Standard objects
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1000:0 |
Device type |
Device type of the EtherCAT slave: the Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. |
UINT32 |
RO |
0x00001389 (5001dec) |
Index 1008 Device name
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1008:0 |
Device name |
Device name of the EtherCAT slave |
STRING |
RO |
EL7332 |
Index 1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
Index 100A Software version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
100A:0 |
Software version |
Firmware version of the EtherCAT slave |
STRING |
RO |
08 |
Index 1018 Identity
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1018:0 |
Identity |
Information for identifying the slave |
UINT8 |
RO |
0x04 (4dec) |
1018:01 |
Vendor ID |
Vendor ID of the EtherCAT slave |
UINT32 |
RO |
0x00000002 (2dec) |
1018:02 |
Product code |
Product code of the EtherCAT slave |
UINT32 |
RO |
0x1CA43052 (480522322dec) |
1018:03 |
Revision |
Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description |
UINT32 |
RO |
0x00100000 (1048576dec) |
1018:04 |
Serial number |
Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 |
UINT32 |
RO |
0x00000000 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardized loading and saving of backup entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum across all backup entries of the EtherCAT slave |
UINT32 |
RO |
0x00000000 (0dec) |
Index 1400 CNT RxPDO-Par Control compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1400:0 |
CNT RxPDO-Par Control compact Ch.1 |
PDO Parameter RxPDO 1 |
UINT8 |
RO |
0x06 (6dec) |
1400:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 1 |
OCTET-STRING[2] |
RO |
01 16 |
Index 1401 CNT RxPDO-Par Control Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1401:0 |
CNT RxPDO-Par Control Ch.1 |
PDO Parameter RxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1401:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 2 |
OCTET-STRING[2] |
RO |
00 16 |
Index 1402 CNT RxPDO-Par Control compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1402:0 |
CNT RxPDO-Par Control compact Ch.2 |
PDO Parameter RxPDO 3 |
UINT8 |
RO |
0x06 (6dec) |
1402:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 3 |
OCTET-STRING[2] |
RO |
03 16 |
Index 1403 CNT RxPDO-Par Control Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1403:0 |
CNT RxPDO-Par Control Ch.2 |
PDO Parameter RxPDO 4 |
UINT8 |
RO |
0x06 (6dec) |
1403:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 4 |
OCTET-STRING[2] |
RO |
02 16 |
Index 1600 CNT RxPDO-Map Control compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1600:0 |
CNT RxPDO-Map Control compact Ch.1 |
PDO Mapping RxPDO 1 |
UINT8 |
RO |
0x06 (6dec) |
1600:01 |
SubIndex 001 |
1. PDO Mapping entry (1 bits align) |
UINT32 |
RO |
0x0000:00, 2 |
1600:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x02 (Enable latch extern on positive edge)) |
UINT32 |
RO |
0x7000:03, 1 |
1600:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x03 (Set counter)) |
UINT32 |
RO |
0x7000:04, 1 |
1600:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x04 (Enable latch extern on negative edge)) |
UINT32 |
RO |
0x0000:00, 4 |
1600:05 |
SubIndex 005 |
5. PDO Mapping entry (4 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
1600:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x7000 (CNT Outputs Ch.1), entry 0x11 (Set counter value)) |
UINT32 |
RO |
0x7000:11, 16 |
Index 1600 DCM RxPDO-Map Control Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1600:0 |
DCM RxPDO-Map Control Ch.1 |
UINT8 |
RO |
0x05 (5dec) |
1600:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7000 (DCM Outputs Ch.1), entry 0x01 (Enable)) |
UINT32 |
RO |
0x7000:01, 1 |
1600:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7000 (DCM Outputs Ch.1), entry 0x02 (Reset)) |
UINT32 |
RO |
0x7000:02, 1 |
