Gain/Offset function
Gain/Offset function 1:Fig.153: Block diagram for determining the output values in default settings (gain/offset function)
The terminal is compared to the vendor calibration data by the vendor in order to achieve the specified output accuracy. The vendor calibration data are password protected and cannot be changed.
If manipulation of the output value is necessary on the system side,
See also the block diagram.
With:
Gainscale
= 0x80n0:12
UserScale Gain
Offsetscale
= 0x80n0:11
UserScale Offset
Gainuser
= 0x80n0:16
UserCalibration Gain
Offsetuser
= 0x80n0:15
UserCalibration Offset
(with the bipolar EL403x terminals 0x800 = 2048dec to be added)
Gainvendor
= 0x80nF:02
VendorCalibration Gain
Offsetvendor
= 0x80nF:01
VendorCalibration Offset
XDAC
= 0x80nE:01
DAC Raw Value
Ys
EtherCAT PDO setpoint
Is the influence of the scaling:
User scaling enabled:
Ysc = Ys1 * Gainscale*2-16 + Offsetscale
User scaling disabled:
Ysc = Ys1
And the influence on the calibration values:
Vendor calibration enabled:
XDAC = Ysc * Gainvendor *2 -16 + Offsetvendor
User calibration enabled:
XDAC = Ysc * Gainuser *2- 20 + Offsetuser
No calibration enabled:
XDAC = Ysc
Gain/Offset function 2:
No simultaneous enablement of vendor and user calibration
Only the vendor calibration (0x80n0:08 "Enable vendor calibration") or
the user calibration (0x80n0:01 "Enable user calibration") may be enabled.