Box States

Directly below the PROFINET controller protocol there is a collective PROFINET error and a collective PROFINET status. Both show the number of devices for which a problem has occurred or for which a diagnosis is available. The error indicates possible problems with the connection establishment or reasons for a termination. The diagnosis provides status information about an existing connection.

Box States 1:

PnIoError - number of PROFINET IO devices that have an error

PnIoDiag - number of PROFINET IO devices where a diagnosis is available

It is possible to check at a glance which device or box has a problem in the protocol under Box States.

Box States 2:

Presently the following error messages are displayed under the “PnIoState”.

Number

Text

Description

Remedy/Cause

0

No Error

No error

No error

1

PROFINET Device state machine is in boot mode

PROFINET DeviceStateMachine is still in the start-up phase

Not an error, wait

2

Device not found

Device does not reply to the Identify Request

Check the connection; device switched on and connected; was the device named correctly?

3

The station name is not unique

The station name is not unique

There are two or more devices in the network with the same PROFINET name. A correct identification cannot take place.

4

IP could not set

IP address could not be set.

The PROFINET device has rejected the IP settings for some reason. Check whether the IP settings are correct.

5

IP conflict

IP conflict in the network

A possible cause is that several devices have the same IP address.

6

DCP set was not successful

There was no reply or an erroneous reply to a DCP Set

Check connection, device connected, was the device called by its correct name?

7

Watchdog error

The connection was broken off with a Watchdog error

Check the cycle time, check the connection, if necessary increase the Watchdog factor.

8

Datahold error

The connection was broken off with a Datahold error

Frame Data status was invalid for the length of the DataHoldTimer. Restart the device if necessary

9

RTC3: Sync signal could not be started

For IRT only: the Sync signal could not be started.

Is EtherCAT Sync signal correct or has Sync0 started?

10

PROFINET Controller has a link error

The PROFINET controller has no link

Check cable and connection.

11

The alias name is not unique

The alias name is not unique

There are two or more devices in the network with the same alias name. This is made up of the neighborhood information (PortId.ChassisId). A correct identification cannot take place.

12

The automatic name assignment is not possible - wrong device type

The automatic name assignment is not possible

The expected PROFINET device is not in the projected position (VendorId or DeviceId does not correspond). This means that no automatic naming and thus no device start-up is possible.

31

Only for EtherCAT gateways: WC-State of cyclic EtherCAT frame is 1

For EL6631 only: EtherCATWC state is set to 1

Check the mode on the EtherCAT master & slave (OP?).

 

As opposed to the state, more than one status can be displayed in the “BoxPnIoDiag”, i.e. the whole thing is bit-coded and up to 16 pieces of information can be displayed. The following statuses are currently displayed.

0x0000 = No diagnosis

0xXXX1 = IOC-AR is not established

0xXXX2 = IOC-AR is established

0xXXX4 = IOC-AR is established but no ApplReady

0xXXX8 = IOC-AR is established but module difference

0xXX1X = At least one AlarmCR get diagnosis alarm

0xX1XX = At least one InputCR is invalid

0xX2XX = At least one InputCR Provider is in stop

0xX4XX = At least one InputCR Problemindicator is set

0x1XXX = At least one OutputCR is invalid

0x2XXX = At least one OutputCR Provider is in stop

0x4XXX = At least one OutputCR Problemindicator is set

On the one hand information about the status of the IO Controller Single AR is displayed here. In addition, collective statuses are formed from the Frame Data statuses of the individual CRs. This applies to the input and output CRs (currently only one CR is possible, in future several). A PROFINET alarm is also displayed in "PnIoDiag"

Readout via ADS

The Box Status can be read out via an ADS Read.

ADS Read:

NetId = AMSNETID of the PROFINET controller

Port = BoxPort (0x1000 + BoxId)

Indexgroup = 0xF829

IndexOffset = 0

Length = sizeof(TPnIoDeviceDiagData);

where:typedef struct{

WORD pnioState;

WORD pnioDiag;

WORD NrOfInputCRs;

WORD NrOfOutputCRs;

WORD reserved[8];} TPnIoDeviceDiagData, *PTPnIoDeviceDiagData;

Readout via CoE (for EL663x)

The Box Status can also be read out via CoE for the EL663x. The index 0xAyy0 (where yy is the Adaptor / Device number) and the subindex 0x001 must be taken for this.