Switching signal from a digital input of the EL7411
This chapter describes the configuration exemplarily for the digital input "Input 1".
- 1. In the Solution Explorer:
click on NC axis > "ENC", open the tab "Parameters" and expand the section "Homing".
- 2. Set the parameter "Reference Mode" to "Homing Sensor Only (PLC cam or digital input 1..8)".
- 3. Set the parameter "Homing Sensor Source" to "Digital Input 1 (Active High), device depending mapping".
- 4. In the Solution Explorer:
click on the EL7411, open the tab "Process Data", select the Sync Manager 3 "Inputs" and activate the PDO Assignment 0x1A10.
- The process data object "DI Inputs" is activated.
- 5. EL7411 > "DI Inputs" > "Input 1" right click, "Change Link" select.
- A dialog box appears.
- 6. click on "All Types", select the variable "nState8" and confirm with "OK".
- 7. Confirm with "OK".
- 8. Add the library "Tc2_MC2" to the PLC project:
Navigate to PLC > "References", right click, "Add Library..."
- 9. Insert an instance of the function block "MC_Home" from the library "Tc2_MC2" in the PLC.
Do not connect the input "bCalibrationCam".
- You can start homing with a positive edge at input "Execute".