Protective earth (PE)
The housings of the ELM/EKM series are made of die-cast zinc and are thus metallic. This results in a need for clarification regarding the use of protective earthing against the risk of electric shock.
Attention: The relevant application standards refer to the surrounding control cabinet/control box as "housing", whereas this documentation refers to the Beckhoff terminal as "housing".
See also chapter "Notes regarding analog equipment - shielding and earth" in this documentation.
Protective earth (PE) 1:
The housing offers the option of an M3 bolted connection for connecting a ring terminal to PE.
The procedure for this is as follows:
Notes on whether a PE connection is necessary in the specific application
Note on protective earth (PE) with regard to analog measurements
The protective earth conductor system is specifically designed for discharging high currents. This may result in significant high-frequency interference, which could adversely affect an analog measuring device if it is/has to be connected to the protective conductor system. In such cases, a strictly star-shaped configuration of the FE and PE systems may be advisable, in order to have as few interference sources as possible on the PE system that are close to the analog measuring system. Ideally, no PE connection should be used at all. However, in this case the installation must comply with the two conditions referred to above, which may necessitate splitting the system into a high-voltage and a low-voltage control cabinet, so that no PE would be required for the latter.