Standard objects
Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
| Index (hex) | Name | Meaning | Data type | Flags | Default |
| 1000:0 | Device type | Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | 0x039A1389 (60429193 dec) |
Index 1008 Device name
| 1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | EL9227 |
Index 1009 Hardware version
| 1009:0 | Hardware version | Hardware version of the EtherCAT slave | STRING | RO |
Index 100A Software version
| 100A:0 | Software version | Firmware version of the EtherCAT slave | STRING | RO |
Index 1018 Identity
| 1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
| 1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
| 1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x240B3052 (604713042dec) |
| 1018:03 | Revision | Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description | UINT32 | RO | 0x00000000 (0dec) |
| 1018:04 | Serial number | Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 | UINT32 | RO | 0x00000000 (0dec) |
| 10F0:0 | Backup parameter handling | Information for standardized loading and saving of backup entries | UINT8 | RO | 0x01 (1dec) |
| 10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave | UINT32 | RO | 0x00000000 (0dec) |
Index 1A00 OCP TxPDO-Map Inputs Ch.1
| 1A00:0 | OCP TxPDO-Map Inputs Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x10 (16dec) |
| 1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x01 (Enabled)) | UINT32 | RO | 0x6000:01, 1 |
| 1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x02 (Tripped)) | UINT32 | RO | 0x6000:02, 1 |
| 1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x03 (Short Circuit)) | UINT32 | RO | 0x6000:03, 1 |
| 1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x04 (Overload)) | UINT32 | RO | 0x6000:04, 1 |
| 1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x05 (Hardware Protection)) | UINT32 | RO | 0x6000:05, 1 |
| 1A00:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x06 (Overvoltage)) | UINT32 | RO | 0x6000:06, 1 |
| 1A00:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x07 (Undervoltage)) | UINT32 | RO | 0x6000:07, 1 |
| 1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x08 (Current Level Warning)) | UINT32 | RO | 0x6000:08, 1 |
| 1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x09 (Cool Down Lock)) | UINT32 | RO | 0x6000:09, 1 |
| 1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0A (Disabled By Switch)) | UINT32 | RO | 0x6000:0A, 1 |
| 1A00:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0B (Disabled By DI)) | UINT32 | RO | 0x6000:0B, 1 |
| 1A00:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0C (Disabled By Output)) | UINT32 | RO | 0x6000:0C, 1 |
| 1A00:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0D (Diag)) | UINT32 | RO | 0x6000:0D, 1 |
| 1A00:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0E (TxPDO State)) | UINT32 | RO | 0x6000:0E 1 |
| 1A00:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0F (Input cycle counter)) | UINT32 | RO | 0x6000:0F, 2 |
| 1A00:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x11 (State Device Switch)) | UINT32 | RO | 0x6000:11, 1 |
| 1A00:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x12 (State Digital Input)) | UINT32 | RO | 0x6000:12, 1 |
| 1A00:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x13 (Error)) | UINT32 | RO | 0x6000:13, 1 |
| 1A00:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x14 (State Reset)) | UINT32 | RO | 0x6000:14, 1 |
| 1A00:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x15 (State Switch)) | UINT32 | RO | 0x6000:15, 1 |
| 1A00:15 | SubIndex 021 | 21. PDO Mapping entry (11 bits align) | UINT32 | RO | 0x0000:00, 11 |
| 1A00:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x21 (Load)) | UINT32 | RO | 0x6000:21, 16 |
| 1A00:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x22 (Current)) | UINT32 | RO | 0x6000:22, 16 |
| 1A00:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x23 (Voltage In)) | UINT32 | RO | 0x6000:23, 16 |
| 1A00:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x24 (Voltage Out)) | UINT32 | RO | 0x6000:24, 16 |
Index 1C00 Sync manager type
| 1C00:0 | Sync manager type | Using the Sync Managers | UINT8 | RO | 0x04 (4dec) |
| 1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dec) |
| 1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dec) |
| 1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dec) |
| 1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dec) |
Index 1C12 RxPDO assign
