Technical data EL9501, EL9561
Output
EL9501
EL9561
Number of outputs
1
Function
Voltage output, with current limitation
Wiring
2-wire
Output power
15 W
4.8 W
Efficiency Up,in/Up, out
Down control, approx. 90 %
Down control, approx. 75 %
Ground reference
single-ended
potential-free
Max. sampling rate
1 ksps PDO update
Internal sampling rate depending on configured set filter:
- 50 Hz FIR with 625 µs / 1600 Hz
- 60 Hz FIR with 520 µs / 1920 Hz
- otherwise 500 µs / 2000 Hz
Sampling type
simultaneous (1 ch.)
Load
any (ohmic)
Output current
max. 2 A, limited by the output power
Resistant to short circuit
yes
Rate of change, max.
1000 V/sec. 1)
Load type
ohmic, inductive, capacitive up to 1 mF
1) Reduction possible via CoE setting
Output end value (AEW, FSV)
5 V
20 V
Output range, nominal
0.25…5 V
1…20 V
Output range, technically usable 1)
0.25…5.3 V typ.
1.0…21.1 V typ.
PDO resolution
11 bit
PDO LSB
~2.5 mV
~10.0 mV
Output uncertainty 4)
Basic accuracy at 23°C, max. 100 mA
±0.5 %
±25 mV
±0.5 %
±100 mV
additionally for operation in the specified operating temperature range (extended basic accuracy) 2)
±0.5 %
±25 mV
±0.5 %
±100 mV
additionally for operation in the full current range 2 A
±1.2 % 5)
±60 mV
±0.3 % 5)
±60 mV
Noise 3)
FNoise, PtP
<10.0 mV typ.
FNoise, RMS
<1.5 mV typ.
Channel crosstalk
n.a.
Temperature coefficient
105 ppm/K typ.
Output impedance
30 mΩ typ. 5)
1) hardware-dependent, may vary, see output notes in chap. X
2) value corresponds to Tk * 48 K, for operation at -25°C
3) 33 ohm load, 10 V output voltage
4) in nom. output range
5) calculated from "Output uncertainty when operating in the full current range", RImpedance = ΔU / ΔI
Note: To prevent control fluctuations or oscillations, the terminal does not include an internal load compensation circuit to compensate for the load-current-induced drop in the source voltage (source impedance). If load compensation is required, it must be performed externally by the overlying control system based on feedback information. This allows the control loop to be individually adjusted to the circuit.
Current limitation
Measuring range, end value (FSV, full scale value)
2 A
Resolution
approx. 17 mA
Basic accuracy: deviation at 23°C
±3 % 1)
Extended basic accuracy: deviation when operating in the specified operating temperature range
±5 % 1)
1) preliminary
Input voltage Up,in
Output voltage Up,out
Output current
available in EL9501
x
x
x
available in EL9561
x
x
Function
Voltage measurement
Voltage measurement
Current measurement
Wiring
internal
Ground reference
internal
Max. sampling rate
1 ksps PDO rate
ADC acquisition depending on the configured filter:
50 Hz FIR with 625 µs (1600 Hz)
60 Hz FIR with 520 µs (1920 Hz)
otherwise 500 µs (2000 Hz)
Sampling type
multiplexing, with an approx. 50 µs delay between input channels 1..4 2)
Internal resistance
internal
Input filter cut-off frequency
300 kHz (-3 dB, 1st order low-pass)
From HW03: 5 kHz
Settling time
6 µs typ. (0…90 %)
From HW03: 82 µs typ. (0...90 %)
Measuring range, nominal
0…30 V
0…20 V
0…2 A
30 V
20 V
2 A
Measuring range, technically available
0…32.1 V
0…25 V
2.14 A
Recommended operating voltage range
24 (+20/-15 %)
0…20 V
0…20 V
Destruction limit
35 V (+24 V vs. 0 V; long term)
2 kV (+24 V vs. 0 V; surge pulse)
60 V (output+ vs. GND due to reverse voltage)
PDO resolution (including sign)
16 bit
16 bit
16 bit
Conversion method
SAR
SAR
SAR
Measurement uncertainty
Basic accuracy: measurement deviation at 23 °C
±0.2 %
±60 mV
±0.2 %
±40 mV
±1.5 %
±30 mA
Extended basic accuracy: measurement deviation when operating in the specified operating temperature range
±0.5 %
±150 mV
±0.5 %
±100 mV
±2.5 %
±50 mA
62.5 ppm/K typ.
1.875 mV/K
62.5 ppm/K typ.
1.25 mV/K
210 ppm/K
0.42 mA/K
Noise
FNoise, PtP
<5.9 mV typ.
<4.9 mV typ.
<1.8 mA typ.
FNoise, RMS
<0.86 mV typ.
<0.74 mV typ.
<0.27 mA typ.
Channel crosstalk
n.a.
Largest short-term deviation during a specified electrical interference test
±1 %
±1 %
±1 %
1) Preliminary information
2) see explanation in chapter "Commissioning EL9501, EL9561"
General
EL9501
EL9561
Power supply
Internal logic via Ebus
Operation Power contacts Up required for power supply function
Input voltage Up
24 V DC (-15 % / +20 %)
Distributed clocks
no
Electrical isolation power supply/E-bus
functional separation 707 V DC (type test)
according to basic insulation to EN 61010, test voltage 2,000 V, 7 s, production test 1)
Electrical isolation Up,in/Up, out
Current consumption via E-bus
80 mA typ.
Current consumption of power contacts
5 mA + output power/output voltage
10 mA + output power/output voltage
Min. EtherCAT cycle time
50 µs
Diagnostics in the process image
yes
Support NoCoEStorage
yes
Special features
Constant voltage output (CV),
2 output ranges 5/20 V, output diagnostics
2 output ranges 5/20 V, output diagnostics,
electrical isolation Up,in/Up, out
Installation
on 35 mm mounting rail, conforms to EN 60715
Weight
approx. 55 g
Permissible ambient temperature range during operation
-25…+60 °C
Permissible ambient temperature range during storage
-40…+85 °C
Relative humidity
95 %, no condensation
EMC immunity/emission
conforms to EN 61000-6-2 / EN 61000-6-4
Vibration/shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Protection rating
IP20
Installation position
variable
Approvals/markings*)
CE, UKCA, EAC
1) the insulation coordination complies with the technical specifications according to EN 61010-1, chapter K. 3, working voltage max. 300 V, pollution degree 2