Signal type RS422 (diff. input)
Differential signal levels according to RS422 are expected with the following settings in "Counter mode" (0x80n1:1D):
A cut-off frequency of up to 20 million increments per second is permissible with 4-fold evaluation (corresponds to 5 MHz).
Signal type RS422 (diff. input) 1:
RS422 signal level
Legend:
VCM
Common mode voltage range
A, B, C
Signals A, B, C
VID
Differential voltage
A̅, B̅, C̅
Inverted signals A̅, B̅, C̅
VIDLow
Differential voltage too low
Notice
Exceeding of Common Mode range
Exceeding the Common Mode voltage range can lead to destruction of the device.
RS422 - wire break and short circuit detection (open circuit)
In the RS422 (differential input) modes it is possible to detect a wire break or short circuit at the individual encoder inputs.
Activation and diagnosis of a wire break or short circuit can be found in the chapter RS422 - Wire break and short circuit detection (Open circuit).
Signal type RS422 (diff. input) 2:
Error bits not permanently set in case of wire break at an encoder input
If a wire break is only present at one encoder input (e.g. only track A), it may happen in individual cases that the differential voltage (VID) is above the limit range (VIDLow) due to the applied common mode voltage (VCM).
This means that the error is not clearly identified.
The corresponding error bits ("Open circuit" and "Error A") are not permanently present!
Notice
Differential and single-ended connection
The RS422 signal transmits a differential voltage, which makes the signal less sensitive to interference compared to a single-ended signal.
  • If the encoder signal is to be transmitted over longer distances or at higher frequencies, an encoder with RS422 signals is recommended.
  • Shielded and twisted pair cables should be used.