Diag-Messages

The terminal provides the following diagnostic messages:

Diag-Code

Meaning

TwinCAT Message

Troubleshooting

#x0001

no error

no error

-

#x1180

Supply voltage ok

Supply voltage ok

-

#x1707

Channel is not in overload anymore

Channel is not in overload anymore

-

#x1708

Channel %d is not in overload anymore

Channel %d is not in overload anymore

-

#x170E

No overtemperature anymore

No overtemperature anymore

-

#x170F

No overtemperature on channel %d anymore

No overtemperature on channel %d anymore

-

#x1710

Full voltage range is available again

Full voltage range is available again

-

#x4101

Terminal-Overtemperature

Terminal-Overtemperature

Device is too warm internally, but continues to work, ensure cooling

#x4102

Overtemperature on channel %d

Overtemperature on channel %d

Device is too warm internally, but continues to work, ensure cooling

#x4710

More than four channels configured for current output, voltage output is limited to ±5 V

More than four channels configured for current output, voltage output is limited to ±5 V

If > ±5 V is required on the U channels, other outputs/devices must be used to output the current values.

#x8144

Hardware fault %d

Hardware fault %d

Check load, measure output function externally, contact support if necessary

#x8601

Supply voltage too low

Supply voltage too low

Check voltage of power contacts Up

#x8707

Channel overload (Channel %d)

Channel overload (Channel %d)

Check wiring and load, possibly short circuit/OpenLoad?

#x870A

Range error of channel %d

Range error of channel %d

External voltage applied to the channel?

Diag-Messages 1:Fig.152: Display in TwinCAT 3.1

The error states are expressed as follows

Error

PDO
Status.Overrange
Status.Underrange

PDO
Status.Error
(channel by channel)

PDO
Status.Warning
(channel by channel)

DiagMsg

Error-LED
(channel by channel)

Supply UP (power contacts) too low/too high

No

No

No

Yes

All channels

Output channel overtemperature

No

No

Yes

Yes

No

Output channel overload 1)

No

Yes

No

Yes

Yes

Output channel above/below limiter

Yes

Yes

Yes

No

Yes

Device overtemperature

No

no

All channels

yes

No

1) probably short circuit at voltage output and setpoint <> 0 V, probably wire break at current output and setpoint <> 0 mA