Configuration data
Index 8000 FB Settings
8000:0 | FB Settings | Observer settings | UINT8 | RO | 0x16 (22dec) |
8000:11 | Device type | Description of available feedback profiles (incremental encoder and Hall sensor) | UINT32 | RW | 0x00000605 (1541dec) |
8000:14 | Observer bandwidth | Bandwidth of the speed observer [Hz] Typical value range: 200..500 Hz | UINT16 | RW | 0x00C8 (200dec) |
8000:15 | Observer feed-forward | Load ratio [%] 100% = load-free 50% = mass moments of inertia of input and output are equal
Pre-control for velocity measurement. | UINT8 | RW | 0x00 (0dec) |
8000:16 | Sub-increment bits | Bitwise shift to left from target and actual position and following error | UINT8 | RW | 0x00 (0dec) |
Index 8001 FB Touch probe Settings
Index (hex) | Name | Meaning | Data type | Flags | Default | |
8001:0 | FB Touch probe Settings |
| UINT8 | RO | 0x12 (18dec) | |
8001:11 | Touch probe 1 source | permitted values: | INT16 | RW | 0x0001 (1dec) | |
1 | Touch probe input 1 | |||||
2 | Hardware zero impulse | |||||
8001:12 | Touch probe 2 source | permitted values: | INT16 | RW | 0x0001 (1dec) | |
Index 8008 FB Settings ENC
8008:0 | FB Settings ENC |
| UINT8 | RO | 0x13 (19dec) | |
8008:01 | Invert feedback direction | Inversion of the encoder counting direction. Adjusted by the Scan Feedback feature. | BOOLEAN | RW | 0x00 (0dec) | |
8008:02 | Enable power supply | Enablement of the encoder supply voltage | BOOLEAN | RW | 0x00 (0dec) | |
8008:05 | Enable ENC C input | Enablement of the C-input of the terminal for the evaluation of the C-track on the incremental encoder | BOOLEAN | RW | 0x01 (1dec) | |
8008:11 | Supply voltage output | Voltage level of the encoder supply [mV] Typical value range: 2..24 V | UINT32 | RW | 0x00001388 (5000dec) | |
8008:12 | Encoder type | Definition of encoder signal types | UINT16 | RW | 0x0004 (4dec) | |
0 | disabled | |||||
1 | RS422 differential | |||||
2 | TTL single ended | |||||
3 | HTL differential | |||||
4 | HTL single ended | |||||
5 | RS422 differential – high impedance input | |||||
6 | TTL single ended – input filters disabled | |||||
7 | open collector | |||||
8008:13 | Encoder Increments per Revolution | Resolution of the encoder after 4-fold evaluation | UINT32 | RW | 0x00001000 (4096dec) |
Index 800A FB Settings Hall
800A:0 | FB Settings Hall | Settings for the Hall sensors | UINT8 | RO | 0x14 (20dec) | |
800A:02 | Enable power supply | Enablement of the Hall sensor supply voltage | BOOLEAN | RW | 0x00 (0dec) | |
800A:05 | Enable extrapolation | Extrapolation of the measured values of the Hall sensor. This does not improve the physical resolution. | BOOLEAN | RW | 0x00 (0dec) | |
800A:11 | Supply voltage output | Voltage level of the Hall sensor supply [mV] Typical value range: 2…24 V | UINT32 | RW | 0x00001388 (5000dec) | |
800A:12 | phasing | Arrangement of the Hall sensors. Determined by the Scan Feedback function. See chapter Scan Feedback. | UINT8 | RW | 0x01 (1dec) | |
0 | A-B: 60° / B-C: 60° | |||||
1 | A-B: 120° / B-C: 120° | |||||
2 | A-B: 240° / B-C: 240° | |||||
3 | A-B: 300° / B-C: 300° | |||||
4 | A-B: 60° / B-C: 240° | |||||
5 | A-B: 120° / B-C: 300° | |||||
6 | A-B: 240° / B-C: 60° | |||||
7 | A-B: 300° / B-C: 120° | |||||
800A:13 | Hall commutation adjust | Commutation offset of the Hall sensors in 60° increments. Determined by the Scan Feedback function. See chapter Scan Feedback. | UINT8 | RW | 0x00 (0dec) | |
0 | 0° | |||||
1 | 60° | |||||
2 | 120° | |||||
3 | 180° | |||||
4 | 240° | |||||
5 | 300° | |||||
800A:14 | Hall sensor type | Enable or disable the open-collector Hall sensor inputs | UINT8 | RW | 0x01 (1dec) | |
