Analog input connection
Voltage measurement 0 ...10 V / -10 ... +10 V
Analog input connection 1:
Fig.2: Connection example EL4374, voltage measurement, 2- / 4-wire
Notice
Short-circuiting unused inputs
Unused inputs on the same device should be properly short-circuited with short cables directly at the terminal points to avoid crosstalk effects!
Current measurement 0 / 4 … 20 mA
Analog input connection 2:
Fig.3: Connection example EL4374, current measurement, 2- / 3-wire
Notice
Current circuit continuously conductive regardless of CoE setting
The current circuit of the channel is always continuously conductive, even if the channel is set to interface "U" in the CoE.
Analog input connection 3:
Fig.4: Example: Voltage measured via Ch1 at approx. 50 mA input current
“Auto-retry” of the current circuit at intervals of a few seconds leads to 24 V being applied briefly via the terminal input towards 0 V.
This behavior must be observed in particular if power sources are connected to the analog input "actively" (i.e. current output > 0 without a sink connected) and the source with its high open circuit voltage immediately starts to drive the current. An overload situation may occur that does not resolve itself because the current control of the source and the overcurrent protection of the input alternately block each other. To remedy this, the source must then be briefly set to 0 mA, ideally a connection under high open circuit voltage should be avoided.