Technical data
Technical data 1:
RMS value (rms) specifications
All AC value specifications in this documentation such as RMS specifications (rms) refer to a 50/60 Hz 3-phase mains network with a sinusoidal waveform (crest factor 1.414).
Technical data
EL3783
EL3783-0100
Number of inputs
3 x current, 3 x voltage
Oversampling factor
n = 1…100 selectable
Distributed Clocks
yes
Accuracy of Distributed Clocks
<< 1 µs
Measuring error
< ±0.2 % of full scale value
Conversion time
Minimum 50 µs, all channels measured simultaneously
Sampling type
simultaneous
Ground reference
single ended
Mains voltage
(nominal voltage range)
AC:
400 Vrms (ULX-N) or 690 Vrms (ULX-ULY) (TN mains: 600 Vrms).
DC:
480 V with connection via L1 and L2 (or L3)
corresponding to AC:
100 Vrms (ULX-N) for voltage transformers
DC:
120 V with connection via L1 and L2 (or L3)
Technical voltage measuring range
520 Vrms (ULX-N) or 897 Vrms (ULX-ULY)
common reference potential N/GND
max. time for voltages exceeding 500 Vrms (ULX-N) or 863 Vrms (ULX-ULY):
tmax < 10 s **)
130 Vrms (ULX-N)
Max. permitted overvoltage
max. ±736 V (peak value, ULX-N, equivalent to 520 Vrms) or
max. ±1270 V (peak value, ULX-ULY, equivalent to 897 Vrms) **)
max. 300 Vrms (ULX-N) **)
1 digit corresponds to 22.5 mV
1 digit corresponds to 5.75 mV
Voltage resolution (16-bit including sign)
1 digit ~ 22.5 mV
Input resistance voltage circuit
typ. 1.5 MΩ
Nominal current range
AC accordingly: 1 Arms (automatic switching to 5 Arms)
recommended via measuring transformer x A AC/1 A AC
Technical current measuring range
1.84 A (peak value, equivalent to 1.3 Arms) or
9.2 A (peak value, equivalent to 6.5 Arms)
Max. permitted overcurrent
max. ±10 A peak value, equivalent to 7 Arms **),
surge overload capacity 60 A (sinusoidal) for 1 sec.,
the upstream use of current-limiting current transformers is recommended
Largest short-term deviation during a specified electrical interference test
< ±0.5 % of full scale value for the current measurement
Current resolution (16-bit including sign)
1 digit ~ 56.2 µA (~281 µA if 5 A range is active)
Insulation tested with
AC (50Hz) 2000 V for 80 s (Type Test)
Input resistance current circuit
typ. 3 mΩ
Signal type
variable
Electrical isolation
4,500 V, production test 2 sec.
Current consumption power contacts
Current consumption via E-bus
typ. 260 mA
Special features
Technical measuring range for current and voltage 130 % of the respective measuring range,
Anti-aliasing filter (see Basic functional principles), adjustable automatic current range switching, electrically isolated current inputs
Configuration
via TwinCAT System Manager
**) Operation for longer periods above the rated range can impair the function and/or lead to a shortening of the service life
Environmental conditions
EL3783
EL3783-0100
Permissible ambient temperature range during operation
-25°C ... +55°C
0°C ... +55°C
Permissible ambient temperature range during storage
-40°C ... +85°C
-25°C ... +85°C
Permissible relative air humidity
95 %, no condensation
General data
EL3783
EL3783-0100
Weight
approx. 100 g
Dimensions (W x H x D)
approx. 27 mm x 100 mm x 70 mm (width aligned: 24 mm)
Mounting
on 35 mm mounting rail conforms to EN 60715
Installation position
see notice!
Standards and approvals
EL3783
EL3783-0100
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
Conforms to EN 61000-6-2/EN 61000-6-4
Protection class
IP20
Marking / Approval*)
CE, EAC, UKCA
cULus