1 | open collector |
Index 8010 DRV Amplifier Settings
8010:0 | DRV Amplifier Settings | Amplifier settings | UINT8 | RO | 0x64 (100dec) |
8010:01 | Enable TxPDOToggle | Enable or disable the TxPDO toggle in bit 10 of the status word | BOOLEAN | RW | 0x00 (0dec) |
8010:02 | Enable input cycle counter | 1: enabled Two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0. The low bit is represented in bit 10 and the high bit in bit 14 of the Status word. | BOOLEAN | RW | 0x00 (0dec) |
8010:04 | Repeat find commutation | Repeat the commutation angle determination. (Effective for all FOC operation modes) | BOOLEAN | RW | 0x01 (1dec) |
8010:05 | Enable cogging torque compensation | Enable or disable the cogging torque compensation (for FOC operation modes only). | BOOLEAN | RW | 0x00 (0dec) |
8010:12 | Current loop integral time | Integral component of current controller [0.1 ms] | UINT16 | RW | 0x000A (10dec) |
8010:13 | Current loop proportional gain | Proportional component of current controller [0.1 V/A] | UINT16 | RW | 0x000A (10dec) |
8010:14 | Velocity loop integral time (current mode) | Integral component of velocity controller [0.1 ms] (For operation modes with FOC. See chapter Selection of the operation mode) | UINT32 | RW | 0x00000032 (50dec) |
8010:15 | Velocity loop proportional gain (current mode) | Proportional component of velocity controller [µA/(°/s)] (For operation modes with FOC. See chapter Selection of the operation mode) | UINT32 | RW | 0x00000014 (20dec) |
8010:17 | Position loop proportional gain | Proportional component position controller. Unit: (°/s) / ° | UINT32 | RW | 0x0000000A (10dec) |
8010:19 | Nominal DC link voltage | Supplied DC link voltage [mV] | UINT32 | RW | 0x0000BB80 (48000dec) |
8010:1A | Min DC link voltage | Minimum DC link voltage [mV] | UINT32 | RW | 0x00001A90 (6800dec) |
8010:1B | Max DC link voltage | Maximum DC link voltage [mV] | UINT32 | RW | 0x0000EA60 (60000dec) |
8010:29 | Amplifier I2T warn level | I²T model warning threshold [%] | UINT8 | RW | 0x50 (80dec) |
8010:2A | Amplifier I2T error level | I²T model error threshold [%] | UINT8 | RW | 0x69 (105dec) |
8010:2B | Amplifier Temperature warn level | Terminal overtemperature warning threshold [0.1 °C] | UINT16 | RW | 0x0320 (800dec) |
8010:2C | Amplifier Temperature error level | Terminal overtemperature error threshold [0.1 °C] | UINT16 | RW | 0x03E8 (1000dec) |
8010:31 | Velocity limitation | Limitation of the velocity setpoint [rpm] (effective only in CSV and CSP mode) | UINT32 | RW | 0x000186A0 (100000dec) |
Index | Name | Meaning | Data type | Flags | Default | |
8010:33 | Stand still window | Standstill window [rpm] Velocity range for which the axis is considered to be at a standstill. | UINT16 | RW | 0x0000 (0dec) | |
8010:39 | Select info data 1 | Selection of "Info data 1" Optional display of additional information in the cyclic process data. The following parameters are available: | UINT8 | RW | 0x02 (2dec) | |
2 | DC link voltage [mV] | |||||
4 | PCB temperature - internal terminal temperature [0.1 °C] | |||||
7 | I2T Motor [%] | |||||
8 | I2T Amplifier [%] | |||||
10 | Digital inputs Bit0: Digital Input 1 Level Bit1: Digital Input 2 Level Bit2: Fan Status (EL7411 only) Bit3: unused Bit4: Encoder A Bit5: Encoder B Bit6: Encoder C Bit7: unused Bit8: Hall Sensor U Bit 9: Hall Sensor V Bit 10: Hall Sensor W Bit 11: unused Bit 12: Hardware Enable Input Level (required for the STO functionality) | |||||
12 | Phase Voltage U [mV] | |||||
13 | Phase Voltage V [mV] | |||||
14 | Phase Voltage W [mV] | |||||