1600:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7000 (DCM Outputs Ch.1), entry 0x03 (Reduce torque)) |
UINT32 |
RO |
0x7000:03, 1 |
1600:04 |
SubIndex 004 |
4. PDO Mapping entry (5 bits align) |
UINT32 |
RO |
0x0000:00, 5 |
1600:05 |
SubIndex 005 |
5. PDO Mapping entry (8 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
Index 1601 CNT RxPDO-Map Control Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1601:0 |
CNT RxPDO-Map Control Ch.1 |
PDO Mapping RxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1601:01 |
SubIndex 001 |
UINT32 |
RO |
0x0000:00, 2 |
1601:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7000 (CNT Outputs Ch.1), entry 0x03 (Set counter)) |
UINT32 |
RO |
0x7000:03, 1 |
1601:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7000 (CNT Outputs Ch.1), entry 0x04 (Inhibit counter)) |
UINT32 |
RO |
0x7000:04, 1 |
1601:04 |
SubIndex 004 |
4. PDO Mapping entry (4 bits align) |
UINT32 |
RO |
0x0000:00, 4 |
1601:05 |
SubIndex 005 |
UINT32 |
RO |
0x0000:00, 8 |
1601:06 |
SubIndex 006 |
UINT32 |
RO |
0x7000:11, 32 |
Index 1601 DCM RxPDO-Map Velocity Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1601:0 |
DCM RxPDO-Map Velocity Ch.1 |
UINT8 |
RO |
0x01 (1dec) |
1601:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7000 (DCM Outputs Ch.1), entry 0x21 (Velocity)) |
UINT32 |
RO |
0x7000:21, 16 |
Index 1602 CNT RxPDO-Map Control compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1602:0 |
CNT RxPDO-Map Control compact Ch.2 |
PDO Mapping RxPDO 3 |
UINT8 |
RO |
0x06 (6dec) |
1602:01 |
SubIndex 001 |
UINT32 |
RO |
0x0000:00, 2 |
1602:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7010 (DCM Outputs Ch.2), entry 0x02 (Reset)) |
UINT32 |
RO |
0x7010:03, 1 |
1602:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7010 (DCM Outputs Ch.2), entry 0x03 (Reduce torque)) |
UINT32 |
RO |
0x7010:04, 1 |
1602:04 |
SubIndex 004 |
UINT32 |
RO |
0x0000:00, 4 |
1602:05 |
SubIndex 005 |
UINT32 |
RO |
0x0000:00, 8 |
1602:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x7010 (CNT Outputs Ch.2), entry 0x11 (Set counter value)) |
UINT32 |
RO |
0x7010:11, 16 |
Index 1603 CNT RxPDO-Map Control Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1603:0 |
CNT RxPDO-Map Control Ch.2 |
PDO Mapping RxPDO 4 |
UINT8 |
RO |
0x06 (6dec) |
1603:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7010 (DCM Outputs Ch.2), entry 0x01 (Enable)) |
UINT32 |
RO |
0x0000:00, 2 |
1603:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7010 (CNT Outputs Ch.2), entry 0x03 (Set counter)) |
UINT32 |
RO |
0x7010:03, 1 |
1603:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7010 (CNT Outputs Ch.2), entry 0x04 (Inhibit counter)) |
UINT32 |
RO |
0x7010:04, 1 |
1603:04 |
SubIndex 004 |
UINT32 |
RO |
0x0000:00, 4 |
1603:05 |
SubIndex 005 |
UINT32 |
RO |
0x0000:00, 8 |
1603:06 |
SubIndex 006 |
UINT32 |
RO |
0x7010:11, 32 |
Index 1604 DCM RxPDO-Map Control Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1604:0 |
PDO Mapping RxPDO 5 |
UINT8 |
RO |
0x05 (5dec) |
1604:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7020 (DCM Outputs Ch.1), entry 0x01 (Enable)) |
UINT32 |
RO |
0x7020:01, 1 |
1604:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7020 (DCM Outputs Ch.1), entry 0x02 (Reset)) |
UINT32 |
RO |
0x7020:02, 1 |
1604:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7020 (DCM Outputs Ch.1), entry 0x03 (Reduce torque)) |
UINT32 |
RO |
0x7020:03, 1 |
1604:04 |
SubIndex 004 |
UINT32 |
RO |
0x0000:00, 5 |
1604:05 |
SubIndex 005 |
UINT32 |
RO |
0x0000:00, 8 |
Index 1605 DCM RxPDO-Map Velocity Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1605:0 |
PDO Mapping RxPDO 6 |
UINT8 |
RO |
0x01 (1dec) |
1605:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7020 (DCM Outputs Ch.1), entry 0x21 (Velocity)) |
UINT32 |
RO |
0x7020:21, 16 |
Index 1606 DCM RxPDO-Map Control Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1606:0 |
