Status Input input diagnostics
If the encoder has an error signal or status output, this can be connected to the "Status Input" input of the terminal and evaluated. The input is 5 V compatible.
The error signal or status output at the encoder is usually implemented with negative logic. This is indicated by the terminal as follows:
Encoder | EL5102 | ||
Fault signal output | Status Input | Status Input LED | Meaning |
HIGH level / output open | TRUE | off | e.g. encoder OK |
LOW level / PullDown - level is actively pulled down to LOW | FALSE | Red | e.g. encoder faulty |
If an overvoltage is present at the Status Input, it is displayed as follows:
Fault diagnosis in case of overvoltage at the Status Input | Display |
DiagMessage, type "Error", text ID 0x8315 | Error status input (channel n) |
0xA0n0:05 "Error input status" | TRUE |
LED: Status Input Ch. n | Red |