8010:3A | Select info data 2 | Selection of "Info data 2" Optional display of additional information in the cyclic process data. The following parameters are available: | UINT8 | RW | 0x04 (4dec) | |
7 | I²T Motor [%] | |||||
8 | I²T Amplifier [%] | |||||
12 | Phase Voltage U | |||||
13 | Phase Voltage V | |||||
14 | Phase Voltage W | |||||
8010:50 | Following error window | Following error monitor: Following error window Unit: Reference to increments of the raw position data. Can be scaled in the PLC if necessary. 0xFFFFFFFF (-1dec) = following error monitor off Any other value = following error monitoring on [Inc] Applies in conjunction with following error timeout 8010:51. | UINT32 | RW | 0xFFFFFFFF (-1dec) | |
8010:51 | Following error time out | Following error monitor: Timeout [ms] If the following error is larger than the following error window for a time that exceeds the timeout, this leads to an error reaction. | UINT16 | RW | 0x0000 (0dec) | |
8010:54 | Feature bits | Reserved | UINT32 | RW | 0x00000000 (0dec) | |
8010:57 | Position loop velocity feed forward gain | Velocity pre-control of the position controller [%]. | UINT8 | RW | 0x64 (100dec) | |
8010:58 | Select info data 3 | Selection of "Info data 3" Optional display of additional information in the cyclic process data. The following parameters are available: | UINT8 | RW | 0x07 (7dec) | |
2 | DC link voltage (mV) | |||||
4 | PCB temperature (0.1 °C) | |||||
7 | I2T Motor | |||||
8 | I2T Amplifier | |||||
8010:59 | Error suppression mask | Error suppression mask Bit 0: Suppresses detection of a cable breakage of the motor phases Bit 1: Suppresses commutation angle monitoring | UINT32 | RW | 0x00000000 (0dec) | |
8010:5A | Velocity loop integral time (voltage mode) | Integral component of velocity controller [0.1 ms] (for operation modes with six-step. See chapter Selection of the operation mode) | UINT32 | RW | 0x000001F4 (500dec) | |
8010:5B | Velocity loop proportional gain (voltage mode) | Proportional component of velocity controller [μV/(°/s)] (for operation modes with six-step. See chapter Selection of the operation mode) | UINT32 | RW | 0x00000064 (100dec) | |
8010:5C | Velocity loop voltage feed forward gain (voltage mode) | Velocity pre-control of the velocity controller [%] (For operation modes with six-step. See chapter Selection of the operation mode) | UINT8 | RW | 0x32 (50dec) | |
8010:5E | Sensorless offset voltage scaling | Configures the voltage output at standstill [%]. | UINT16 | RW | 0x0032 (50dec) | |
8010:5F | Sensorless observer bandwidth | Bandwidth of the position/velocity observer in sensorless mode [Hz]. | UINT16 | RW | 0x0064 (100dec) | |
8010:60 | Sensorless max acceleration | Maximum acceleration in sensorless operation [°/s²]. | UINT32 | RW | 0x000186A0 (100000dec) | |
8010:61 | Cogging torque compensation | Contains the coefficients of the cogging torque compensation. These are determined by the Cogging Scan function. See chapter Scan Motor Cogging. | OCTET-STRING[16] | RW | {0} | |
8010:62 | Position loop deadband window | Deadband window of the position controller [Inc] For position deviations smaller than the defined range applies (if set velocity is in the "Standstill window" (see parameter: 8010:33) 0 - 75% position controller switched off 75 - 100% linear transition of the position controller gain | UINT32 | RW | 0x00000000 (0dec) | |
8010:63 | Find commutation time | Defines the time for determining the commutation angle [0.1 s] This process is divided into two phases. In total, it takes twice the time specified here. Required time depends on the application. | UINT16 | RW | 0x0009 (9dec) | |