DCM RxPDO-Map Control Ch.2 |
PDO Mapping RxPDO 7 |
UINT8 |
RO |
0x05 (5dec) |
1606:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7030 (DCM Outputs Ch.2), entry 0x01 (Enable)) |
UINT32 |
RO |
0x7030:01, 1 |
1606:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7030 (DCM Outputs Ch.2), entry 0x02 (Reset)) |
UINT32 |
RO |
0x7030:02, 1 |
1606:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7030 (DCM Outputs Ch.2), entry 0x03 (Reduce torque)) |
UINT32 |
RO |
0x7030:03, 1 |
1606:04 |
SubIndex 004 |
UINT32 |
RO |
0x0000:00, 5 |
1606:05 |
SubIndex 005 |
UINT32 |
RO |
0x0000:00, 8 |
Index 1607 DCM RxPDO-Map Velocity Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1607:0 |
DCM RxPDO-Map Velocity Ch.2 |
PDO Mapping RxPDO 8 |
UINT8 |
RO |
0x01 (1dec) |
1607:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7030 (DCM Outputs Ch.2), entry 0x21 (Velocity)) |
UINT32 |
RO |
0x7030:21, 16 |
Index 1800 CNT TxPDO-Par Status compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1800:0 |
CNT TxPDO-Par Status compact Ch.1 |
PDO Parameter TxPDO 1 |
UINT8 |
RO |
0x06 (6dec) |
1800:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1 |
OCTET-STRING[2] |
RO |
01 1A |
Index 1801 CNT TxPDO-Par Status Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1801:0 |
CNT TxPDO-Par Status Ch.1 |
PDO Parameter TxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1801:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2 |
OCTET-STRING[2] |
RO |
00 1A |
Index 1802 CNT TxPDO-Par Status compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1802:0 |
CNT TxPDO-Par Status compact Ch.2 |
PDO Parameter TxPDO 3 |
UINT8 |
RO |
0x06 (6dec) |
1802:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 3 |
OCTET-STRING[2] |
RO |
03 1A |
Index 1803 CNT TxPDO-Par Status Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1803:0 |
CNT TxPDO-Par Status Ch.2 |
PDO Parameter TxPDO 4 |
UINT8 |
RO |
0x06 (6dec) |
1803:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 4 |
OCTET-STRING[2] |
RO |
02 1A |
Index 1A00 CNT TxPDO-Map Status compact Ch.1
1A00:0 | CNT TxPDO-Map Status compact Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x0B (11dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x03 (Set counter done)) | UINT32 | RO | 0x6000:03, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x04 (Counter inhibited)) | UINT32 | RO | 0x6000:04, 1 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x06 (Status of input clock)) | UINT32 | RO | 0x6000:06, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (5 bits align) | UINT32 | RO | 0x0000:00, 5 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x0E (Sync error)) | UINT32 | RO | 0x6000:0E, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6000:10, 1 |
1A00:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x11 (Counter value)) | UINT32 | RO | 0x6000:11, 1 |
Index 1A01 CNT TxPDO-Map Status Ch.1
1A01:0 | CNT TxPDO-Map Status Ch.1 | PDO Mapping TxPDO 2 | UINT8 | RO | 0x0B (11dec) |
1A01:01 | SubIndex 001 | 1. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 2 |
1A01:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x02 (Set counter done)) | UINT32 | RO | 0x6000:03, 1 |
1A01:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x04 (Counter inhibited)) | UINT32 | RO | 0x6000:04, 1 |
1A01:04 | SubIndex 004 | 4. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A01:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x06 (Status of input clock)) | UINT32 | RO | 0x6000:06, 1 |
1A01:06 | SubIndex 006 | 6. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A01:07 | SubIndex 007 | 7. PDO Mapping entry (5 bits align) | UINT32 | RO | 0x0000:00, 5 |
1A01:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x0E (Sync error)) | UINT32 | RO | 0x6000:0E, 1 |
1A01:09 | SubIndex 009 | 9. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A01:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6000:10, 1 |
