Quick start
Proceed as follows for standard commissioning of the EL9576 with an external resistor (e.g. ZB8110).
  1. Install the EL9576 in the E-bus terminal segment on an EtherCAT coupler, e.g. EK1100 or EK1501.
    The terminal can also be used in exclusive conjunction with an EL9400 for operation without an EtherCAT connection.
  2. For operation the EL9576 requires a supply voltage at connections 2 and 6 (UIN) of the terminal as well as a power supply via the E-Bus.
    The following must be observed:
  3. Set up a correct EtherCAT configuration with the terminal.
    Since the device is present and is electrically reachable, the simplest way of accomplishing this is by scanning the devices.
  4. Activate the EtherCAT master and start the terminal in OP state.
    In the input variables the EL9576 must deliver State=8 and WC=0.
  5. Parameterize the resistor you are using in the CoE settings of the EL9576 according to the data sheet for the resistor.
What if...
the terminal is to be operated without the EtherCAT bus?
-> In this case it is still necessary to connect the Bus Terminal to an EtherCAT Bus Coupler or an EL9400 in order to connect the E-bus power supply. However, the bus coupler does not have to be connected to a fieldbus.