| 1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RO | 0x02 (2dec) |
| 1C12:01 | Subindex 001 | 1. allocated RxPDO (contains the index of the associated RxPDO mapping object) | UINT16 | RO | 0x1600 (5632dec) |
| 1C12:02 | Subindex 002 | 2. allocated RxPDO (contains the index of the associated RxPDO mapping object) | UINT16 | RO | 0x1601 (5633dec) |
Index 1C13 TxPDO assign
| 1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RO | 0x02 (2dec) |
| 1C13:01 | Subindex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RO | 0x1A00 (6656dec) |
| 1C13:02 | Subindex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RO | 0x1A02 (6658dec) |
Index 1C33 SM input parameter
| 1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
| 1C33:01 | Sync mode | Current synchronization mode:
 | UINT16 | RW | 0x0000 (0dec) |
| 1C33:02 | Cycle time | Cycle time (in ns):
 | UINT32 | RW | 0x000F4240 (1000000dec) |
| 1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000384 (900dec) |
| 1C33:04 | Sync modes supported | Supported synchronization modes:
 | UINT16 | RO | 0x8001 (32769dec) |
| 1C33:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x00002710 (10000dec) |
| 1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
| 1C33:07 | Minimum delay time |
| 1C33:08 | Command |
 The entries 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
| 1C33:09 | Maximum delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000384 (900dec) |
| 1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
| 1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
| 1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
| 1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index 160n OCP RxPDO map inputs (for n = 0, ch.1; n = 1, ch. 2)
| 160n:0 | OCP RxPDO-Map Inputs | PDO Mapping TxPDO 1 | UINT8 | RO | 0x03 (16dec) |
| 160n:01 | SubIndex 001 | 1. PDO Mapping entry object | UINT32 | RO | 0x70n0:01, 1 |
| 160n:02 | SubIndex 002 | 2. PDO Mapping entry object | UINT32 | RO | 0x70n0:02, 1 |
| 160n:03 | SubIndex 003 | 3. PDO Mapping entry (14 bits align) | UINT32 | RO | 0x00n0:00, 14 |
Index 1C32 SM output parameter (part 1)
| 1C32:0 | SM output parameter | Synchronization parameters for the outputs | UINT8 | RO | 0x20 (32dec) |
| 1C32:01 | Sync mode | Current synchronization mode:
 | UINT16 | RW | 0x0001 (1dec) |
| 1C32:02 | Cycle time | Cycle time (in ns):
| 1C32:03 | Shift time | Time between SYNC0 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
| 1C32:04 | Sync modes supported | Supported synchronization modes:
 | UINT16 | RO | 0x0C07 (3079dec) |
| 1C32:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x0003D090 (250000dec) |
| 1C32:06 | Calc and copy time | Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
| 1C32:07 | Minimum delay time | Min. time between SYNC1 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
Index 1C32 SM output parameter (part 2)
| 1C32:08 | Command |
 Entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:07, 0x1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
| 1C32:09 | Maximum delay time | Time between SYNC1 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
| 1C32:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
| 1C32:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
| 1C32:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
| 1C32:14 | Frame repeat time |
 | UINT32 | RW | 0x00000000 (0dec) |
| 1C32:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index F009 Password protection
| F009:0 | Password protection | Password protection | UINT32 | RW | 0x00000000 (0dec) |
Index 1800 OCP TxPDO-Par Inputs Ch.1
| 1800:0 | OCP TxPDO-Par Inputs Ch. 1 | PDO Parameter TxPDO | UINT8 | RO | 0x06 (6dec) |
| 1800:06 | Exclude TxPDOs | Here the TxPDOs (index of the TxPDO mapping objects) are specified, which may not be transferred together with the specified TxPDO. | OCTET-STRING[2] | RO | 01 1A |
Index 1801 OCP TxPDO-Par Inputs Ch.1 Compact
| 1801:0 | OCP TxPDO-Par Inputs Ch. 1 | PDO Parameter TxPDO | UINT8 | RO | 0x06 (6dec) |
| 1801:06 | Exclude TxPDOs | Here the TxPDOs (index of the TxPDO mapping objects) are specified, which may not be transferred together with the specified TxPDO. | OCTET-STRING[2] | RO | 00 1A |
Index 1802 OCP TxPDO-Par Inputs Ch.2
| 1802:0 | OCP TxPDO-Par Inputs Ch. 2 | PDO Parameter TxPDO | UINT8 | RO | 0x06 (6dec) |
| 1802:06 | Exclude TxPDOs | Here the TxPDOs (index of the TxPDO mapping objects) are specified, which may not be transferred together with the specified TxPDO. | OCTET-STRING[2] | RO | 03 1A |