1A01:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6000 (CNT Inputs Ch.1), entry 0x11 (Counter value)) | UINT32 | RO | 0x6000:11, 32 |
Index 1A02 CNT TxPDO-Map Status compact Ch.2
1A02:0 | CNT TxPDO-Map Status compact Ch.2 | PDO Mapping TxPDO 3 | UINT8 | RO | 0x0B (11dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A02:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x03 (Set counter done)) | UINT32 | RO | 0x6010:03, 1 |
1A02:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x04 (Counter inhibited)) | UINT32 | RO | 0x6010:04, 1 |
1A02:04 | SubIndex 004 | 4. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A02:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x06 (Status of input clock)) | UINT32 | RO | 0x6010:06, 1 |
1A02:06 | SubIndex 006 | 6. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A02:07 | SubIndex 007 | 7. PDO Mapping entry (5 bits align) | UINT32 | RO | 0x0000:00, 5 |
1A02:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x0E (Sync error)) | UINT32 | RO | 0x6010:0E, 1 |
1A02:09 | SubIndex 009 | 9. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A02:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6010:10, 1 |
1A02:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x11 (Counter value)) | UINT32 | RO | 0x6010:11, 16 |
Index 1A03 CNT TxPDO-Map Status Ch.2
1A03:0 | CNT TxPDO-Map Status Ch.2 | PDO Mapping TxPDO 4 | UINT8 | RO | 0x0B (11dec) |
1A03:01 | SubIndex 001 | 1. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A03:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x03 (Set counter done)) | UINT32 | RO | 0x6010:03, 1 |
1A03:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x04 (Counter inhibited)) | UINT32 | RO | 0x6010:04, 1 |
1A03:04 | SubIndex 004 | 4. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A03:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x06 (Status of input clock)) | UINT32 | RO | 0x6010:06, 1 |
1A03:06 | SubIndex 006 | 6. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A03:07 | SubIndex 007 | 7. PDO Mapping entry (5 bits align) | UINT32 | RO | 0x0000:00, 5 |
1A03:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x0E (Sync error)) | UINT32 | RO | 0x6010:0E, 1 |
1A03:09 | SubIndex 009 | 9. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A03:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6010:10, 1 |
1A03:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6010 (CNT Inputs Ch.2), entry 0x11 (Counter value)) | UINT32 | RO | 0x6010:11, 32 |
Index 1A04 DCM TxPDO-Map Status Ch.1
1A04:0 | DCM TxPDO-Map Status Ch.1 | PDO Mapping TxPDO 5 | UINT8 | RO | 0x0E (14dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x01 (Ready to enable)) | UINT32 | RO | 0x6020:01, 1 |
1A04:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x02 (Ready)) | UINT32 | RO | 0x6020:02, 1 |
1A04:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x03 (Warning)) | UINT32 | RO | 0x6020:03, 1 |
1A04:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x04 (Error)) | UINT32 | RO | 0x6020:04, 1 |
1A04:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x05 (Moving positive)) | UINT32 | RO | 0x6020:05, 1 |
1A04:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x06 (Moving negative)) | UINT32 | RO | 0x6020:06, 1 |
1A04:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x07 (Torque reduced)) | UINT32 | RO | 0x6020:07, 1 |
1A04:08 | SubIndex 008 | 8. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A04:09 | SubIndex 009 | 9. PDO Mapping entry (3 bits align) | UINT32 | RO | 0x0000:00, 3 |
1A04:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x0C (Digital input 1)) | UINT32 | RO | 0x6020:0C, 1 |
1A04:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x0D (Digital input 2)) | UINT32 | RO | 0x6020:0D, 1 |
1A04:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x0E (Sync error)) | UINT32 | RO | 0x6020:0E, 1 |
