Measurement ±10 mV
Measurement mode
±10 mV
Measuring range, nominal
-10…+10 mV
Measuring range, end value (full scale value)
10 mV
Measuring range, technically usable
-10.737…+10.737 mV
PDO resolution
24 bit (including sign)
PDO LSB (Extended Range)
1.28 nV
PDO LSB (Legacy Range)
1.192.. nV
Basic accuracy: Measuring deviation at 23°C, with averaging
< ±0.06%FSV = ±600 ppmFSV
Offset/Zero Point deviation (at 23°C)
EOffset
< 550 ppmFSV
Gain/scale/amplification deviation (at 23°C)
EGain
< 150 ppm
Non-linearity over the whole measuring range
ELin
< 160 ppmFSV
Repeatability
ERep
< 50 ppmFSV
Noise (without filtering)
ENoise, PtP
< 1200 ppmFSV
< 9375 [digits]
ENoise, RMS
< 200 ppmFSV
< 1563 [digits]
Max. SNR
> 74.0 dB
Noisedensity@1kHz
< 28.28 Measurement ±10 mV 1:
Noise (with 50Hz FIR filtering)
ENoise, PtP
< 120 ppmFSV
< 938 [digits]
ENoise, RMS
< 21.0 ppmFSV
< 164 [digits]
Max. SNR
> 93.6 dB
Temperature coefficient
TcGain
< 22 ppm/K typ.
TcOffset
< 20 ppmFSV/K typ.
Common-mode rejection ratio (without filtering)
DC: >115 dB typ.
50 Hz: >105 dB typ.
1 kHz: >80 dB typ.
Common-mode rejection ratio (with 50Hz FIR filtering)
DC: >115 dB typ.
50 Hz: >115 dB typ.
1 kHz: >115 dB typ.
Largest short-term deviation during a specified electrical interference test
±0.2%FSV = ±2000 ppmFSV typ.
Input impedance ±Input 1
(Internal resistance)
Differential 4.1 MΩ || 11 nF typ.
CommonMode 1 MΩ || 40 nF typ.
Methodology: Resistor against -UV, capacitance against SGND
Input impedance ±Input 2
No usage of this input in this mode
Measurement ±10 mV 2:Fig.27: Representation ±10 mV measurement range
Note: In Extended Range Mode the Underrange/Overrange display in the PDO status has the character of an information/warning when the nominal measuring range is exceeded, i.e. no Error is displayed in the PDO status and LED. If the technical measuring range is also exceeded, Error = TRUE is also displayed. The detection limit for Underrange/Overrange Error can be set in the CoE.
In Legacy Range mode, an Underrange/Overrange event also leads to an Error in the PDO status.
