EL7031 - Technical data
Technical data
EL7031
Number of outputs
1 stepper motor, 2 phases
Power supply for output stage (via power contacts)
24 VDC (-15% / +20%)
Number of inputs
2
Supply voltage
24 VDC via the power contacts, via the E-bus
Output current
1.5 A (overload- and short-circuit-proof)
Maximum step frequency
1000, 2000, 4000 or 8000 full steps/s (configurable)
Step pattern
full step, half step, up to 64-fold micro stepping
Current controller frequency
approx. 25 kHz
Input signal voltage "0"
-3 V … 2 V
Input signal voltage "1"
2.5 V … 28 V
Input current
typ. 5 mA
Diagnostic LED
error phase A and B, loss of step/stagnation, power, enable
Resolution
approx. 5,000 positions in typical applications (per revolution)
Power supply
via the E-bus, encoder/driver stage/motor: via the power contacts
Current consumption via E-bus
typ. 120 mA
Electrical isolation
500 V (E-bus/signal voltage)
Supports NoCoeStorage function
from firmware 04
Configuration
no address setting required
configuration via TwinCAT System Manager
Weight
approx. 105 g
Permissible ambient temperature range during operation
0°C ... + 55°C
Permissible ambient temperature range during storage
-25°C ... + 85°C
Permissible relative humidity
95 %, no condensation
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Mounting
on 35 mm mounting rail conforms to EN 60715
Vibration/shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27,
see also installation instructions for enhanced mechanical load capacity
EMC immunity/emission
conforms to EN 61000-6-2 / EN 61000-6-4
according to IEC/EN 61800-3
EMC category
Category C3 - standard
Category C2, C1 - auxiliary filter required
Protection class
IP20
Installation position
without fan cartridge ZB8610: standard installing position
with fan cartridge ZB8610: standard installing position, other installing positions (example 1 & 2)
see notice
Approvals/markings*
CE, EAC, UKCA
cULus