8010:64 | Commutation type | Method for determining the commutation angle: | UINT8 | RW | 0x01 (1dec) | |
1 | FOC with incremental encoder | |||||
2 | Six-Step with Hall | |||||
3 | Six-step sensorless | |||||
4 | FOC with incremental encoder and Hall |
Index 8011 DRV Motor Settings
8011:0 | DRV Motor Settings | Motor settings | UINT8 | RO | 0x31 (49dec) |
8011:11 | Max current | Peak current of the motor [mA]. Limitation by maximum output current of the EL7411. The motor current values are to be specified as peak value. | UINT32 | RW | 0x00001770 (6000dec) |
8011:12 | Rated current | Nominal current of the motor [mA], corresponds to the maximum continuous motor output current. The motor current values are to be specified as peak value. Target Torque, Torque actual value and Torque limitation are scaled relative to the rated current in per mill. | UINT32 | RW | 0x000003E8 (1000dec) |
8011:13 | Motor pole pairs | Number of pole pairs | UINT8 | RW | 0x01 (1dec) |
8011:16 | Torque constant | Torque constant [mNm/A] | UINT32 | RW | 0x00000032 (50dec) |
8011:18 | Rotor moment of inertia | Mass moment of inertia of the motor including mechanism [g cm²] | UINT32 | RW | 0x00000064 (100dec) |
8011:19 | Winding inductance | Winding inductance [0.01 mH] | UINT16 | RW | 0x0064 (100dec) |
8011:1B | Motor speed limitation | Motor speed limitation [rpm] | UINT32 | RW | 0x000186A0 (100000dec) |
8011:29 | I2T warn level | I²T motor warning threshold [%] | UINT8 | RW | 0x50 (80dec) |
8011:2A | I2T error level | I²T motor error threshold [%] | UINT8 | RW | 0x69 (105dec) |
8011:2D | Motor thermal time constant | Motor thermal time constant of the winding [0.1 s] | UINT16 | RW | 0x0028 (40dec) |
8011:2E | Rated speed | Nominal speed [rpm] | UINT32 | RW | 0x000003E8 (1000dec) |
8011:2F | Rated voltage | Nominal motor voltage [mV] | UINT32 | RW | 0x0000BB80 (48000dec) |
8011:30 | Winding resistance | Winding resistance, phase - phase [mΩ] | UINT32 | RW | 0x000003E8 (1000dec) |
8011:31 | Voltage constant | Voltage constant [μV/min^(-1) ] Specifies the voltage induced by the motor as a generator (counter-electromotive force). | UINT32 | RW | 0x0000BB80 (48000dec) |
Index 8012 DRV brake settings
8012:0 | DRV brake settings | Brake settings | UINT8 | RO | 0x14 (20dec) |
8012:01 | Manual override (release) | Manual release of the motor brake. Intended for commissioning purposes. | BOOLEAN | RW | 0x00 (0dec) |
8012:11 | Release delay | Time the holding brake requires for opening (releasing) after the current was applied. [ms] | UINT16 | RW | 0x0000 (0dec) |
8012:12 | Application delay | Time the holding brake requires for closing (holding) after the current was switched off. [ms] | UINT16 | RW | 0x0000 (0dec) |
8012:13 | Emergency application timeout | Time that the amplifier waits until the speed reaches the standstill window after the stop request. The holding brake is triggered irrespective of the speed if the set waiting time is exceeded. [ms] Note: This parameter must be adjusted to at least the longest time for the axis to run down. In the case of suspended axes, this parameter should be set to a very short time in order to prevent the axis/load from sagging. | UINT16 | RW | 0x0000 (0dec) |
8012:14 | Brake moment of inertia | Moment of inertia of the motor brake [g cm²] | UINT16 | RW | 0x0000 (0dec) |
Index 8040 DMC Settings
8040:0 | DMC Settings | Settings for Drive Motion Control. | UINT8 | RW | 0x17 (23dec) |
8040:07 | Emergency deceleration | Deceleration for the emergency stop ramp. Indication in milliseconds from nominal motor speed to standstill. | UINT16 | RW | 0x64 (100dec) |
