States of the internal state machine
The state (drive controller) (Index 0x9020:03) provides information about the current state of the internal state machine. For diagnostic purposes this can be read out by the PLC for the propagation delay. The internal cycle works constantly with 250 µs. A connected PLC cycle is very probably slower (e.g. 1 ms). For this reason it may be the case that some states are not visible at all in the PLC, since these will sometimes run through only one internal cycle.
ID
INIT
0x0000
Initialization/preparation for the next travel command.
IDLE
0x0001
Wait for the next travel command.
START
0x0010
The new command is evaluated and the corresponding calculations are performed.
ACCEL
0x0011
Acceleration phase.
CONST
0x0012
Constant phase
DECEL
0x0013
Deceleration phase
EMCY
0x0020
An "Emergency stop" has been triggered.
STOP
0x0021
The motor has stopped.
CALI_START
0x0100
Start of a calibration command.
CALI_GO_CAM
0x0110
The motor is being driven towards the cam.
CALI_ON_CAM
0x0111
The cam has been reached.
CALI_GO_SYNC
0x0120
The motor is being driven in the direction of the HW sync pulse.
CALI_LEAVE_CAM
0x0121
The motor is being driven away from the cam.
CALI_STOP
0x0130
End of the calibration phase.
CALIBRATED
0x0140
The motor is calibrated.
NOT_CALIBRATED
0x0141
The motor is not calibrated.
PRE_TARGET
0x1000
The set position has been reached; the position controller "pulls" the motor further into the target; "In-Target timeout" is started here.
TARGET
0x1001
The motor has reached the target window within the timeout.
TARGET_RESTART
0x1002
A dynamic change of the target position is processed here.
END
0x2000
End of the positioning phase.
WARNING
0x4000
A warning state occurred during the travel command; this is processed here.
ERROR
0x8000
An error state occurred during the travel command; this is processed here.
UNDEFINED
0xFFFF
Undefined state (can occur, for example, if the driver stage has no control voltage).