Feedback system: Hall sensors only
Step 1: Optimization of the velocity controller
1. Set the CoE parameter 8010:17 "Position loop proportional gain" to zero.
The position controller is disabled.
Interference of the position controller with the velocity controller is prevented.
2. Gradually reduce the integral component 8010:5A "Velocity loop integral time (voltage mode)".
At the same time, gradually increase the proportional component 8010:5B "Velocity loop proportional gain (voltage mode)".
While doing so, observe the actual value of the velocity and the actual value and the setpoint of the position.
From a certain point, the actual value of the velocity begins to oscillate or the difference between the actual value and the setpoint of the position increases.
3. Reduce the integral and proportional components by 20%. The 20% serves as a control reserve for abrupt movements.
4. If the actual value of the velocity overshoots, reduce 8010:5C "Velocity loop voltage feed forward gain (voltage mode)".
The velocity controller is optimized.
Step 2: Optimization of the position controller
Requirement: The velocity controller is optimized.
1. Gradually increase the proportional component 8010:17 "Position loop proportional gain" so that the position difference oscillates around the value zero and the setpoint specification of the position is followed appropriately.
The position controller is optimized.