8040:08 | Calibration position | If homing is successful, the "Actual position" is set to this value. It is basically displayed unscaled in 64 bits. Scaling: The 32 low-order bits refer to single-turn revolution, the 32 high-order bits to multi-turn revolutions. | UINT64 | RW | 0x00 (0dec) |
8040:09 | Calibration velocity (towards plc cam) | Speed for driving on the referencing cams. Is specified in 10,000ths of 0x8011:1B "Motor speed limitation". | UINT16 | RW | 0x64 (100dec) |
8040:0A | Calibration velocity (off plc cam) | Speed to drive down from the referencing cam. Is specified in 10,000ths of 0x8011:1B "Motor speed limitation". | UINT16 | RW | 0x0A (10dec) |
8040:0E | Modulo factor | Modulo factor for modulo travel commands. The default value of 2^32 corresponds to a single-turn revolution and thus e.g. 360°. | UINT64 | RW | 0x100000000 (4294967296dec) |
8040:12 | Block calibration torque limit | Torque limitation for block calibration. The value is specified in 1000ths of 0x8011:12 "Rated current" | UINT16 | RW | 0x64 (100dec) |
8040:13 | Block calibration stop distance | Specifies the distance by which to move out of the block after calibration. Scaling see 0x8040:08. | UINT64 | RW | 0x100000000 (4294967296dec) |
8040:14 | Block calibration lag threshold | Maximum permissible position lag during block calibration. Scaling see 0x8040:08. | UINT64 | RW | 0x100000000 (4294967296dec) |
8040:15 | Target position window | General position target window for travel commands for reaching the InTarget state. Scaling see 0x8040:08. The "Target position window" is valid in connection with 0x8040:16 "Target position monitor time". | UINT64 | RW | 0x16C16C1 (23860929dec) |
8040:16 | Target position monitor time | The actual position must be within the position target window 0x8040:15 for the specified time to reach the InTarget state. Unit: ms. | UINT16 | RW | 0x14 (20dec) |
8040:17 | Target position timeout | Specifies the time for the timer to start when the setpoint generator reaches the target position. If the InTarget condition (see 0x8040:15 and 0x8040:16) is not reached within this time, the travel command is aborted. The function block for the travel command returns an error. Unit: ms. | UINT16 | RW | 0x1770 (6000dec) |
Index 8041 DMC Features
8041:0 | DMC Features | Drive Motion Control functions | UINT8 | RW | 0x1B (27dec) |
8041:13 | Invert calibration cam search direction | For the default homing sequence the direction for referencing cam search can be inverted.
8041:14 | Invert sync impulse search direction | For the default homing sequence the direction for sync pulse search can be inverted.
8041:19 | Calibration cam source | Signal source of the referencing cam:
8041:1A | Calibration cam active level | Signal level of the referencing cam that is evaluated as "active". | UINT8 | RW | 0x00 (0dec) |
8041:1B | Latch source | Signal source of the latch signal:
Index F800 FAN Settings
F800:0 | FAN Settings | Fan settings | UINT8 | RO | 0x11 (17dec) | |
F800:01 | Select function of Fan mode/Standard output | Select fan output function: | BIT4 | RW | 0x01 (1dec) | |
0 | Fan mode | |||||
1 | Digital output | |||||
F800:05 | Select function of fan diag/Standard input | Select fan input function: | BIT4 | RW | 0x01 (1dec) | |
0 | Fan diag | |||||
1 | Digital input | |||||
F800:11 | Fan behaviour | Fan behavior | UINT8 | RW | 0x0D (13dec) | |
0 | Controlled by fan temperature sensor | |||||
1 | Always on - low speed | |||||
4 | Always on - mid speed | |||||
9 | Always on - full speed | |||||
10 | Controlled by terminal temperature | |||||
13 | No fan installed |