Changing EtherNet/IP settings
With the following products the settings can also be changed by ADS.
The Store Category must be defined in the System Manager for the setting. This is entered in the object 0xF800:2B "Advanced options" for all EtherNet/IP devices in the scanner or, for the slave interface, in object 0x8000:2B or 0x8010:2B for the optional 2nd slave.
If the corresponding flag is set, the IP address from the memory is used; if nothing is entered there the flag is ignored and parameters from the System Manager are used.
Changing EtherNet/IP settings 1:Fig.116: Object 0xF800, Master Settings
ADS-Write command
AMSNetId:
In the case of the EL6652(-0010) this is the same as the EtherCAT AmsNetId; in the case of the supplement the AMSNetId is to be taken from the System Manager.
Port:
When using the EL6652(-0010) the port number is the corresponding EtherCAT Slave address of the terminal. In the case of the EtherNet/IP supplement the port number is to be permanently set to 0xFFFF.
IDXGRP: 0x0001F480
IDXOFFS: 0x00000000
After adjusting the settings a TwinCAT restart is to be carried out in the case of the supplement, as well as switching once to PreOp mode in the case of the EL6652. The new settings are then accepted on transition to the OP mode.
Setting for setting (4 bytes + object size (256 bytes))
Byte Offset 0: 0x45
Byte Offset 1: 0x23
Byte Offset 2: ObjIndex LoByte (e.g. 0x8000 for Slave 1 and 0x8010 for Slave 2 and 0xF800 for the Master)
Byte Offset 3: ObjIndex HiByte
Byte Offset 4-260: Data of the object (see object description below)
Setting for resetting (4 bytes)
Byte Offset 0: 0x00
Byte Offset 1: 0x00
Object description
Offset
Data Type
SubIndex
Store Category
1
2
0x00..0x01
Id
UINT16
1
0x02..0x03
Reserved
UINT16
0x04..0x23
Product Name
BYTE[32], STRING(31)
3
X
0x24..0x27
Device Type
UINT32
4
0x28..0x2B
Verndor ID
UINT32
5
0x2C..0x2F
Product Code
UINT32
6
X
0x30..0x33
Revision
UINT32
7
0x34..0x37
Serial Number
UINT32
8
0x38..0x7D
Reserved
BYTE[70]
0x7E..0x83
MAC Address
BYTE[6]
32
0x84..0x87
IP Address
UINT32
33
X
0x88..0x8B
Network Mask
UINT32
34
X
0x8C..0x8F
Gateway Address
UINT32
35
X
0x90..0x91
DHCP Max Retries
UINT16
36
0x92..0x93
TCP/IP TTL
UINT16
37
0x94..0x95
TCP/IP UDP Checksum
UINT16
38
0x96..0x97
TCP/IP TCP Timeout
UINT16
39
0x98..0x99
Multicast TTL
UINT16
40
0x9A..0x9B
Multicast Checksum
UINT16
41
0x9C..0x9D
Forward Class3 to PLC
UINT16
42
0x9E..0x9F
Flags
UINT16
43
0xA0..0xFF
Reserved
Byte[96]
Store Category
The "Store Category" defines, which *.tsm settings should be overwritten with settings from the remanent memory. To do this, bits 9 & 8 must be set accordingly under "Flags" in the System Manager project. In order to modify both, both bits must be set.
(Bit9=Cat2, Bit8=Cat1)
ADS-Read command
AMSNetId:
Port:
Slave:
IDXGRP: 0x44818000
IDXOFFS:ID of the slave interface
LEN: 256
The ID of the slave interface is taken from the setting in the System Manager, the ID is set by the system and can only be read.
Changing EtherNet/IP settings 2:Fig.117: Object 0x8000: slave settings
Master:
IDXGRP: 0x4481F800
IDXOFFS:0x00000000
LEN: 256
The data are saved in the data array as described above.
Example for TwinCAT 2.11 R3 and EL6652 or EL6652-0010, reading and writing the IP setting:
Changing EtherNet/IP settings 3: Download