EL4134-0020, EL4134-0030 - Technical data
Technical data | EL4134-0020 | EL4134-0030 | ||
Connection technology | 2-wire, single-ended | |||
Number of outputs | 4 | |||
Output voltage | -10 V...+10 V (short-circuit proof) | |||
Accuracy | < ±0.1 % (relative to full scale value) | |||
Resolution | 16 bits (including sign) | |||
Sampling type | simultaneous | |||
Ground reference | single ended | |||
Load | > 5 kΩ | |||
Distributed Clocks (DC) | yes | |||
Max. sampling rate (output rate) | DC disabled **) | 4 kSps (corresponds to minimum EtherCAT cycle time of 250 µs) | ||
DC enabled | 2.5 kSps (corresponds to minimum EtherCAT cycle time of 400 µs) | |||
Power supply for the electronics | via the E-bus | |||
Power supply for outputs | via the E-bus | |||
Current consumption via E-bus | typ. 190 mA (265 mA***)) | |||
Electrical isolation | 500 V (E-bus/field voltage) | |||
Bit width in process image | Outputs: 4 x 16 bit data | |||
Configuration | no address or configuration settings required | |||
Weight | approx. 65 g | |||
Permissible ambient temperature range during operation | 0 °C ... +55 °C | |||
Permissible ambient temperature range during storage | -25 °C ... +85 °C | |||
Permissible relative air humidity | 95 %, no condensation | |||
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) | |||
on 35 mm mounting rail, conforms to EN 60715 | ||||
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 see also Installation instructions for enhanced mechanical load capacity | |||
EMC immunity / emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |||
Protection rating | IP20 | |||
Installation position | variable | |||
Calibration certificate | ||||
Identification / approval*) |
**) SyncManager synchronous, EtherCAT frame triggered.
The EL41xx does not support oversampling, therefore the output rate is equal to the EtherCAT cycle time.
***) valid for HW / FW / revision combinations before HW 10 / FW 03, Rev.-1021
Ex markings
Standard | Marking |
ATEX | II 3 G Ex nA IIC T4 Gc |
IECEx | Ex nA IIC T4 Gc |