Potentiometer measurement
The potentiometer should be supplied with the integrated power supply unit (max. 5 V, configurable). The slider voltage is then measured relative to the supply voltage and output in %. Technical, the measurement is similar to a strain gauge half bridge.
Potentiometers from 1 kΩ can be used.
Diagnostics
- Slider breakage: full-scale deflection or 0 display
- Supply interruption: full-scale deflection or 0 display
| Measurement mode | Potentiometer (3/ 5 wire) | |||||
| Operation mode | The supply voltage is configurable via CoE, | |||||
| Measuring range, nominal | -1…1 V/V | |||||
| Measuring range, end value (full scale value) | 1 V/V | |||||
| Measuring range, technically usable | -1…1 V/V | |||||
| PDO resolution | 24 bit (incl. sign) | |||||
| PDO LSB (Extended Range) | 0.128 ppm | |||||
| PDO LSB (Legacy Range) | 0.119… ppm | |||||
| Basic accuracy: Measuring deviation at 23°C, with averaging | < ±0.05%FSV = ±500 ppmFSV | |||||
| Temperature coefficient (Terminal) | TcTerminal | < 15 ppm/K typ. | ||||
| Input impedance ±Input 1 (Internal resistance) | Differential 4.1 MΩ || 11 nF typ. | |||||
| CommonMode 1 MΩ || 40 nF typ. Methodology: Resistor against -UV, capacitance against SGND | ||||||
| Input impedance ±Input 2 (Internal resistance) | Differential 5 MΩ || 10 nF typ. | |||||
| CommonMode 1.25 MΩ || 40 nF typ. Methodology: Resistor against -UV (+2.5V), capacitance against SGND | ||||||
| Offset/Zero Point deviation (at 23°C) | EOffset | < 480 [ppmFSV] | ||||
| Gain/scale/amplification deviation (at 23°C) | EGain | < 100 [ppm] | ||||
| Non-linearity over the whole measuring range | ELin | < 75 [ppmFSV] | ||||
| Repeatability | ERep | < 50 [ppmFSV] | ||||
| Noise (peak-to-peak, without filtering) | ENoise, PtP | < 150 [ppmFSV] | < 1172 [digits] | |||
| ENoise, RMS | < 22 [ppmFSV] | < 172 [digits] | ||||
| Max. SNR | > 93.2 [dB] | |||||
| Noisedensity @1kHz | < 0.31  | |||||
| Noise (peak-to-peak, with 50Hz filtering) | ENoise, PtP | < 14 [ppmFSV] | < 109 [digits] | |||
| ENoise, RMS | < 2.5 [ppmFSV] | < 20 [digits] | ||||
| Max. SNR | > 112 [dB] | |||||
| Common-mode rejection ratio (without filtering)3 | DC: | 50 Hz: | 1 kHz: | |||
| Common-mode rejection ratio (with 50Hz filtering)3 | DC: | 50 Hz: | 1 kHz: | |||
| Largest short-term deviation during a specified electrical interference test | ±0.2%FSV = ±2000 ppmFSV typ. | |||||
3) Values related to a common mode interference between SGND and internal ground.
Potentiometer measurement range
| Note: In Extended Range Mode the Underrange/Overrange display in the PDO status has the character of an information/warning when the nominal measuring range is exceeded, i.e. no Error is displayed in the PDO status and LED. If the technical measuring range is also exceeded, Error = TRUE is also displayed. The detection limit for Underrange/Overrange Error can be set in the CoE. In Legacy Range mode, an Underrange/Overrange event also leads to an Error in the PDO status. |
 typ.
 typ. typ.
 typ.
