Process data overview
Process data outputs
PDO
Member
Data type
Pos.
Meaning
DO Group m Outputs
(m=1..4)
Outputs Channel m
Y1
BIT
0
Make contact X1, X2 → Y1 switch through
Y2
BIT
0
Make contact X1, X2 → Y2 switch through
Y3
BIT
0
Make contact X1, X2 → Y3 switch through
Y4
BIT
0
Make contact X1, X2 → Y4 switch through
Process data inputs
PDO
Member
Data type
Pos.
Meaning
DO Inputs Device
Device Status
Error
BIT
0
Error within the channel, for details see further status bits or DiagnoseHistory
Diag
BIT
4
There is a DiagMessage in the CoE 0x10F3, it can be read from the terminal, e.g. via the TwinCAT Logger
Input cycle counter
BIT2
6, 7
Increments by 1 in each EtherCAT cycle, 0... 3. The controller can monitor this counter. If it does not increment by 1 in a cycle, this indicates a transmission error during this cycle. If necessary, adjust the ShiftTime in Distributed Clocks mode.
WcState
WcState
BIT
0
TRUE: The terminal does not participate in the EtherCAT data exchange, because it is not present or incorrectly configured
FALSE: The terminal regularly participates in the data exchange. Check the validity of the data with the respective status etc.
InputToggle
BIT
0
Toggles 0/1 when the slave sends new data via EtherCAT
PDO
Member
Data type
Pos.
Meaning
InfoData
State
UINT
0
State of the EtherCAT state machine: INIT, PreOP, SafeOP, OP
AdsAddr
netId
AMSNETID
0
ADS address (NetID/port) through which the CoE of the slave can be reached from the application
port
WORD
0
DcOutputShift
DINT
0
~Time between SYNC0 event and reading of the outputs (in ns, only DC mode)
DcInputShift
DINT
0
~Time between SYNC0 event and reading of the inputs (in ns, only DC mode)
Structure of the process data (TwinCAT 3) ELM264x/ ELM274x:
Process data overview 1:Fig.8: PDO of the ELM2644 valid for ELM2642, ELM274x and EL2642, too (according to the number of channels)