CoE directory (see variable "bError").
- If 6th was executed, the Klemme can be set to "Linear" (1) via the object "PAI Settings Ch. 1" 0x8000:2E in the CoE directory. As a result, the Klemme also performs the correction calculation internally (see: "nScaledSampleVal").
Comments:
Alternatively, the TC3 Analytics Library (TF3510) can be used instead of the function block "FB_GET_MIN_MAX". The function block "FB_ALY_MinMaxAvg_1Ch" can also be used for the determination of the min./max. values. The total calculation can then also be modified in this program by using the mean value provided by this function block.
In the case of the ELM350x/ ELM370x Klemmen , the "PAI Scaler Settings" object is 0x80n6, in addition to which the nOffset and nGain variables can also be directly written without the type conversion (REAL to DINT); scaling of the amplitude correction values with 65536 is also no longer necessary.
Example program 1 and 2 variable declaration:
PROGRAM MAIN
bEnable :BOOL; // Start the code (Offset / Gain adjust)
nPAI_Sample AT%I* :DINT; // Input samples of the measurement value
// Enter your Net-Id here:
userNetId :T_AmsNetId := 'a.b.c.d.x.y';
// Enter EtherCAT device address here:
nUserSlaveAddr :UINT := 1002; // Check, if correct
// Configurations:
fMinFrequencyIn :REAL:=1.5; // Hz
bScalingOrder :BOOL:=FALSE; // TRUE: Start scale offset first
bWriteToCoEEnable :BOOL:=FALSE; // TRUE: Enable writing to CoE
// "Main" State controlling Offset/Gain adjusting:
nMainCal_State :BYTE:=0;
// For CoE Object 0x8005 access:
fb_coe_write :FB_EcCoESdoWrite; // FB for writing to CoE
nSTATE_WRITE_COE :BYTE := 0;
nSubIndex :BYTE;
nCoEIndexScaler :WORD := 16#8005; // Use channel 1
// For ELM3xxx this is 0x8006
nSubIndScalGain :BYTE := 16#02;
nSubIndScalOffs :BYTE := 16#01;
nADSErrId :UDINT; // Copy of ADS-Error ID
fb_get_min_max :FB_GET_MIN_MAX; // Min/Max values needed
// Note: you may also use "FB_ALY_MinMaxAvg_1Ch" of TwinCAT analytics)
// instead; there avg (average values can also be determinated
// Variables used for offset scaling:
nSTATE_SCALE_OFFSET :INT := 0;
bScaleOffsetStart :BOOL := FALSE;
bScaleOffsetDone :BOOL := FALSE;
fOffsetDeviationVal :REAL;
nOFFSET_MIN_VAL_REF :WORD := 200; // Max. limit value for offset
// Variables used for gain scaling:
nSTATE_SCALE_GAIN :INT := 0;
bScaleGainStart :BOOL := FALSE;
bScaleGainDone :BOOL := FALSE;
nPRESET_MAX_VAL :REAL := 3000000; // Target amplitude value
// Variables for evaluating of gain and offset:
nOffset :REAL := 0; // Offset value
nGain :REAL := 1; // Gain value
nScaledSampleVal :REAL;
nDINT_Value :DINT;
fb_trig_bEnable :R_TRIG; // Trigger FB for Enable
bError :BOOL := FALSE; // Evaluate..
END_VARExecution part:
// THIS CODE IS ONLY AN EXAMPLE - YOU HAVE TO CHECK APTITUDE FOR YOUR APPLICATION
// Example program 1 and 2 program code:
// 1. PAI setting of 0x80n0:2E must be "Extended Range" at first
// 2. When writing of scaling values were done, switch to "Linear"
// Calculation of the temporary value (..and use for ScopeView to check)
nScaledSampleVal := nOffset + nGain * DINT_TO_REAL(nPAI_Sample);
// Main-State Procedure:
CASE nMainCal_State OF
0:
fb_trig_bEnable(CLK:=(bEnable AND NOT bError));
IF fb_trig_bEnable.Q THEN // Poll switch or button
// Initialize temporary offset and gain values:
nOffset:= 0;
nGain := 1;
bScaleOffsetStart := bScalingOrder;
bScaleGainStart := NOT bScalingOrder;
fb_get_min_max.nMinFreqInput := fMinFrequencyIn;
nMainCal_State := 10; // Start
END_IF
10:
IF (bScaleGainDone AND NOT bScalingOrder)
OR (bScaleOffsetDone AND bScalingOrder) THEN
bScaleOffsetStart := NOT bScalingOrder;
bScaleGainStart := bScalingOrder;
nMainCal_State := nMainCal_State + 10;
END_IF
20:
IF bScaleGainDone AND bScaleOffsetDone THEN
nMainCal_State :=0; // All done, initalization for next start
END_IF
END_CASE
// ----- Offset scaling (program 1) -----
IF bScaleOffsetStart THEN
CASE nSTATE_SCALE_OFFSET OF
0:
bScaleOffsetDone := FALSE; // Initialization of confirmation flag
// Get min/max values within a period of the signal:
fb_get_min_max(nInputValue:=nScaledSampleVal);
IF fb_get_min_max.bRESULT THEN // Wait if Limit-Values are valid
// Min/Max Values valid, continue..
