Setpoint processing, User Scale
The digital setpoint sent from the controller to the analog output channel must or can be changed in the device in order to
The output value / setpoint can be changed in 3 functional units, all three can be active at the same time:
The User Scale functional unit is intended for reinterpretations/transformations of the setpoint, so "50 kg" of the controller can become "10 V" with Gain = 0.2. It is implemented as a linear transformation with gain/offset.
Parameter:
Index (hex)
Data type
Meaning
80n0:01
Enable User Scale
disabled by default, calculation only takes place if TRUE
80n0:11
User Scale Offset
SINT16
is added directly in digits.
80n0:12
User Scale Gain
UINT16
1 bit corresponds to 2-16, so "1" corresponds to x7FFF/32767dec
80nD:1D
User Scale Offset (Real32)
REAL32
80nD:1E
User Scale Gain (Real32)
REAL32
The intermediate value after this functional unit can be viewed in index 0x90n0:01.
Notice
Setpoint processing, User Scale 1:
Changing the interface
When changing the interface, the gain and offset are reset to 1 and 0 respectively!