1A04:0D | SubIndex 013 | 13. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A04:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6020:10, 1 |
Index 1A05 DCM TxPDO-Map Synchron info data Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A05:0 |
DCM TxPDO-Map Synchron info data Ch.1 |
PDO Mapping TxPDO 6 |
UINT8 |
RO |
0x02 (2dec) |
1A05:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x11 (Info data 1)) |
UINT32 |
RO |
0x6020:11, 16 |
1A05:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x6020 (DCM Inputs Ch.1), entry 0x12 (Info data 2)) |
UINT32 |
RO |
0x6020:12, 16 |
Index 1A06 DCM TxPDO-Map Status Ch.2
1A06:0 | DCM TxPDO-Map Status Ch.2 | PDO Mapping TxPDO 7 | UINT8 | RO | 0x0E (14dec) |
1A06:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x01 (Ready to enable)) | UINT32 | RO | 0x6030:01, 1 |
1A06:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x02 (Ready)) | UINT32 | RO | 0x6030:02, 1 |
1A06:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x03 (Warning)) | UINT32 | RO | 0x6030:03, 1 |
1A06:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x04 (Error)) | UINT32 | RO | 0x6030:04, 1 |
1A06:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x05 (Moving positive)) | UINT32 | RO | 0x6030:05, 1 |
1A06:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x06 (Moving negative)) | UINT32 | RO | 0x6030:06, 1 |
1A06:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x07 (Torque reduced)) | UINT32 | RO | 0x6030:07, 1 |
1A06:08 | SubIndex 008 | 8. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A06:09 | SubIndex 009 | 9. PDO Mapping entry (3 bits align) | UINT32 | RO | 0x0000:00, 3 |
1A06:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x0C (Digital input 1)) | UINT32 | RO | 0x6030:0C, 1 |
1A06:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x0D (Digital input 2)) | UINT32 | RO | 0x6030:0D, 1 |
1A06:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x0E (Sync error)) | UINT32 | RO | 0x6030:0E, 1 |
1A06:0D | SubIndex 013 | 13. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A06:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6030:10, 1 |
Index 1A07 DCM TxPDO-Map Synchron info data Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A07:0 |
DCM TxPDO-Map Synchron info data Ch.2 |
PDO Mapping TxPDO 8 |
UINT8 |
RO |
0x02 (2dec) |
1A07:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x11 (Info data 1)) |
UINT32 |
RO |
0x6030:11, 16 |
1A07:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x6030 (DCM Inputs Ch.2), entry 0x12 (Info data 2)) |
UINT32 |
RO |
0x6030:12, 16 |
Index 1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Using the sync managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs |
UINT8 |
RW |
0x06 (6dec) |
1C12:01 |
Subindex 001 |
1. allocated RxPDO (contains the index of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1600 (5632dec) |
1C12:02 |
Subindex 002 |
2. allocated RxPDO (contains the index of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1602 (5634dec) |
1C12:03 |
Subindex 003 |
3. allocated RxPDO (contains the index of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1604 (5636dec) |
1C12:04 |
Subindex 004 |
4. allocated RxPDO (contains the index of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1605 (5637dec) |
1C12:05 |
Subindex 005 |
5. allocated RxPDO (contains the index of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1606 (5638dec) |
1C12:06 |
Subindex 006 |
6. allocated RxPDO (contains the index of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1607 (5639dec) |
Index 1C13 TxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C13:0 |
TxPDO assign |
PDO Assign Inputs |
UINT8 |
RW |
0x04 (4dec) |
1C13:01 |
Subindex 001 |
1. allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A00 (6656dec) |
1C13:02 |
Subindex 002 |
2. allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A02 (6658dec) |
