Technical data
Technical data
EL3681
EL3681-0030
Number of inputs
1 voltage or 1 current (1 A / 10 A)
Technology
Digital multimeter with automatic range selection
Measured values
Current AC/DC, voltage AC/DC **)
Voltage measuring ranges
300 mV, 3 V, 30 V, 300 V
Dielectric strength – destruction limit
480 V ACRMS/DC
Measuring ranges current
100 mA, 1 A and 10 A via high current path
Current carrying capacity - destruction limit
Measuring range 1 A: given by fuse;
Measuring range 10 A: short-time withstand current 30 A for 1 s (min. 5 min. cooling time)
Measuring procedure
DC with arithmetic averaging
AC with TrueRMS, 0..1 kHz input signal, Crest factor < 3 allowed
Resolution
18 bit + sign in each measuring range
Sampling type
simultaneous
Conversion method
DualSlope
Ground reference
differential
Internal resistance
Measuring range DC 300 mV - 300 V: 12.5 MΩ
Measuring range DC 100 mA - 1 A: 0.2 Ω
Measuring range DC 10 A: 3 mΩ
Measuring range AC 300 mV - 300 V: 1 MΩ, approx. 33 pF
Measuring range AC 100 mA - 1 A: 0.2 Ω
Measuring range AC 10 A: 3 mΩ
Measuring error
see table in chapter "Accuracy"
Max. sampling rate
62.5 ms
Electrical isolation
1,500 V (connection terminal/E-bus)
Power supply for the electronics
via the E-bus
Current consumption via E-bus
typ. 150 mA
Configuration
via TwinCAT System Manager
Weight
app. 70 g
Permissible ambient temperature range during operation
-25 °C… +60 °C
Permissible ambient temperature range during storage
-40 °C… +85 °C
Permissible relative air humidity
95 %, no condensation
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Installation
on 35 mm mounting rail, conforms to EN 60715
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
variable
Calibration certificate
with external calibration certificate
Marking *)
CE, EAC, UKCA
*) In AC mode, the terminal operates in TrueRMS mode, i.e. it does not digitally record the peak values Vpp, which are approx. 1.4 times larger, but the RMS value, see "Measuring procedure" and chapter "Technology".