TwinCAT tree
The operating principle of the EL47xx in conjunction with SYNC0 and SYNC1 pulses was already described in section "Basic Function Principles". This section describes the application of the Beckhoff TwinCAT System Manager for setting the parameters.
Once the terminal has been scanned in, the following tree structure appears (see Fig. TwinCAT tree EL4732).
TwinCAT tree 1:Fig.169: TwinCAT tree EL4732
Ch1/Ch2 CycleCount and Ch1/Ch2 Value
Each EL4732 record contains a CycleCounter for each channel that is incremented with each record, and n analog measured values with a width of 2 bytes each. With an oversampling factor of n = 25 a record therefore consists of a 16-bit CycleCounter (overflowing) and 25 16-bit samples per channel. The CycleCounter in the higher-level control system can be used to verify the consistency of the record transfer.
By default the EL47xx is set to n = 1, resulting in the process image shown in Fig. TwinCAT tree EL4732.
WcState 0/1 (Online tab)
Boolean variable indicating the working counter status of the terminal. An invalid working counter (value: 1) is displayed if the EtherCAT slave with its EtherCAT slave controller (ESC) did not read or write process data from or to the EtherCAT frame read.
TwinCAT tree 2:Fig.171: WCState, Online tab
InfoData, State
Shows the online status (EtherCAT state machine) of the terminal.
TwinCAT tree 3:Fig.172: InfoData, State, Online tab
Value
0x___1
Slave in 'INIT' state
0x___2
Slave in 'PREOP' state
0x___3
Slave in 'BOOT' state
0x___4
Slave in 'SAFEOP' state
0x___8
Slave in 'OP' state
0x001_
Slave signals error
0x002_
Invalid vendorId, productCode... read
0x004_
Initialization error occurred
0x010_
Slave not present
0x020_
Slave signals link error
0x040_
Slave signals missing link
0x080_
Slave signals unexpected link
0x100_
Communication port A
0x200_
Communication port B
0x400_
Communication port C
0x800_
Communication port D
Table 1: States of the EtherCAT state machine