1C13:03 |
Subindex 003 |
3. allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A04 (6660dec) |
1C13:04 |
Subindex 004 |
4. allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A06 (6662dec) |
1C13:05 |
Subindex 005 |
5. allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x0000 (0dec) |
1C13:06 |
Subindex 006 |
6. allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x0000 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C32:0 |
SM output parameter |
Synchronization parameters for the outputs |
UINT8 |
RO |
0x20 (32dec) |
1C32:01 |
Sync mode |
Current synchronization mode:
UINT16 |
RW |
0x0001 (1dec) |
1C32:02 |
Cycle time |
Cycle time (in ns):
UINT32 |
RW |
0x000F4240 (1000000dec) |
1C32:03 |
Shift time |
Time between SYNC0 event and output of the outputs (in ns, DC mode only) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:04 |
Sync modes supported |
Supported synchronization modes:
UINT16 |
RO |
0x0C07 (3079dec) |
1C32:05 |
Minimum cycle time |
Minimum cycle time (in ns) |
UINT32 |
RO |
0x0001E848 (125000dec) |
1C32:06 |
Calc and copy time |
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:07 |
Minimum delay time |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:08 |
Command |
The entries 1C32:03, 1C32:05, 1C32:06, 1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. |
UINT16 |
RW |
0x0000 (0dec) |
1C32:09 |
Maximum delay time |
Time between SYNC1 event and output of the outputs (in ns, DC mode only) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:0B |
SM event missed counter |
Number of missed SM events in OPERATIONAL (DC mode only) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0C |
Cycle exceeded counter |
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0D |
Shift too short counter |
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:20 |
Sync error |
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) |
BOOLEAN |
RO |
0x00 (0dec) |
Index 1C33 SM input parameter
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C33:0 |
SM input parameter |
Synchronization parameters for the inputs |
UINT8 |
RO |
0x20 (32dec) |
1C33:01 |
Sync mode |
UINT16 |
RW |
0x0022 (34dec) |
1C33:02 |
Cycle time |
as 0x1C32:02 |
UINT32 |
RW |
1C33:03 |
Shift time |
Time between SYNC0 event and reading of the inputs (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:04 |
UINT16 |
RO |
0x0C07 (3079dec) |
1C33:05 |
as 1C32:05 |
UINT32 |
RO |
1C33:06 |
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:07 |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:08 |
Command |
as 0x1C32:08 |
UINT16 |
RW |
0x0000 (0dec) |
1C33:09 |
Time between SYNC1 event and reading of the inputs (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:0B |
as 0x1C32:11 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0C |
as 0x1C32:12 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0D |
as 0x1C32:13 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:20 |
Sync error |
as 0x1C32:32 |
BOOLEAN |
RO |
0x00 (0dec) |
F000:0 | Modular device profile | General information for the modular device profile | UINT8 | RO | 0x02 (2dec) |
F000:01 | Module index distance | Index distance of the objects of the individual channels | UINT16 | RO | 0x0010 (16dec) |
F000:02 | Maximum number of modules | Number of channels | UINT16 | RO | 0x0004 (4dec) |
Index F008 Code word
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
F008:0 |
Code word |
reserved |
UINT32 |
RW |
0x00000000 (0dec) |
Index F010 Module list
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
F010:0 |
Module list |
Max. Subindex |
UINT8 |
RW |
0x04 (4dec) |
F010:01 |
SubIndex 001 |
Profile number CNT |
UINT32 |
RW |
0x00000096 (150dec) |
F010:02 |
SubIndex 002 |
UINT32 |
RW |
F010:03 |
SubIndex 003 |
Profile number DCM |
UINT32 |
RW |
0x000002DD (733dec) |
F010:04 |
SubIndex 004 |
UINT32 |
RW |