EL4074
EL4074 1:Fig.8: EL4074 LED and connection
LED
Color
Meaning
RUN
green
These LEDs indicate the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set
Single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
flickering
State of the EtherCAT State Machine: BOOTSTRAP = function for Firmware updates of the terminal
ERROR
Ch1…4
red
- Analog output overload:
wire break at I output, short circuit at U output
- Setpoint exceeds Limiter: below low limit /above high limit
- Internal error DAC
Notice
Cable lengths > 30 m
For longer cable lengths > 30 m, suitable overvoltage protection must be provided (e.g. EL9540-0010) if corresponding interference could affect the signal cable.
EL4074 connection
Terminal point
No.
Internally connected with connection
Max. current carrying capacity *)
Ch1 output
1
Voltage/current output, channel 1
overload protected
Ch2 output
2
Voltage/current output, channel 2
overload protected
Ch3 output
2
Voltage/current output, channel 3
overload protected
Ch4 output
2
Voltage/current output, channel 4
overload protected
+24 V DC
5
+24 V
6; 7, 8 +24 V power contact
1 A
+24 V DC
6
+24 V
5, 7, 8 +24 V power contact
1 A
+24 V DC
7
+24 V
5, 6, 8 +24 V power contact
1 A
+24 V DC
8
+24 V
5, 6, 7, +24 V power contact
1 A
GND
9
Analog ground (reference potential for Ch1...Ch4)
10, 11, 12
100 mA **)
GND
10
9, 11, 12
100 mA **)
GND
11
9, 10, 12
100 mA **)
GND
12
9, 10, 11
100 mA **)
0 V
13
0 V
14, 15, 16, 0 V power contact
1 A
0 V
14
0 V
13, 15, 16, 0 V power contact
1 A
0 V
15
0 V
13, 14, 16, 0 V power contact
1 A
0 V
16
0 V
13, 14, 15, 0 V power contact
1 A
*) Constant current; short-term higher currents are to be avoided and can cause thermal overload (damage)
**) The "GND" potential is internally coupled to the "0V" potential, but is subject to a reduced current carrying capacity
Voltage output 0...10 V / -10...+10 V
EL4074 2:Fig.9: Connection example EL4074, voltage output, 2-/4-wire
Current output -20 / 0 / +4…+20 mA
EL4074 3:Fig.10: Connection example EL4074, current output, 2-/4-wire