Settings in CoE register
Adaptation of current and voltage
Notice | |
The motor may overheat! In order to prevent overheating of the connected motor it is important to adapt the current and voltage output from the stepper interface to the motor. |
To this end set the index 0x8010:01 "Maximum current" and 0x8010:03 "Nominal voltage" in the CoE register to suitable values (see Fig. Adaptation of current and voltage).
Reduced current can be set in index 0x8010:02. This reduces the coil current when at a standstill (and therefore the power dissipation). Please note that the torque is also reduced.
Base frequency selection
Microstepping is set to 1/64 and cannot be changed. However, the base frequency can be changed (default: 2000). To this end select the terminal and select the CoE Online tab. Change the base frequency by double-clicking on the index 0x8012:05 "Speed range" (Fig. Setting the base frequency).
Selecting the feedback system (only for the module with encoder connections)
Two feedback system options are available for selection:
- Encoder: Use external encoder for position feedback
- Internal Counter (default): Use internal counter for position feedback
CoE "Feedback type" By default, the stepper module is set to internal counter. If an external encoder is used, the setting must be changed by double-clicking on the index 0x8012:08 "Feedback type" in the Enum menu (Fig. Selecting the feedback system). |
KA factor
The KA factor can be used to adapt the current during the acceleration phases. The current increase is calculated as follows.
Current increase in mA = speed difference x K A / 1000
The steeper the speed ramp, the higher the current increase.
This value can be set in index 0x8011:07 "Ka factor (curr.)" (see fig. Setting the KA-factor).
