Calibration and scaling
Vendor calibration, index 0x80B0:08, 0x80BF:01, 0x80BF:02
The vendor calibration is enabled in the factory setting. It can be disabled via
Index 0x80B0:08 "Enable vendor calibration".
The parameterization of the vendor calibration is carried out via the indices: 0x80BF:01 (offset vendor calibration) and 0x80BF:02 (gain vendor calibration).
Calibration and scaling 1:
Output error with disabled vendor calibration
  • If you use the user calibration, it may be a good idea to disable the vendor calibration.
  • The vendor reserves the right to carry out the basic calibration of the terminals. Therefore, the vendor calibration cannot be changed.
User calibration, index 0x80B0:07, 0x80B0:17, 0x80B0:18
The user calibration is disabled in the factory setting. It can be enabled via
Index 0x80B0:07 "Enable user calibration".
Parameterization is carried out via the indices:
0x80B0:17 (offset user calibration) and 0x80B0:18 (gain user calibration).
Notice
The user calibration affects the measuring range monitoring.
Incorrect calibration coefficients can lead to the Status bits and Status LEDs no longer behaving as expected; see Output range monitoring.
User scale, index 0x80B0:01, 0x80B0:11, 0x80B0:12
The user scale is disabled in the factory setting. It can be enabled via
index 0x80B0:01 "Enable user scale".
0x80B0:11 (offset user scale and 0x80B0:12 (gain user scale).
Correction calculation
The terminal continuously accepts the setpoints from the EtherCAT process data, converts them according to the settings and passes them on to the internal DAC (digital-analog converter), which forms the electrical output signal (see Data stream).
Calibration / scaling
Status
Conversion
Meaning
User scale (user calibration)
active:
0x80B0:01 = TRUE
YSC= YS1 x AS x 2-16 + BS
YSC: Value after user scale
YS1: Value before user scale
AS: Gain user scale (0x80B0:12)
BS: Offset user scale (0x80B0:11)
Disabled (default):
0x80B0:01 = FALSE
YSC = YS1
Vendor calibration
active (default):
0x80B0:08 = TRUE
XDAC = YSC x AH x 2-16 + BH
XDAC: Output value with active vendor calibration with:
BH: Offset vendor calibration (0x80BF:01)
AH: Gain vendor calibration (0x80BF:02)
User calibration
active:
0x80A0:07 = TRUE
XDAC = YSC x AA x 2-20 + BA
XDAC: Output value with active user calibration with:
BA: Offset user calibration (0x80B0:15)
AA: Gain user calibration (0x80B0:16)
No calibration
0x80B0:01 = FALSE,
0x80B0:08 = FALSE,
0x80A0:07 = FALSE
XDAC = YSC
XDAC: Output value if vendor and user calibration are disabled.