Index 1803 OCP TxPDO-Par Inputs Ch.2 Compact
| 1803:0 | OCP TxPDO-Par Inputs Ch. 2 | PDO Parameter TxPDO | UINT8 | RO | 0x06 (6dec) |
| 1803:06 | Exclude TxPDOs | Here the TxPDOs (index of the TxPDO mapping objects) are specified, which may not be transferred together with the specified TxPDO. | OCTET-STRING[2] | RO | 02 1A |
| F000:0 | Modular device profile | General information for the modular device profile | UINT8 | RO | 0x02 (2dec) |
| F000:01 | Module index distance | Index distance of the objects of the individual channels | UINT16 | RO | 0x0010 (16dec) |
| F000:02 | Maximum number of modules | Number of channels | UINT16 | RO | 0x0002 (2dec) |
Index F010 Module list
| F010:0 | Module list | Max. Subindex | UINT8 | RW | 0x02 (2dec) |
| F010:01 | SubIndex 001 | OCP Profile 922 | UINT32 | RW | 0x0000039A (922dec) |
Index 100B Bootloader version
| 100B:0 | Bootloader version | Bootloader version of the EtherCAT slave | STRING | RO | N/A |
Index 1A01 OCP TxPDO-Map Inputs Ch.1 Compact
| 1A01:0 | OCP TxPDO-Map Inputs Ch.1 Compact | PDO Mapping TxPDO 2 | UINT8 | RO | 0x10 (16dec) |
| 1A01:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x01 (Enabled)) | UINT32 | RO | 0x6000:01, 1 |
| 1A01:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x02 (Tripped)) | UINT32 | RO | 0x6000:02, 1 |
| 1A01:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x03 (Short Circuit)) | UINT32 | RO | 0x6000:03, 1 |
| 1A01:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x04 (Overload)) | UINT32 | RO | 0x6000:04, 1 |
| 1A01:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x05 (Hardware Protection)) | UINT32 | RO | 0x6000:05, 1 |
| 1A01:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x06 (Overvoltage)) | UINT32 | RO | 0x6000:06, 1 |
| 1A01:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x07 (Undervoltage)) | UINT32 | RO | 0x6000:07, 1 |
| 1A01:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x08 (Current Level Warning)) | UINT32 | RO | 0x6000:08, 1 |
| 1A01:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x09 (Cool Down Lock)) | UINT32 | RO | 0x6000:09, 1 |
| 1A01:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0A (Disabled By Switch)) | UINT32 | RO | 0x6000:0A, 1 |
| 1A01:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0B (Disabled By DI)) | UINT32 | RO | 0x6000:0B, 1 |
| 1A01:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0C (Disabled By Output)) | UINT32 | RO | 0x6000:0C, 1 |
| 1A01:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0D (Diag)) | UINT32 | RO | 0x6000:0D, 1 |
| 1A01:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0E (TxPDO State)) | UINT32 | RO | 0x6000:0E 1 |
| 1A01:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x0F (Input cycle counter)) | UINT32 | RO | 0x6000:0F, 2 |
| 1A01:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x11 (State Device Switch)) | UINT32 | RO | 0x6000:11, 1 |
| 1A01:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x12 (State Digital Input)) | UINT32 | RO | 0x6000:12, 1 |
| 1A01:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x13 (Error)) | UINT32 | RO | 0x6000:13, 1 |
| 1A01:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x14 (State Reset)) | UINT32 | RO | 0x6000:14, 1 |
| 1A01:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6000 (Inputs Ch.1), entry 0x15 (State Switch)) | UINT32 | RO | 0x6000:15, 1 |
| 1A01:15 | SubIndex 021 | 21. PDO Mapping entry (11 bits align) | UINT32 | RO | 0x0000:00, 11 |
Index 1A02 OCP TxPDO-Map Inputs Ch.2
| 1A02:0 | OCP TxPDO-Map Inputs Ch.2 | PDO Mapping TxPDO 3 | UINT8 | RO | 0x10 (16dec) |
| 1A02:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x01 (Enabled)) | UINT32 | RO | 0x6010:01, 1 |
| 1A02:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x02 (Tripped)) | UINT32 | RO | 0x6010:02, 1 |
| 1A02:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x03 (Short Circuit)) | UINT32 | RO | 0x6010:03, 1 |
| 1A02:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x04 (Overload)) | UINT32 | RO | 0x6010:04, 1 |
| 1A02:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x05 (Hardware Protection)) | UINT32 | RO | 0x6010:05, 1 |
| 1A02:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x06 (Overvoltage)) | UINT32 | RO | 0x6010:06, 1 |
| 1A02:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x07 (Undervoltage)) | UINT32 | RO | 0x6010:07, 1 |
| 1A02:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x08 (Current Level Warning)) | UINT32 | RO | 0x6010:08, 1 |
