Technology
Measurement of AC variables with the EL3773
Normal three-phase mains supply
The normal 3-phase low-voltage grids in Central Europe are characterized by the following interrelationship: rated voltage is usually the effective voltage URMS, e.g. 230 VRMS, as a star voltage between one of the three live conductors (L1, L2 or L3) and neutral N.
With a pure sinusoidal oscillation (unloaded grid) a maximum peak voltage (max. amplitude) of approx. ±325Vpeak to N is calculated from the then valid crest factor from in the star voltage.
A phase-to-phase voltage of (RMS) can be measured between the live conductors.
RMS value specifications
![]() | RMS value (rms) specifications All AC value specifications in this documentation such as RMS specifications (rms) refer to a 50/60 Hz 3-phase mains network with a sinusoidal waveform. |
The EL3773 EtherCAT Terminal is a power monitoring terminal for state monitoring of a 3-phase AC voltage system. The following properties are characteristic of the EL3773:
- 3 channels measure -410 to +410 V to N through analog-to-digital converters in 16-bit resolution as amplitude value
- 3 channels measure -1.5 to +1.5 A to N through analog-to-digital converters in 16-bit resolution as amplitude value
- all 6 analog input channels are measured simultaneously
- the EL3773 is an oversampling terminal and can therefore record not just 1, but up to 100 samples (amplitude values) per channel in each PLC/EtherCAT cycle. These are sent as a data packet to the controller via the cyclic process data.
The minimum sampling time is 100 µs, corresponding to 10,000 samples/second. - The voltage and current curve can have any form; the EL3773 is thus suitable for AC and DC measurements
- various filter functions (low-pass and notch filter) are available for each channel
- the EL3773 can be synchronized with other EtherCAT device over Distributed Clocks, but can also be operated without Distributed Clocks with oversampling
- no pre-evaluations or calculations of the amplitude values take place in the EL3773
Hence, the EL3773 is suitable for very different applications, for example
- 3-phase monitoring: the voltage and current to N are measured for a 3-phase load
- 3-load monitoring: the voltage and current to N can be measured for 3 loads even if connected to the same phase
- each channel can measure as desired, provided the measured is referred to N (or GND in DC networks)
- Measurement of non-sinusoidal amplitude curves, including rectangular or DC curves
Evaluations and calculations of the raw data sent to the controller, such as active power (P), cumulative power consumption (W) or power factor (cos φ) must take place in the controller. The controller has sufficient computing power for true RMS or performance calculation and complex custom algorithms based on the measured voltages and currents.
![]() | Design of voltage measuring range Low-voltage power supply systems are defined, for example, in IEC 60038. Since 2003 the specification here is 230/400 VRMS ±10%, corresponding to ±357 Vpeak. So that substantial spikes can also be measured, the EL3773 supports a measuring range of 288 VRMS AC, corresponding to ±407 Vpeak (nominal: ±410 V). |