Configuration data
Index 80n0 Settings (for n = 0, Ch.1; n = 1, Ch. 2)
80n0:0 | Settings | Max. Subindex | UINT8 | RO | 0x1A (26dec) |
80n0:11 | Nominal current | Nominal current (set fuse value), IN | UINT8 | RW | (0x80nF:17) |
80n0:12 | Characteristic | Characteristic curve: Indicates the time after which the system is switched off at which current level. | UINT8 | RW | 0x01 (1dec) |
80n0:13 | Current-Level Warning | Prewarning: Indicates the current value from which a prewarning is issued. | UINT16 | RW | 0x005A (90dec) |
80n0:14 | Fuse Init State | Initialization state: Describes the state of the outputs which they should have when the voltage is applied again after a voltage interruption. Off, On or return to the last state when the voltage was still applied. | UINT8 | RW | 0x02 (2dec) |
80n0:15 | Input Functions (DI & Switch) | Input functions (digital input & LED button): Describes the function of the digital input and the LED button which should be executed if required. It describes the behavior, so to speak. Reset only, power on/off only, reset and power on/off or disabled. | UINT8 | RW | 0x02 (2dec) |
80n0:16 | Overvoltage Behaviour | Overvoltage behavior: Describes how the outputs should respond when an overvoltage (>32 V DC, hysteresis 2 V) is present at the input. Tripping and do not switch on again automatically when the overvoltage has been resolved, or tripping with auto reset and automatic switching on again when the overvoltage has been resolved. | UINT8 | RW | 0x01 (1dec) |
80n0:17 | Undervoltage level | Undervoltage threshold: This is the value from which an undervoltage (adjustable from 17 to 24 V DC, hysteresis 1 V) is displayed. | UINT8 | RW | 0xAA (170dec) |
80n0:18 | Reverse Current Filter | Reverse feed filter: Describes when the system is switched off if the voltage at the output is 1 V higher than at the input. | UINT8 | RW | 0x01 (1dec) |
80n0:19 | Switch Programming Control | LED button programming option: Indicated whether the nominal current of programmable terminals can be programmed via the LED button. Disable: Locked and not allowed. Only one query of the nominal current is possible! Enable: Programming possible | UINT8 | RW | --- |
80n0:1A | Switch On Channel Delay | Channel switch-on delay: Describes the behavior of the switch-on delay from channel 2 to 1. Off: No delay from channel 2 to 1. | UINT16 | RW | 0x0000 (1dec) |
Index 80n1 manual characteristic settings (for n = 0, ch.1; n=1, ch. 2)
80n1:0 | Manual Characteristic Settings | Max. Subindex | UINT8 | RO | 0x1A (26dec) |
80n1:01 | Time value (1.1 * In) | Describes the tripping time in ms, when triggering occurs at 1.1 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:02 | Time value (1.2 * In) | Describes the tripping time in ms, when triggering occurs at 1.2 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:03 | Time value (1.3 * In) | Describes the tripping time in ms, when triggering occurs at 1.3 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:04 | Time value (1.4 * In) | Describes the tripping time in ms, when triggering occurs at 1.4 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:05 | Time value (1.5 * In) | Describes the tripping time in ms, when triggering occurs at 1.5 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:06 | Time value (1.6 * In) | Describes the tripping time in ms, when triggering occurs at 1.6 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:07 | Time value (1.7 * In) | Describes the tripping time in ms, when triggering occurs at 1.7 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:08 | Time value (1.8 * In) | Describes the tripping time in ms, when triggering occurs at 1.8 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:09 | Time value (1.9 * In) | Describes the tripping time in ms, when triggering occurs at 1.9 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:0A | Time value (2.0 * In) | Describes the tripping time in ms, when triggering occurs at 2 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:0B | Time value (2.2 * In) | Describes the tripping time in ms, when triggering occurs at 2.2 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:0C | Time value (2.4 * In) | Describes the tripping time in ms, when triggering occurs at 2.4 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:0D | Time value (2.6 * In) | Describes the tripping time in ms, when triggering occurs at 2.6 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:0E | Time value (2.8 * In) | Describes the tripping time in ms, when triggering occurs at 2.8 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:0F | Time value (3.0 * In) | Describes the tripping time in ms, when triggering occurs at 3 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:10 | Time value (3.25 * In) | Describes the tripping time in ms, when triggering occurs at 3.25 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:11 | Time value (3.5 * In) | Describes the tripping time in ms, when triggering occurs at 3.5 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:12 | Time value (3.75 * In) | Describes the tripping time in ms, when triggering occurs at 3.75 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:13 | Time value (4.0 * In) | Describes the tripping time in ms, when triggering occurs at 4 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:14 | Time value (4.33 * In) | Describes the tripping time in ms, when triggering occurs at 4.33 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:15 | Time value (4.66 * In) | Describes the tripping time in ms, when triggering occurs at 4.66 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:16 | Time value (5.0 * In) | Describes the tripping time in ms, when triggering occurs at 5 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:17 | Time value (5.5 * In) | Describes the tripping time in ms, when triggering occurs at 5.5 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:18 | Time value (6.0 * In) | Describes the tripping time in ms, when triggering occurs at 6 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:19 | Time value (7.0 * In) | Describes the tripping time in ms, when triggering occurs at 7 times IN. | UINT16 | RW | 0x0000 (0dec) |
80n1:1A | Time value (9.0 * In) | Describes the tripping time in ms, when triggering occurs at 9 times IN. | UINT16 | RW | 0x0000 (0dec) |
Index 80n0 DIG Safe State Active Ch.n
(n=2 for Ch.1; n=3 for Ch.2
Index (hex) | Name | Meaning | Data type | Flags | Default value |
80n0:0 | DIG Safe State Active | Maximum subindex | UINT8 | RO | 0x01 (1dec) |
80n0:01 | Active | Enabling of the output state defined in index 0x80n1:01 in case of a bus error 0: output retains its current state. | BOOLEAN | RW | 0x01 (1dec) |
Index 80n1 DIG Safe State Value Ch.n
80n1:0 | DIG Safe State Value | Maximum subindex | UINT8 | RO | 0x01 (1dec) |
80n1:01 | Value | Defines the state of the output in case of a bus error: 0: output off | BOOLEAN | RW | 0x00 (0dec) |