Setpoint processing, user/vendor calibration

The electrical set output value generated and digitized by the DAC must or can be changed in the device in order to

The output value can be changed in 3 functional units, all 3 can be active at the same time:

The "User/vendor calibration" functional unit is intended for correcting hardware-specific influences. They are implemented as 3rd order polynomial transformations (offset, gain, x², x³).

Note: The term "calibration", which is historically based at Beckhoff, is used here in the CoE, even if it has nothing to do with deviation statements of a calibration certificate. Actually, this is a description of the vendor or customer calibration data/adjustment data used by the device during operation in order to maintain the assured analog accuracy.

- User Calibration

The "User calibration" functional unit can be used by the user if alternative, system-dependent correction values are to be used permanently.

To be able to work with both INT16-based gain/offset values and Real32 coefficients, processing in "User Calibration" (if Enable User calibration = 1) proceeds as follows:

  • for setpoint >=0: "Value after User calibration" = S0 + "Value after Vendor calibration" * S1 +("Value after Vendor calibration")² * S2
  • for setpoint <0: "Value after User calibration" = S0 + "Value after Vendor calibration" * S1n +("Value after Vendor calibration")² * S2

Parameter:

Index

Name

Data type

Meaning

80n0:07

Enable User calibration

BOOL

disabled by default, calculation only takes place if TRUE

80n0:17

User calibration offset

SINT16

1 bit = AEWnom / 32767,
default: 0

80n0:18

User calibration gain

UINT16

1 bit corresponds to 2-16, "1" therefore corresponds to x7FFF/32767dec,
default: 1

80nC:01

User calibration data

BYTE4

4 bytes of free memory space;
here it is possible to store the calibration date in the form of 8 CHAR, for example

80nC:03..0D

User Scale Gain (Real32)

REAL32

Real32 coefficients S0/S1/S2/S3/S1n of the calculation polynomial,
default: S0=0, S1=1, S1n = 1, S2=0

The intermediate value after this functional unit can be viewed in index 90n0:0A.

The number of setting changes in this functional unit is counted up in index 90n2:12 "User Calibration Counter" (cannot be deleted).

Procedure: the counter is incremented the first time any parameter in the data area index 80nC or index 80n0:17/18 is changed; further changes in the data area in the following 30 seconds are not taken into account for the counter. After this time has elapsed, a parameter change will increment the counter again.

- Vendor Calibration

The electrical channel is calibrated by Beckhoff in the Vendor Calibration functional unit for compliance with the given uncertainty specification (see Technical Data, previously: output error). The vendor calibration data from Beckhoff is available in this area.

Parameter:

Index

Name

Data type

Meaning

80n0:08

Enable vendor calibration

BOOL

enabled by default, the data is taken into account.
Can be disabled on the application side if only the User Calibration Data is to be used for the calculation

80nF

Vendor calibration data

-

not intended for user modification

The intermediate value after this functional unit can be viewed in index 90n0:0B under 'Value after Vendor Calibration'.

The number of setting changes in this functional unit is counted up in index 90n2:12 as 'Vendor Calibration Counter' and cannot be deleted.

Procedure: the counter is incremented the first time any parameter in the data area is changed; further changes in the data area in the following 30 seconds are not taken into account for the counter. After this time has elapsed, a parameter change will increment the counter again.

Password protection for user data

Some user data are protected against unwanted or inadvertent writing by an additional password to be entered in CoE 0xF009:

  • CoE write accesses by the user, PLC or startup entries in Single or CompleteAccess mode
  • Overwrite the values by RestoreDefaultParameter Access to 0x80n0 (or 0x80nD, if available)
Setpoint processing, user/vendor calibration 1:Fig.186: Password protection for the 0x8000:17 and 0x8000:18 entries (example)

Use of CoE 0xF009

  • Entering 0x12345678 enables the password protection → Object shows "1" (enabled)
    Protected objects can now no longer be changed, no error message occurs during a write access!
  • Entering 0x11223344 disables password protection → Object displays "0" (disabled)

Password protection takes effect with the following AI settings:

Index

Designation

80n0:07

Enable User calibration

80n0:08

Enable Vendor calibration

80n0:17

User calibration offset

80n0:18

User calibration gain

80nC

User calibration data

80nD:1A

Limiter Low Value

80nD:1B

Limiter High Value