Comparison of nominal and actual configuration
If a connection exists, the project planning can be checked on the “Diagnosis” tab. At this level “Real Identification Data” returns the actually existing modules in an AR, “Expected Identification Data” indicates the expected modules (i.e. those projected in the controller) and “Module Difference” shows the differences to the device found in the nominal-actual comparison.
Fig.33: "Diagnosis" tab, checking the project planning If you are on the “Diagnosis” tab within the API, you can select the corresponding API about which information is to be obtained. If, for example, the PROFINET device is a drive, then this usually supports the Profidrive profile, which is identified in turn via API 0x3A00. If the Real Identification Data is to be read from this API, for example, then this access takes place via the Profidrive profile.
Fig.34: "Diagnosis" tab, API selectionIn addition, the “Get Real Configuration” button becomes active within an API (except for drives). It is possible via this to adopt the read-in data record into the current project. Note that modules that have already been created will be overwritten when doing this. This means that the links are lost, even in the case of previously correctly created modules.
When displaying the module differences, additional information is displayed by marking the message.
Fig.35: "Diagnosis" tab, adopt data set into projectDiagnosis Data
The available diagnosis can be read out by pressing the “Diagnosis Data” button. At device level all available diagnosis data for the existing AR is read out here.
Fig.36: "Diagnosis", Button Diagnosis DataA maximum of two diagnosis parameters are displayed in the list; others are marked by “…”. If the individual message is clicked, all available diagnosis information is displayed in the window below.
Cyclic diagnosis via “PnIoBoxState” and “PnIoBoxDiag”
These variables are cyclically exchanged with the process image between the PROFINET driver and the System Manager.
Presently the following error messages are displayed under the PnIoBoxState.
|
Number |
Text |
Description |
Remedial action / reason |
|---|---|---|---|
|
0 |
No error |
No error |
No error |
|
1 |
PROFINET Device state machine is in boot mode |
PROFINET Device State Machine is still in the start-up phase |
Not an error, wait |
|
2 |
Device not found |
Device does not reply to the Identify Request |
Check connection, device connected, was the device called by its correct name? |
|
3 |
The stationname is not unique |
The station name is not unique |
There are two or more devices in the network with the same PROFINET name. A correct identification cannot take place. |
|
4 |
IP could not set |
IP address could not be set. |
The PROFINET device has rejected the IP settings for some reason. Check whether the IP settings are correct. |
|
5 |
IP conflict |
An IP conflict has occurred in the network. |
A possible cause is that several devices have the same IP address. |
|
6 |
DCP set was not successful |
There was no reply or an erroneous reply to a DCP Set. |
Check connection, device connected, was the device called by its correct name? |
|
7 |
Watchdog error |
The connection was broken off with a Watchdog error. |
Check the cycle time, check the connection, if necessary increase the Watchdog factor. |
|
8 |
Datahold error |
The connection was broken off with a Datahold error. |
Frame Data status was invalid for the length of the DataHoldTimer. Restart the device if necessary. |
|
9 |
RTC3: Sync signal could not started |
For IRT only: the Sync signal could not be started. |
Is EtherCAT Sync signal correct or has Sync0 started? |
|
10 |
PROFINET Controller has a link error |
The PROFINET controller has no link. |
Check cable and connection. |
|
11 |
The aliasname is not unique |
The alias name is not unique |
There are two or more devices in the network with the same alias name. This is made up of the neighbourhood information (PortId.ChassisId). A correct identification cannot take place. |
|
12 |
The automatic name assignment isn't possible - wrong device type |
The automatic name assignment is not possible. |
The expected PROFINET device is not in the projected position (VendorId or DeviceId does not correspond). Hence, no automatic naming and thus no device start is possible. |
|
31 |
only for EtherCAT gateways: WC-State of cyclic EtherCAT frame is 1 |
For EL6631 only: EtherCAT WC State is 1 |
Check the mode on the EtherCAT master & slave (OP?). |
As opposed to the state, more than one status can be displayed in the “PnIoBoxDiag”, i.e. the whole thing is bit-coded and up to 16 pieces of information can be displayed. The following statuses are currently displayed.
0x0000 = No diagnosis
0xXXX1 = IOC-AR is not established
0xXXX2 = IOC-AR is established
0xXXX4 = IOC-AR is established but no ApplReady
0xXXX8 = IOC-AR is established but module difference
0xXX1X = At least one AlarmCR get diagnosis alarm
0xX1XX = At least one InputCR is invalid
0xX2XX = At least one InputCR Provider is in stop
0xX4XX = At least one InputCR Problemindicator is set
0x1XXX = At least one OutputCR is invalid
0x2XXX = At least one OutputCR Provider is in stop
0x4XXX = At least one OutputCR Problemindicator is set
On the one hand information about the status of the IO Controller Single AR is displayed here. In addition, collective statuses are formed from the Frame Data statuses of the individual CRs. The whole thing happens for the input and the output CRs (currently only one is possible; in future the controller will support several CRs). In addition a PROFINET alarm is also displayed in the “PnIoBoxDiag”