EL5102 - Technical data
Technical data
EL5102
Encoder type
Incremental, differential (RS422), single-ended (TTL, open collector), counter, pulse generator
Encoder connection
Differential inputs (RS422): A, A̅, B, B̅, C, C̅
Single-ended connection (TTL, Open Collector): A, B, C
Counters, pulse generators: A, B
Number of channels
2 x A, B, C
Additional inputs
Latch, Gate/Latch (24 VDC, tON > 1 µs) per channel,
Status Input input (max. 5 VDC, negative switching, tON > 10 µs) per channel
Encoder operating voltage
5 VDC (preset), 12 VDC, 24 VDC switchable, 0.3 A per channel (generated from the 24 VDC power contacts)
Counter
32 bit (default) or 16 bit switchable
Cut-off frequency
RS422 mode: 20 million increments/s with 4-fold evaluation, corresponds to 5 MHz
TTL mode: 4 million increments/s with 4-fold evaluation, corresponds to 1 MHz
Open Collector: 400,000 increments/s with 4-fold evaluation, corresponds to 100 kHz
Quadrature decoder
4-fold evaluation (preset), 2-fold, 1-fold evaluation switchable
Micro-increments resolution
1/256 bit micro-increments
Broken wire detection to sensor
Yes for RS422 encoder
Distributed Clocks
Yes
Timestamp
Resolution 1 ns
Special functions
Frequency, period duration and duty cycle measurement, micro increments, adjustable interference pulse filters,
Timestamp on: last incremental edge, zero pulse C, Latch input and Gate/Latch input
Cycle time
min. 100 µs
Current consumption via E-bus
typ. 210 mA
Current consumption from power contacts
typ. 20 mA + load
Electrical isolation
500 V (E-bus/field voltage)
Configuration
via TwinCAT EtherCAT subscriber configuration
Weight
approx. 100 g
Permissible ambient temperature range during operation
0°C ... +55°C
Permissible ambient temperature range during storage
-25°C ... +85°C
Permissible relative air humidity
95%, no condensation
Dimensions (W x H x D)
approx. 27 mm x 100 mm x 70 mm (width aligned: 24 mm)
Installation on mounting rails
on 35 mm mounting rail according to EN 60715
Enhanced mechanical load capacity
Yes, see also Installation instructions for enhanced mechanical load capacity
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP20
Installation position
variable
Approvals / markings*
CE, EAC, UKCA