Settings in CoE register

Adaptation of current and voltage

Notice

The motor may overheat!

In order to prevent overheating of the connected motor it is important to adapt the current and voltage output from the stepper interface to the motor.

To this end set the index 0x8010:01 "Maximum current" and 0x8010:03 "Nominal voltage" in the CoE register to suitable values (see Fig. Adaptation of current and voltage).

Reduced current can be set in index 0x8010:02. This reduces the coil current when at a standstill (and therefore the power dissipation). Please note that the torque is also reduced.

Settings in CoE register 1:Fig.151: Adaptation of current and voltage

Base frequency selection

Microstepping is set to 1/64 and cannot be changed. However, the base frequency can be changed (default: 2000). To this end select the terminal and select the CoE Online tab. Change the base frequency by double-clicking on the index 0x8012:05 "Speed range" (Fig. Setting the base frequency).

Settings in CoE register 2:Fig.152: Setting the base frequency

Selecting the feedback system (only for the module with encoder connections)

Two feedback system options are available for selection:

Settings in CoE register 3:

CoE "Feedback type"

By default, the stepper module is set to internal counter. If an external encoder is used, the setting must be changed by double-clicking on the index 0x8012:08 "Feedback type" in the Enum menu (Fig. Selecting the feedback system).

Settings in CoE register 4:Fig.153: Selecting the feedback system

KA factor

The KA factor can be used to adapt the current during the acceleration phases. The current increase is calculated as follows.

Current increase in mA = speed difference  x  K A / 1000

The steeper the speed ramp, the higher the current increase.

Settings in CoE register 5:Fig.154: Speed ramps

This value can be set in index 0x8011:07 "Ka factor (curr.)" (see fig. Setting the KA-factor).

Settings in CoE register 6:Fig.155: Setting the KA factor