Control and status data
The control and status data are located in the first 16 bits of the input and output process image. Communication between the terminal and the controller is controlled via this data.
Status data
Bit position | Name | Meaning | Data type | |
0 | Transmit accepted | The terminal acknowledges receipt of data by changing the state of this bit. Only now new data can be transferred from the controller to the terminal. | BOOLEAN | |
1 | Receive request | By changing the state of this bit, the terminal informs the controller that the DataIn bytes contain the number of bytes displayed in “Input length”. The controller must acknowledge receipt of the data by changing the state of the ReceiveAccepted bit. Only then new data can be transferred from the terminal to the controller. | BOOLEAN | |
2 | Init accepted | 0 | The terminal is ready again for serial data exchange. | BOOLEAN |
1 | Initialization was completed by the terminal. | |||
3 | Buffer full | The reception FIFO is full. All incoming data will be lost from this point on! | BOOLEAN | |
4 | Parity error | A parity error has occurred. | BOOLEAN | |
5 | Framing error | A framing error has occurred. | BOOLEAN | |
6 | Overrun error | An overrun error has occurred. | BOOLEAN | |
7 | - |
8...15 | Input length | Number of input bytes available for transfer from the terminal to the controller. | UINT8 | |
Control data
0 | Transmit request | By changing the state of this bit, the controller informs the terminal that the DataOut bytes contain the number of bytes displayed in “Output length”. The terminal acknowledges receipt of the data by changing the state of the “TransmitAccepted” bit. Only now new data can be transferred from the controller to the terminal. | BOOLEAN | |
1 | Receive accepted | The controller acknowledges receipt of data by changing the state of this bit. Only then new data can be transferred from the terminal to the controller. | BOOLEAN | |
2 | Init request | 0 | The controller once again requests the terminal to prepare for serial data exchange. | BOOLEAN |
1 | The controller requests terminal for initialization. The transmit and receive functions will be blocked, the FIFO pointer will be reset and the interface will be initialized with the values of the responsible Settings object. The execution of the initialization will be acknowledged by the terminal with the ‘Init accepted’ bit. | |||
3 | Send continuous | Continuous sending of data from the FIFO. | BOOLEAN | |
4...7 | - |
8...15 | Output length | Number of output bytes available for transfer from the controller to the terminal. | UINT8 | |
PDO Assignment
The terminal makes two input/output process images available for each channel. These differ only in the representation of the control/status data.
In the case of bitwise representation, the data is made available as shown in the tables above. In the case of word-wise representation, the first 16 bits of the process data are combined in one word.
The process data objects begin as standard with a control/status word. This PDO assignment is required in order to use the ‘TwinCAT PLC Serial Communication’ library.
Status Inputs |
Control Outputs |
Representation |
0x1A00 |
0x1600 |
bitwise Ch. 1 |
0x1A01 |
0x1601 |
bitwise Ch. 2 |
0x1A02 |
0x1602 |
bitwise Ch. 3 |
0x1A03 |
0x1603 |
bitwise Ch. 4 |
0x1A04 |
0x1604 |
word-wise Ch 1 |
0x1A05 |
0x1605 |
word-wise Ch 2 |
0x1A06 |
0x1606 |
word-wise Ch 3 |
0x1A07 |
0x1607 |
word-wise Ch 4 |