| 1A02:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x09 (Cool Down Lock)) | UINT32 | RO | 0x6010:09, 1 |
| 1A02:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0A (Disabled By Switch)) | UINT32 | RO | 0x6010:0A, 1 |
| 1A02:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0B (Disabled By DI)) | UINT32 | RO | 0x6010:0B, 1 |
| 1A02:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0C (Disabled By Output)) | UINT32 | RO | 0x6010:0C, 1 |
| 1A02:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0D (Diag)) | UINT32 | RO | 0x6010:0D, 1 |
| 1A02:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0E (TxPDO State)) | UINT32 | RO | 0x6010:0E 1 |
| 1A02:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0F (Input cycle counter)) | UINT32 | RO | 0x6010:0F, 2 |
| 1A02:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x11 (State Device Switch)) | UINT32 | RO | 0x6010:11, 1 |
| 1A02:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x12 (State Digital Input)) | UINT32 | RO | 0x6010:12, 1 |
| 1A02:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x13 (Error)) | UINT32 | RO | 0x6010:13, 1 |
| 1A02:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x14 (State Reset)) | UINT32 | RO | 0x6010:14, 1 |
| 1A02:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x15 (State Switch)) | UINT32 | RO | 0x6010:15, 1 |
| 1A02:15 | SubIndex 021 | 21. PDO Mapping entry (11 bits align) | UINT32 | RO | 0x0000:00, 11 |
| 1A02:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x21 (Load)) | UINT32 | RO | 0x6010:21, 16 |
| 1A02:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x22 (Current)) | UINT32 | RO | 0x6010:22, 16 |
| 1A02:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x23 (Voltage In)) | UINT32 | RO | 0x6010:23, 16 |
| 1A02:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x24 (Voltage Out)) | UINT32 | RO | 0x6010:24, 16 |
Index 1A03 OCP TxPDO-Map Inputs Ch.2 Compact
| 1A03:0 | OCP TxPDO-Map Inputs Ch.2 Compact | PDO Mapping TxPDO 4 | UINT8 | RO | 0x10 (16dec) |
| 1A03:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x01 (Enabled)) | UINT32 | RO | 0x6010:01, 1 |
| 1A03:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x02 (Tripped)) | UINT32 | RO | 0x6010:02, 1 |
| 1A03:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x03 (Short Circuit)) | UINT32 | RO | 0x6010:03, 1 |
| 1A03:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x04 (Overload)) | UINT32 | RO | 0x6010:04, 1 |
| 1A03:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x05 (Hardware Protection)) | UINT32 | RO | 0x6010:05, 1 |
| 1A03:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x06 (Overvoltage)) | UINT32 | RO | 0x6010:06, 1 |
| 1A03:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x07 (Undervoltage)) | UINT32 | RO | 0x6010:07, 1 |
| 1A03:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x08 (Current Level Warning)) | UINT32 | RO | 0x6010:08, 1 |
| 1A03:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x09 (Cool Down Lock)) | UINT32 | RO | 0x6010:09, 1 |
| 1A03:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0A (Disabled By Switch)) | UINT32 | RO | 0x6010:0A, 1 |
| 1A03:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0B (Disabled By DI)) | UINT32 | RO | 0x6010:0B, 1 |
| 1A03:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0C (Disabled By Output)) | UINT32 | RO | 0x6010:0C, 1 |
| 1A03:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0D (Diag)) | UINT32 | RO | 0x6010:0D, 1 |
| 1A03:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0E (TxPDO State)) | UINT32 | RO | 0x6010:0E 1 |
| 1A03:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x0F (Input cycle counter)) | UINT32 | RO | 0x6010:0F, 2 |
| 1A03:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x11 (State Device Switch)) | UINT32 | RO | 0x6010:11, 1 |
| 1A03:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x12 (State Digital Input)) | UINT32 | RO | 0x6010:12, 1 |
| 1A03:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x13 (Error)) | UINT32 | RO | 0x6010:13, 1 |
| 1A03:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x14 (State Reset)) | UINT32 | RO | 0x6010:14, 1 |
| 1A03:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6010 (Inputs Ch.2), entry 0x15 (State Switch)) | UINT32 | RO | 0x6010:15, 1 |
| 1A03:15 | SubIndex 021 | 21. PDO Mapping entry (11 bits align) | UINT32 | RO | 0x0000:00, 11 |
Index F008 Code word
| F008:0 | Code word | reserved | UINT32 | RW | 0x00000000 (0dec) |