// calculate current offset deviation:
fOffsetDeviationVal :=
(fb_get_min_max.nMaxVal - ABS((fb_get_min_max.nMaxVal-fb_get_min_max.nMinVal)/2));
// Offset deviation check:
IF ABS(fOffsetDeviationVal) < nOFFSET_MIN_VAL_REF THEN
// Deviation in acceptable range - offset scaling done,
// now write correction value into CoE Object:
nDINT_Value := REAL_TO_DINT(nOffset);
// Initiate writing to CoE:
nSubIndex := nSubIndScalOffs;
nSTATE_WRITE_COE := 10;
nSTATE_SCALE_OFFSET := nSTATE_SCALE_OFFSET + 10;
ELSE
// Calculate new offset value (new by old with deviation)
nOffset := nOffset - fOffsetDeviationVal;
END_IF
END_IF
10:
IF(nSTATE_WRITE_COE = 0) THEN
// Scaling offset done within CoE for the device
bScaleOffsetDone := TRUE;
bScaleOffsetStart := FALSE;
nSTATE_SCALE_OFFSET := 0;
END_IF
END_CASE
END_IF
// ----- Gain scaling (program 2) -----
IF bScaleGainStart THEN
CASE nSTATE_SCALE_GAIN OF
0:
bScaleGainDone := FALSE; // Initialization of confirmation flag
fb_get_min_max(nInputValue:=DINT_TO_REAL(nPAI_Sample));
// Calculate Gain
nGain := nPRESET_MAX_VAL/ABS((fb_get_min_max.nMaxVal-fb_get_min_max.nMinVal)/2);
// ..shift gain value by 16 Bit left and convert to DINT:
nDINT_Value := REAL_TO_DINT(65536 * nGain);
//Due to 'output = gain * input + offset', the offset have to be adapted:
nOffset := nOffset * nGain;
nSubIndex := nSubIndScalGain;
nSTATE_SCALE_GAIN := nSTATE_SCALE_GAIN + 10;
END_IF
10:
IF NOT (nOffset = 0) THEN
// (bScalingOrder is TRUE)
// Initiate writing to CoE (again):
END_IF
END_IF
20:
// Scaling gain done within CoE for the device
bScaleGainStart := FALSE;
bScaleGainDone := TRUE;
nSTATE_SCALE_GAIN := 0; // Set initial state
END_IF
END_CASE
END_IF
IF (nSTATE_WRITE_COE > 0) THEN
IF bWriteToCoEEnable THEN
CASE nSTATE_WRITE_COE OF
10:
// Prepare CoE write access
fb_coe_write(
sNetId:= userNetId,
nSlaveAddr:= nUserSlaveAddr,
nIndex:= nCoEIndexScaler,
bExecute:= FALSE,
tTimeout:= T#1S
nSTATE_WRITE_COE := nSTATE_WRITE_COE + 10;
20:
// Write nDINT_Value to CoE Index "Scaler":
fb_coe_write(
nSubIndex:= nSubIndex,
pSrcBuf:= ADR(nDINT_Value),
cbBufLen:= SIZEOF(nDINT_Value),
bExecute:= TRUE
30:
fb_coe_write();
IF NOT fb_coe_write.bBusy THEN
nSTATE_WRITE_COE := 0;
END_IF
END_CASE
ELSE
END_IF
END_IF
IF(fb_coe_write.bError) AND NOT bError THEN
bError := TRUE;
nADSErrId := fb_coe_write.nErrId;
// CoE write acccess error occured: reset all
nSTATE_WRITE_COE := nMainCal_State := 0;
bScaleOffsetDone := bScaleOffsetStart := FALSE;
bScaleGainDone := bScaleGainStart := FALSE;
END_IF
