Connection, display and diagnostics
Connection, display and diagnostics 1:
EL4374 LED and connection
LED
Color
Meaning
RUN
green
These LEDs indicate the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set
single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
flickering
State of the EtherCAT State Machine: BOOTSTRAP = function for Firmware updates of the terminal
ERROR
Input Ch1, 2
red
- Error ADC
- Significantly below the measuring range
- Significant exceeding of the measuring range
ERROR
Output Ch3, 4
red
- Error DAC
- Analog output overload: wire break at I output, short circuit at U output
- Limiter low limit undercut
- Limiter High limit exceeded
Notice
Maximum current load of the power contacts and connection points
  • The power contacts 24 V / 0 V may be loaded with max. 10 A each
  • Outgoing 24 V / 0 V terminal points may be loaded with max. 3 A each
Notice
Cable lengths >30 m
For longer cable lengths >30 m, suitable overvoltage protection must be provided (e.g. EL9540-0010) if corresponding interference could affect the signal cable.
EL4374 connection
Terminal point
No.
Comment
Internally connected with connection
Ch1 Input U+
1
Voltage input, channel 1
Ch2 Input U+
2
Voltage input, channel 2
+24 V
3
+24 V
4, 5, 6; +24 V power contact
+24 V
4
+24 V
3, 5, 6; +24 V power contact
+24 V
5
+24 V
3, 4, 6; +24 V power contact
+24 V
6
+24 V
3, 4, 5; +24 V power contact
Ch3 Output U+
7
Voltage/current output, channel 3
Ch4 Output U+
8
Voltage/current output, channel 4
GND
9
Analog ground (reference potential for Ch1...Ch4)
10, 15, 16
GND
10
9, 15, 16
Ch1 Input I+
11
Current input, channel 1
Ch2 Input I+
12
Current input, channel 2
0 V
13
0 V
14; 0 V power contact
0 V
14
0 V
13; 0 V power contact
GND
15
9, 10, 16
GND
16
9, 10, 15