EL7037 - LEDs and connection
WARNING
WARNING! Risk of electric shock and damage of devices possible!
Bring the bus terminal system into a safe, powered down state before starting installation, disassembly or wiring of the Bus Terminals!
EL7037 - LEDs and connection 1:
LEDs and connection EL7037
Connection
Terminal point
Signal
1
A
Encoder input A
2
C
Encoder input C (zero input). If object 0x7000:01 is set in the control word and a rising edge occurs at encoder input C, the current counter value is stored as a reference mark in the latch register.
3
Encoder supply +24V
Encoder supply + 24 V, internally connected with positive power contact and pin 6, 7
4
A1
Motor winding A1
5
B1
Motor winding B1
6
+24V
+24 VDC, internally connected with positive power contact and pin 3, 7
7
+24V
8
Input 1
Digital input 1 (24 VDC)
9
B
Encoder input B
10
Latch
Latch input. The current counter value is stored as a reference mark in the latch register, if
  • object 0x7000:02 is set and a rising edge occurs at the latch input; or
  • object 0x000:04 is set and a falling edge occurs at the latch input.
11
Encoder supply 0V
Encoder supply 0 V, internally connected with negative power contact and pin 14, 15
12
A2
Motor winding A2
13
B2
Motor winding B2
14
0V
0 VDC, internally connected with negative power contact and pin 11, 15
15
0V
0 VDC, internally connected with negative power contact and pin 11, 14
16
Input 2
Digital input 2 (24 VDC), also configurable as a digital output (0,5 A)
LEDs
EL7037 - LEDs and connection 2:
EL7037 - LEDs
No.
LED
Color
Meaning
1
RUN
green
This LED indicates the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = Initialization of the terminal or BOOTSTRAP = Function for firmware updates of the terminal
blinking
State of the EtherCAT State Machine: PREOP = Setting for mailbox communication and variant standard settings
single flash
State of the EtherCAT State Machine: SAFEOP = Channel checking of the Sync Manager and the Distributed Clocks. Outputs stay in safe operation mode.
on
State of the EtherCAT State Machine: OP = Normal operation mode, mailbox- and process data communication possible
2
Encoder
green
on
Encoder ready for operation
3
A
green
on
Signal at encoder input A
4
B
green
on
Signal at encoder input B
5
C
green
on
Signal at encoder input C
6
Latch
green
on
Signal at latch input
7
Turn CW
green
on
Motor is triggered clock wise
8
Input 1
green
on
Signal at digital input 1
9
Driver
green
on
Driver stage ready for operation
10
Power
green
off
The power supply voltage (24 VDC) is absent or
the motor control is blocked (Index 0x6010:02 is not set))
on
The power supply voltage (24 VDC) is present
11
Warning
yellow
on
Configuration error, e.g.:
  • Motor power supply not connected
  • 80°C temperature exceeded
  • 100% duty cycle reached
12
Error A
red
on
Configuration error of output stage A, e.g.:
  • 100°C temperature exceeded
  • short circuit
13
Error B
red
on
Configuration error of output stage B, e.g.:
  • short circuit
14
Enable
green
off
The motor control is blocked (Index 0x6010:02 is not set) or EL7037 is not ready for operation
on
The motor control is activated (Index 0x6010:02 is set) or EL7037 is ready for operation
15
Turn CCW
green
on
Motor is triggered counter clock wise
16
Input 2
green
on
Signal at digital input 2