EL5102 - LEDs
EL5102 - LEDs 1:Fig.34: EL5102 - LEDs
LEDs left side
No.
Color
A1
green, red
green on
indicates TRUE level
2
B1
red on
There is a broken wire at the respective input. Diagnosis is only possible if the following three conditions are met.
  • The corresponding input is differentially wired, i.e.:
    "Counter mode" 0x8001:1D =0 (encoder RS422 (diff. input)) or
    "Counter mode" 0x8001:1D =1 (counter RS422 (diff. input))
  • "Error Detection" for the respective input is enabled:
    "Error Detection A" 0x8000:0B = TRUE
    "Error Detection B" 0x8000:0C = TRUE
    "Error Detection C" 0x8000:0D = TRUE.
  • The differential voltage VID Low is typically less than 0.67 V (subject to change).
3
C1
4
Status input 1
red
Fault signal input from encoder. Input is internally connected to 5 V via a pull-up resistor. The encoder output must actively pull the signal against GND.
on
Output active at the encoder; a fault message is present at the encoder or an overvoltage at the input
off
Output not active at the encoder; no fault message is present
5
PowerENC.ch1
green
Encoder supply voltage for channel 1 is available
7
Latch 1
green
is lit, if a signal (+24 V) is connected to the latch 1 input
9
Run
green
This LED indicates the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for firmware updates of the terminal
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set
Single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
10
Diag
red
Initialization process active or state of the EtherCAT State Machine: BOOT
15
Gate 1
green
is lit, if a signal (+24 V) is connected to the gate 1 input
LEDs right side
No.
Color
A2
green, red
green on
2
B2
red on
    "Counter mode" 0x8011:1D =0 (encoder RS422 (diff. input)) or
    "Counter mode" 0x8011:1D =1 (counter RS422 (diff. input))
    "Error Detection A" 0x8010:0B = TRUE
    "Error Detection B" 0x8010:0C = TRUE
    "Error Detection C" 0x8010:0D = TRUE.
3
C2
4
Status input 2
red
on
off
5
PowerENC.ch2
green
Encoder supply voltage for channel 2 is available
7
Latch 2
is lit, if a signal (+24 V) is connected to the latch 2 input
15
Gate 2
is lit, if a signal (+24 V) is connected to the gate 2 input